I can tell you from experience, when antifreeze leaks onto a typed Hydraulic
Placard, all of the information disappears, completely.
From: Douglas Hicks
Sent: Thursday, July 07, 2016 7:06 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Base of riser on placards
Legible does not
I've used BOR at transition from UG to aboveground pipe.(Easy to find on
Hydraulics and thus find for Calc Plate)
Calc Plate , use a Sharpie then go over with Engraver.
@ 1 Main Drain test Static PSI was OK, then when opened main drainthe PSI
dropped and we got a garden hose amount.The Cities ho
SL
>
>
>
>
>
>
>
> *From:* Sprinklerforum [mailto:
> sprinklerforum-boun...@lists.firesprinkler.org] *On Behalf Of *Ben Young
> *Sent:* Monday, July 11, 2016 5:30 AM
> *To:* sprinklerforum@lists.firesprinkler.org
> *Subject:* Re: Base of riser on placards
>
&g
n...@lists.firesprinkler.org] *On Behalf Of *Ben Young
> *Sent:* Monday, July 11, 2016 5:30 AM
>
> *To:* sprinklerforum@lists.firesprinkler.org
> *Subject:* Re: Base of riser on placards
>
>
>
> Steve,
>
> I have to respectfully disagree with you on this. My main conce
hadn’t … who knows?
SL
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Ben Young
Sent: Monday, July 11, 2016 5:30 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Base of riser on placards
Steve,
I have to respectfully disagree with you on this
results to the BOR demand is a
> substantive metric.
>
>
>
> SL
>
>
>
> *From:* Sprinklerforum [mailto:
> sprinklerforum-boun...@lists.firesprinkler.org] *On Behalf Of *rongreenman
> .
> *Sent:* Friday, July 08, 2016 10:29 AM
> *To:* sprinklerforum@lists.firesprinkler.or
sts.firesprinkler.org] *On Behalf Of *Brad
> Casterline
> *Sent:* Friday, July 08, 2016 4:08 PM
> *To:* sprinklerforum@lists.firesprinkler.org
> *Subject:* Re: Base of riser on placards
>
>
>
> Sorry, I just wanted to add one more thing--
> Personally, I would be skidd
@lists.firesprinkler.org
Subject: Re: Base of riser on placards
Sorry, I just wanted to add one more thing--
Personally, I would be skiddish drawing too many conclusions from calc
placards. As-Builts and Main Drain Tests is what I would want. I would call BOR
the Riser Gauge. That would also be the Test
a year when you do the main drain
>>> test. Maybe you could add both BOR and Source demands, but I don’t agree
>>> with posting Source data in lieu of BOR.
>>>
>>>
>>>
>>> SL
>>>
>>>
>>>
>>> *From:* Sprinklerforum [m
value at least once a year when you do the main drain
>> test. Maybe you could add both BOR and Source demands, but I don’t agree
>> with posting Source data in lieu of BOR.
>>
>>
>>
>> SL
>>
>>
>>
>> *From:* Sprinklerforum [mailto:
>>
urce data in lieu of BOR.
>>
>>
>>
>> SL
>>
>>
>>
>> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
>> On Behalf Of Todd Williams
>> Sent: Friday, July 08, 2016 10:15 AM
>> To: sprinklerforum@lists.firesprinkl
nklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Todd Williams
Sent: Friday, July 08, 2016 2:15 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Base of riser on placards
I've also seen placards that are total crap, but that's another issue...
Todd G Williams, PE
Fire Protection Design/C
er.org
Subject: Re: Base of riser on placards
A main drain test is for comparison to previous main drain tests only. There
should be one done when the system in put in service. Any deviation from that
means a change in available water but not any hydraulic analysis
Sent using CloudM
placard
thread…
Scott
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Todd Williams
Sent: Friday, July 08, 2016 1:55 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Base of riser on placards
A
.
