If it is just a compartment to house the HVAC unit with an access panel is
it a closet?


Ron Greenman

[email protected]

253.576.9700

The Universe is monstrously indifferent to the presence of man. -Werner
Herzog, screenwriter, film director, author, actor and opera
director (1942-)


On Mon, Aug 20, 2018 at 3:08 PM MFP Design, LLC <[email protected]> wrote:

> *The annex never over-rides the main body.  Without looking, I believe
> that annex D references the Life Safety Code.  If that is a governing code
> of your project, then you could argue to take exceptions in the LSC.
> However, if you are just in I-Code land, then you will follow 13.  That is
> my understanding.*
>
>
>
> [image: MFP_logo_F]
>
> Travis Mack, SET
>
> MFP Design, LLC
>
> 3356 E Vallejo Ct
>
> Gilbert, AZ 85298
>
> 480-505-9271
>
> fax: 866-430-6107
>
> email:[email protected]
>
>
>
> http://www.mfpdesign.com
> <https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesign.com%2F&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=HJ8OA4xyeHAoxXNz5mu%2FYfycgtd5nsFrrpvzulZiNkQ%3D&reserved=0>
>
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2Fpages%2FMFP-Design-LLC%2F92218417692&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=H%2BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk%3D&reserved=0>
>
> Send large files to us via: https://www.hightail.com/u/MFPDesign
> <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
>
> LinkedIn: https://www.linkedin.com/in/travismack
> <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>
>
>
>
> *“**The bitterness of poor quality remains long after the sweetness of
> low price is forgotten.**”*
>
>
>
> *From:* Sprinklerforum <[email protected]> *On
> Behalf Of *Jay White
> *Sent:* Monday, August 20, 2018 2:54 PM
> *To:* [email protected]
> *Subject:* NFPA 13 Closet Definition
>
>
>
> NFPA 13 requires sprinklers in closets housing mechanical equipment. Is it
> still considered a closet if it does not have a door? There is just a
> removable panel to access the HVAC unit. There would be no access to the
> sprinkler at the top of the space. NFPA 13 also requires sprinklers in all
> closets except hotels & motels. Does Annex D 1.1.6.1 overide this
> requirement for clothes closets in apartment buildings?
>
>
>
> *Jay White*
>
> *Sales/Design Manager*
>
> *Dynamic Fire Protection*
>
> *9771 Highway 25 South*
>
> *Starkville, MS 39759*
>
> *PH:   662-312-2426*
>
> *FAX: 662-324-1545*
>
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to