RE: [EXTERNAL] Re: NFPA 13 Closet Definition

2018-08-21 Thread gmc
between the unit and framing has been a few inches an no sprinklers were required. From: Sprinklerforum On Behalf Of Prahl, Craig/GVL Sent: Tuesday, August 21, 2018 9:49 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: [EXTERNAL] Re: NFPA 13 Closet Definition Call it a closet or a

RE: [EXTERNAL] Re: NFPA 13 Closet Definition

2018-08-21 Thread Prahl, Craig/GVL
Call it a closet or a mechanical space but if your mandate is to provide sprinklers throughout, then that space isn't exempt from being sprinklered. Maybe consider a sidewall from an adjacent accessible space or extend the height of the access panel? If NFPA 13 doesn't' list apartment closets

Re: NFPA 13 Closet Definition

2018-08-21 Thread Roland Huggins
If it is a cavity in the wall and the only access is through a removable panel, we call it a concealed space. As for LSC and closets. IF both the LSC and IBC are applicable, what happens when you have two codes with differing requirements. You take the most conservative of the two. So if BOT

Re: NFPA 13 Closet Definition

2018-08-20 Thread Ron Greenman
If it is just a compartment to house the HVAC unit with an access panel is it a closet? Ron Greenman rongreen...@gmail.com 253.576.9700 The Universe is monstrously indifferent to the presence of man. -Werner Herzog, screenwriter, film director, author, actor and opera director (1942-) On Mon

RE: NFPA 13 Closet Definition

2018-08-20 Thread MFP Design, LLC
The annex never over-rides the main body. Without looking, I believe that annex D references the Life Safety Code. If that is a governing code of your project, then you could argue to take exceptions in the LSC. However, if you are just in I-Code land, then you will follow 13. That is my unders