Sent: Friday, July 08, 2016 1:29 PM
To: sprinklerforum@lists.firesprinkler.org
[sprinklerforum@lists.firesprinkler.org]
Subject: Re: Base of riser on placards
So I have the total demand at the BOR and the expected pressure loss from
static with the entire design area flowing. How does a main dr
tions.com
>
>
>
> [image: CSS Logo]
>
>
>
> *From:* Sprinklerforum [mailto:
> sprinklerforum-boun...@lists.firesprinkler.org] *On Behalf Of *rongreenman
> .
> *Sent:* Friday, July 08, 2016 1:29 PM
> *To:* sprinklerforum@lists.firesprinkler.org
> *Subject:* Re: Base of
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of rongreenman .
Sent: Friday, July 08, 2016 1:29 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Base of riser on placards
So I have the total demand at the BOR and the expected pressure loss from
stati
n drain test results to the BOR demand is a
> substantive metric.
>
>
>
> SL
>
>
>
> *From:* Sprinklerforum [mailto:
> sprinklerforum-boun...@lists.firesprinkler.org] *On Behalf Of *rongreenman
> .
> *Sent:* Friday, July 08, 2016 10:29 AM
> *To:* sprinklerforu
-boun...@lists.firesprinkler.org] On
Behalf Of rongreenman .
Sent: Friday, July 08, 2016 10:29 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Base of riser on placards
So I have the total demand at the BOR and the expected pressure loss from
static with the entire design area flowing. How
oun...@lists.firesprinkler.org] *On Behalf Of *Todd
> Williams
> *Sent:* Friday, July 08, 2016 10:15 AM
> *To:* sprinklerforum@lists.firesprinkler.org
> *Subject:* RE: Base of riser on placards
>
>
>
> I'll ask the unthinkable question, is the BoR demand on the placard
&g
Williams
Sent: Friday, July 08, 2016 10:15 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Base of riser on placards
I'll ask the unthinkable question, is the BoR demand on the placard worthwhile?
Hydraulic calculations are done back to the effective point of the flow test.
The underg
I'll ask the unthinkable question, is the BoR demand on the placard worthwhile?
Hydraulic calculations are done back to the effective point of the flow test.
The underground losses, hose demand and sometimes backflow preventer losses are
taken before the BoR. Consequently you cannot compare the
I’ve asked this question in the past and the answers have been all over the
board.
I tend to think the BOR location needs to be consistent from project to
project, whether it’s a single system riser or multiple system risers. In our
part of the universe, most (but not all) backflow preven
:craig.pr...@ch2m.com>
Sent: Thursday, July 07, 2016 1:20 PM
To:
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Base of riser on placards
I don’t care what you call BOR. I’d be happy just to see a LEGIBLE and COMPLETE
Placard on each ri
@lists.firesprinkler.org] On
Behalf Of Steve Leyton
Sent: Thursday, July 07, 2016 4:10 PM
To:
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Base of riser on placards
Since it's intended to ID the demand residual pressure of a particu
Legible does not mean typed on a piece of paper, or scratched on a tinfoil
label.
From: craig.pr...@ch2m.com
Sent: Thursday, July 07, 2016 1:20 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Base of riser on placards
I don’t care what you call BOR. I’d be happy just to see a
gt; craig.pr...@ch2m.com
>
>
>
> *From:* Sprinklerforum [mailto:
> sprinklerforum-boun...@lists.firesprinkler.org] *On Behalf Of *Steve
> Leyton
> *Sent:* Thursday, July 07, 2016 4:10 PM
> *To:* sprinklerforum@lists.firesprinkler.org
> *Subject:* RE: Base of riser on placards
>
>
>
>
, July 07, 2016 4:10 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Base of riser on placards
Since it’s intended to ID the demand residual pressure of a particular design
area, it would make sense to locate it at a gauge that can be easily read to
corroborate the available and demand
Since it’s intended to ID the demand residual pressure of a particular design
area, it would make sense to locate it at a gauge that can be easily read to
corroborate the available and demand pressures, no? We usually pick a point
about 3 feet off the floor, because it’s nearly always within 1