Every time we have run into this situation it has been with metal framing.
The AHJ has looked at it and determined that the space around the unit is
considered a non combustible concealed space and thought it equivalent to an
air handler unit. In every case we have looked at the clear space between
the unit and framing has been a few inches an no sprinklers were required.

 

 

From: Sprinklerforum <[email protected]> On
Behalf Of Prahl, Craig/GVL
Sent: Tuesday, August 21, 2018 9:49 AM
To: [email protected]
Subject: RE: [EXTERNAL] Re: NFPA 13 Closet Definition

 

Call it a closet or a mechanical space but if your mandate is to provide
sprinklers throughout, then that space isn't exempt from being sprinklered.
Maybe consider a sidewall from an adjacent accessible space or extend the
height of the access panel?

 

If NFPA 13 doesn't' list apartment closets with the hotel/motel exception,
it doesn't apply.  The hotel/motel closet area is also limited to 24 sq. ft.
Most apartment closets are larger than that.

 

D.1.1.6.1 only exempts sprinklers in closets under 12 sq. ft. but still
requires sprinklers for closets containing equipment regardless of size.
But you need to read the Introduction to Appendix D as this Appendix is for
information and is not part of the NFPA 13 Standard requirements.  So,
unless NFPA 101 is an adopted standard in the Jurisdiction where your
project is located or has been otherwise required, Appendix D is not
applicable.  The Architect of Record should have established the applicable
codes to be applied to the project.  Check there to determine what is and
isn't applicable.

 

 

 

Craig Prahl | Jacobs | Group Lead - Fire Protection | 864.676.5252 |
[email protected] <mailto:[email protected]>  |
<http://www.jacobs.com/> www.jacobs.com

On Aug 20, 2018, at 2:54 PM, Jay White <[email protected]
<mailto:[email protected]> > wrote:

 

NFPA 13 requires sprinklers in closets housing mechanical equipment. Is it
still considered a closet if it does not have a door? There is just a
removable panel to access the HVAC unit. There would be no access to the
sprinkler at the top of the space. NFPA 13 also requires sprinklers in all
closets except hotels & motels. Does Annex D 1.1.6.1 overide this
requirement for clothes closets in apartment buildings?

 

Jay White

Sales/Design Manager

Dynamic Fire Protection

9771 Highway 25 South

Starkville, MS 39759

PH:   662-312-2426

FAX: 662-324-1545

 

 

 

_______________________________________________
Sprinklerforum mailing list
 <mailto:[email protected]>
[email protected]
 
<https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org
_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwMFAg&c=OgZOSER8c1RLeytE
exU279Q2qk0jVwkrOdYe5iSi-kk&r=6qYbbLx8x0UrMujmEGNoh-2hzoFD2d1EB5d2sQF0_OI&m=
CXBEtbxDUWgna97j5NyIBrS_IDznWg4WWlN_G2X9KIk&s=qmicTZIuvvyxVaYWSeDVvyGDSGujIP
_Wd1SqlKYjLGg&e=>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 

____________________________________________________________________________
____________

NOTICE - This communication may contain confidential and privileged
information that is for the sole use of the intended recipient. Any viewing,
copying or distribution of, or reliance on this message by unintended
recipients is strictly prohibited. If you have received this message in
error, please notify us immediately by replying to the message and deleting
it from your computer.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to