RE: Underground flushing velocities

2010-04-06 Thread George Church
23 PM To: Scott A. Futrell; sprinklerforum@firesprinkler.org Subject: Re: Underground flushing velocities If the underground contractor does not have his act together and your contract requires you to wait for him, inform the owner/GC that you regard this as a delay and give timely notice of a

Re: Underground flushing velocities

2010-04-05 Thread cherokeefire...@aol.com
If the underground contractor does not have his act together and your contract requires you to wait for him, inform the owner/GC that you regard this as a delay and give timely notice of a claim. That usually gets them moving for me! Forest Wilson Cherokee Fire Sent from my Verizon Wireless

Re: Underground flushing velocities

2010-04-05 Thread Ron Greenman
ew it, flush and fill. Last resort kinda thing, or at least > I wish it were more often. > > -Original Message- > From: sprinklerforum-boun...@firesprinkler.org > [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman > Sent: Monday, April 05, 2010 1:20

RE: Underground flushing velocities

2010-04-05 Thread George Church
On Behalf Of Ron Greenman Sent: Monday, April 05, 2010 1:20 PM To: sprinklerforum@firesprinkler.org Subject: Re: Underground flushing velocities Put a disclaimer in the proposal/contract that you aren't responsible for the UG and that you can't connect until the guy that is does his job.

RE: Underground flushing velocities

2010-04-05 Thread Scott A. Futrell
Our spec tells the sprinkler contractor not to connect to the ug until they've received the completed ug test papers and we have a copy. We also, in writing, inform the MEP of the requirement, including the 13/24 flush and test requirements. Sprinkler contractors almost always (very high percenta

Re: Underground flushing velocities

2010-04-05 Thread Ron Greenman
Copper Ridge Dr > P.O. Box 882136 > Steamboat Springs, CO 80488 > Tel:  970-879-7952 > Fax: 970-879-7926 > > > George Church > Subject: RE: Underground flushing velocities > > We put it on a U certif. noted we did flushing > only, and we put it in the file. If t

Re: Underground flushing velocities

2010-04-05 Thread rahe . loftin
Same rule in Texas Rahe Loftin - Original Message - From: "Thom McMahon" [tmcma...@firetechinc.com] Sent: 04/05/2010 10:37 AM CST To: Subject: RE: Underground flushing velocities Nice for you, unfortunately our state Div. of Fire Safety has made this rule that y

RE: Underground flushing velocities

2010-04-05 Thread Thom McMahon
o know 24, but often they are not, often they don't know anything about 24 and guess who the owner blames. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 George Church Subject: RE: Underground flushing vel

RE: Underground flushing velocities

2010-04-05 Thread George Church
um@firesprinkler.org Subject: RE: Underground flushing velocities Art, The flushing should be done before the valve is set. It should be done at the spigot flange. Typically, a pipe of the same size as the underground is attached to the floor flange and aimed out a door. Pitoting the output sh

RE: Underground flushing velocities

2010-04-05 Thread Craig.Prahl
Behalf Of rahe.lof...@gsa.gov Sent: Thursday, April 01, 2010 10:39 AM To: sprinklerforum@firesprinkler.org Subject: RE: Underground flushing velocities Craig, Pretty simple in order to not confuse us poor uneducated AHJs. I have no idea how we have been able to figure out anything considering how co

RE: Underground flushing velocities

2010-04-03 Thread rahe . loftin
Art, The flushing should be done before the valve is set. It should be done at the spigot flange. Typically, a pipe of the same size as the underground is attached to the floor flange and aimed out a door. Pitoting the output should tell you if the prescribed amount of water is discharged. Than

RE: Underground flushing velocities

2010-04-02 Thread Thom McMahon
x 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Art Tiroly Sent: Friday, April 02, 2010 10:30 AM To: sprinklerforum@firesprinkle

RE: Underground flushing velocities

2010-04-02 Thread Art Tiroly
warrant attention? -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Roland Huggins Sent: Wednesday, March 31, 2010 2:06 PM To: sprinklerforum@firesprinkler.org Subject: Re: Underground flushing velocities What it

RE: Underground flushing velocities

2010-04-01 Thread rahe . loftin
arch 31, 2010 2:06 PM To: sprinklerforum@firesprinkler.org Subject: Re: Underground flushing velocities What it actually says is: shall not be less than ONE of the following. So as long as you meet ANY one of the following you comply. As for why all the discussion on 10 ft/s, that is the golde

