I think he is saying that his concealed space is >36" in depth. If so,
then specially listed are not mandated.
If so, I have always used the QR reduction for 10' ceiling height in
those spaces provided it is a wet system. I have had some AHJs require
I go to the floor to get my deck height. So, if you were 14' floor to
floor with a 10' ceiling and 24" open web floor trusses, then you could
use QR SSU to protect. A conservative approach would be to go with 14'
for your QR reduction point.
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]
http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign
LinkedIn: https://www.linkedin.com/in/travismack
On 10/13/2016 2:26 PM, Cliff Whitfield wrote:
Taylor,
I believe you will need to use Concealed Space Sprinklers for that
area and will need to calc based on the manf data sheet.
Cliff Whitfield, SET
President
Fire Design, Inc.
*From:* Sprinklerforum
[mailto:[email protected]] *On Behalf Of
*Taylor Schumacher
*Sent:* Thursday, October 13, 2016 4:55 PM
*To:* [email protected]
*Subject:* Combustible Concealed Space-Area Reduction
Good afternoon forum,
I’m looking to apply the remote area reduction per 11.2.3.2.3.1 in
NFPA 13 2010 to a floor truss space over 36” using quick response,
standard spray sprinklers.
Could anyone tell me if my assumptions are right?
*TAYLOR SCHUMACHER, CET*
Security Fire Sprinkler
*P *320.656.0847 | *F * 320.656.0312 | *E *[email protected]
<mailto:[email protected]>
------------------------------------------------------------------------
Avast logo
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
This email has been checked for viruses by Avast antivirus software.
www.avast.com
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org