Subject: RE: PVC drain line
Creating a PVC drain header for the branch lines should not be done.
Same reason as not running PVC with sprinkler head tees. Not an approved
material.
Art Tiroly
ATCO Fire Protection
From: Sprinklerforum
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
On
@lists.firesprinkler.org
Subject: RE: PVC drain line
Yes, I do think that is the way to go, but it is a sprink contractor making
the suggestion. I'm trying to justify a response one way or the other.
Scott
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
From: Sprinkler
So you have a "tree" system ESFR you want to turn into a "grid" system with
plastic pipe.. Sounds like a bunch of calcs to be done. From "my" point of
view I would tie 2 branch lines together like a gang drain come off that to a
valve in the ceiling with steel pipe Depending on the size of
Why not fabricate small pieces (1-0) with a outlet for the head and put a
grooved cap on the end to flush at later time.
Long term solution imho
Sent from my cell phone. Please excuse spelling etc.
Mark Phillips
Vice President of Fire Protection, Kirlin Carolinas, LLC
t: 919-526-1584 | m: 91
r the sweetness of low
price is forgotten."
From: Sprinklerforum On
Behalf Of Scott Futrell
Sent: Friday, March 30, 2018 3:22 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: PVC drain line
Well.
Am I having a Friday afternoon brain fart?
Where does 13 say I can&
lf Of MFP Design, LLC
Sent: Friday, March 30, 2018 5:17 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: PVC drain line
I thought I was going to be called crazy for suggesting a valve at the end of
each line and then running it in PVC. It would be expensive for sure. Let me
know if yo
forum-boun...@lists.firesprinkler.org] On
Behalf Of Matthew J Willis
Sent: Friday, March 30, 2018 5:13 PM
To: Forum
Subject: RE: PVC drain line
So,
The answer would be no. Right?
Plastic is fine for drain, not listed. But all piping before the valve is.
R/
Matt
Sent from my Verizon 4G
he sweetness of low price
is forgotten.”
From: Sprinklerforum On Behalf
Of Matthew J Willis
Sent: Friday, March 30, 2018 3:13 PM
To: Forum
Subject: RE: PVC drain line
So,
The answer would be no. Right?
Plastic is fine for drain, not listed. But all piping before the valve is.
R/
Matt
Sent from
a=tT5E7L
sZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>
https://www.linkedin.com/in/travismack
"The bitterness of poor quality remains long after the sweetness of low
price is forgotten."
From: Sprinklerforum On
Behalf Of Matthew J Willis
Sent: Friday, March 30, 2018 3:13 PM
Once downstream of a labeled valve, fine. Upstream, and including valve, no. A
gang drain, for example uses materials complying with normal NFPA 13 materials.
I’m assuming valve at each branch line in order to get adequate flow.
Best.
Bruce Verhei
> On Mar 30, 2018, at 14:59, Scott Futrell
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: PVC drain line
I say it's fine if you have drain valves at the end of each line and transition
to pvc after the valve. But that may be expensive.
So I say pvc is ok after the drain valve.
But is that practical?
On Fri, Mar 30, 2018 at 4:59 P
oun...@lists.firesprinkler.org] On
Behalf Of Jeff Normand
Sent: Friday, March 30, 2018 5:07 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: PVC drain line
I say it's fine if you have drain valves at the end of each line and transition
to pvc after the valve. But that may be expensive.
So I
I say it's fine if you have drain valves at the end of each line and
transition to pvc after the valve. But that may be expensive.
So I say pvc is ok after the drain valve.
But is that practical?
On Fri, Mar 30, 2018 at 4:59 PM, Scott Futrell wrote:
> A Friday afternoon conundrum for the group