Re: Combustible Concealed Space-Area Reduction

2016-10-14 Thread Roland Huggins
o:sprinklerforum-boun...@lists.firesprinkler.org > <mailto:sprinklerforum-boun...@lists.firesprinkler.org>] On Behalf Of Roland > Huggins > Sent: Friday, October 14, 2016 11:15 AM > To: sprinklerforum@lists.firesprinkler.org > <mailto:sprinklerforum@lists.firesprinkler.org> &g

Re: Combustible Concealed Space-Area Reduction

2016-10-14 Thread Roland Huggins
um-boun...@lists.firesprinkler.org > <mailto:sprinklerforum-boun...@lists.firesprinkler.org>] On Behalf Of John > Corcoran > Sent: Friday, October 14, 2016 8:56 AM > To: sprinklerforum@lists.firesprinkler.org > <mailto:sprinklerforum@lists.firesprinkler.org> > S

RE: Combustible Concealed Space-Area Reduction

2016-10-14 Thread Taylor Schumacher
14, 2016 8:56 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Combustible Concealed Space-Area Reduction Some input from our tech team: While NFPA 13 "requires" that specially tested and listed sprinklers be used in combustible concealed spaces 36" and less, the

RE: Combustible Concealed Space-Area Reduction

2016-10-14 Thread John Corcoran
orum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org> Subject: Re: Combustible Concealed Space-Area Reduction I think he is saying that his concealed space is >36" in depth. If so, then specially listed are not mandated. If so, I have always used the QR reduction for 10' ceiling

Re: Combustible Concealed Space-Area Reduction

2016-10-14 Thread Ben Young
Behalf Of *Travis Mack, SET > *Sent:* Thursday, October 13, 2016 5:51 PM > *To:* sprinklerforum@lists.firesprinkler.org > *Subject:* Re: Combustible Concealed Space-Area Reduction > > > > I think he is saying that his concealed space is >36" in depth. If so, >

RE: Combustible Concealed Space-Area Reduction

2016-10-13 Thread Cliff Whitfield
o 60" deep with 16 x 16 spacing on the market now. Cliff Whitfield From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Travis Mack, SET Sent: Thursday, October 13, 2016 5:51 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: Combustible Conce

Re: Combustible Concealed Space-Area Reduction

2016-10-13 Thread Travis Mack, SET
I think he is saying that his concealed space is >36" in depth. If so, then specially listed are not mandated. If so, I have always used the QR reduction for 10' ceiling height in those spaces provided it is a wet system. I have had some AHJs require I go to the floor to get my deck height.

RE: Combustible Concealed Space-Area Reduction

2016-10-13 Thread Cliff Whitfield
Taylor, I believe you will need to use Concealed Space Sprinklers for that area and will need to calc based on the manf data sheet. Cliff Whitfield, SET President Fire Design, Inc. From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Taylor