If it is a cavity in the wall and the only access is through a removable panel, 
we call it a concealed space.

As for LSC and closets.  IF both the LSC and IBC are applicable, what happens 
when you have two codes with differing requirements.  You take the most 
conservative of the two.  So if BOTH codes require   sprinklers and the IBC say 
follow 13 (no closet exception), then fully follow 13.  If ONLY The LSC 
requires sprinklers then the driving code allows the exception.

Roland 

Roland Huggins, PE - Senior VP Engineering
American Fire Sprinkler Assn.    
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>

Fire Sprinklers Saves Lives




> On Aug 20, 2018, at 2:54 PM, Jay White <[email protected]> wrote:
> 
> NFPA 13 requires sprinklers in closets housing mechanical equipment. Is it 
> still considered a closet if it does not have a door? There is just a 
> removable panel to access the HVAC unit. There would be no access to the 
> sprinkler at the top of the space. NFPA 13 also requires sprinklers in all 
> closets except hotels & motels. Does Annex D 1.1.6.1 overide this requirement 
> for clothes closets in apartment buildings?
>  
> Jay White
> Sales/Design Manager
> Dynamic Fire Protection
> 9771 Highway 25 South
> Starkville, MS 39759
> PH:   662-312-2426
> FAX: 662-324-1545
>  
>  
>  
> _______________________________________________
> Sprinklerforum mailing list
> [email protected] 
> <mailto:[email protected]>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 
> <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to