Taylor,

 

I believe you will need to use Concealed Space Sprinklers for that area and
will need to calc based on the manf data sheet.

 

Cliff Whitfield, SET

President

Fire Design, Inc.

 

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Taylor Schumacher
Sent: Thursday, October 13, 2016 4:55 PM
To: [email protected]
Subject: Combustible Concealed Space-Area Reduction

 

Good afternoon forum,

 

I'm looking to apply the remote area reduction per 11.2.3.2.3.1 in NFPA 13
2010 to a floor truss space over 36" using quick response, standard spray
sprinklers.

 

Could anyone tell me if my assumptions are right?

 

TAYLOR SCHUMACHER, CET

Security Fire Sprinkler 

P  320.656.0847  |  F  320.656.0312  |  E  [email protected]
<mailto:[email protected]> 

 



---