RE: Underground flushing velocities

2010-04-01 Thread Frank Herrick
Herrick -Original Message- From: Matthew J. Willis [mailto:m...@norredfire.com] Sent: Tuesday, March 30, 2010 3:57 PM To: Afsa Tech Forum Subject: Re: Underground flushing velocities If you have a pump, flows in 20 are higher. Matt Sent on the Sprint(r) Now Network from my BlackBerry(r) -

RE: Underground flushing velocities

2010-03-31 Thread Thom McMahon
The reason #3 is so popular is that it is so simple to apply in the field. Step#1: Open supply valve to riser. (Always direct water flow to a safe location.) Step#2: Allow full flow until water runs clear or for at least 2 minutes. Step#3: Close supply valve and cap riser, you're done flushing. No

RE: Underground flushing velocities

2010-03-31 Thread Thom McMahon
n, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 Subject: RE: Underground flushing velocities Oh come on Craig, any AHJ knows that a Velociraptor is Bob K ___ Sprinkl

RE: Underground flushing velocities

2010-03-31 Thread Cliff Whitfield
2010 2:26 PM To: sprinklerforum@firesprinkler.org Subject: RE: Underground flushing velocities You are correct the word any does not appear in the text. I guess my comment was slanted from the view that in the text for NFPA 24-1995. "The minimum rate of flow shall be not less than the wate

RE: Underground flushing velocities

2010-03-31 Thread Law, Kevin W
> From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum- > boun...@firesprinkler.org] On Behalf Of Law, Kevin W > Sent: Wednesday, March 31, 2010 11:38 AM > To: sprinklerforum@firesprinkler.org > Subject: RE: Underground flushing velocities > > The key is the req

RE: Underground flushing velocities

2010-03-31 Thread Law, Kevin W
forum@firesprinkler.org Subject: Re: Underground flushing velocities What it actually says is: shall not be less than ONE of the following. So as long as you meet ANY one of the following you comply. As for why all the discussion on 10 ft/s, that is the golden rule and they had to talk about something so they t

Re: Underground flushing velocities

2010-03-31 Thread Roland Huggins
Now you don't really mean that. These are three reasonable criteria and even the option (3) ensures you don't simply open an 1 inch ITV and say that's all I can flow. Conversely, option 3 cn also flow way beyond what is needed. The DOE plant where I served a long term sentence had a kill

RE: Underground flushing velocities

2010-03-31 Thread Bob Knight
...@ch2m.com Sent: Wednesday, March 31, 2010 12:15 PM To: sprinklerforum@firesprinkler.org Subject: RE: Underground flushing velocities The local AHJ wouldn't know the difference between Velocity and Velociraptor so no point even going there. So for the next NFPA 24 go-round they need to chang

RE: Underground flushing velocities

2010-03-31 Thread Craig.Prahl
Subject: RE: Underground flushing velocities With all due respect, I don't see the word 'any' anywhere in 10.10.2.1.3. I'm looking at the 2010 version, maybe older versions contain the word 'any'. Ed Kramer Littleton, CO > -Original Message- > From: spri

RE: Underground flushing velocities

2010-03-31 Thread Craig.Prahl
9 craig.pr...@ch2m.com http://www.ch2m.com -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ed Kramer Sent: Wednesday, March 31, 2010 2:09 PM To: sprinklerforum@firesprinkler.org Subject: RE: Underground flushing

RE: Underground flushing velocities

2010-03-31 Thread Craig.Prahl
sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Roland Huggins Sent: Wednesday, March 31, 2010 2:06 PM To: sprinklerforum@firesprinkler.org Subject: Re: Underground flushing velocities What it actually says is: shall not be less than ONE o

RE: Underground flushing velocities

2010-03-31 Thread John Denhardt
nklerforum-boun...@firesprinkler.org [mailto:sprinklerforum- > boun...@firesprinkler.org] On Behalf Of Law, Kevin W > Sent: Wednesday, March 31, 2010 11:38 AM > To: sprinklerforum@firesprinkler.org > Subject: RE: Underground flushing velocities > > The key is the requirement state

RE: Underground flushing velocities

2010-03-31 Thread Ed Kramer
r.org [mailto:sprinklerforum- > boun...@firesprinkler.org] On Behalf Of Law, Kevin W > Sent: Wednesday, March 31, 2010 11:38 AM > To: sprinklerforum@firesprinkler.org > Subject: RE: Underground flushing velocities > > The key is the requirement states it shall not be less than ANY one of

Re: Underground flushing velocities

2010-03-31 Thread Roland Huggins
lto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of > craig.pr...@ch2m.com > Sent: Wednesday, March 31, 2010 10:20 AM > To: sprinklerforum@firesprinkler.org > Subject: RE: Underground flushing velocities > > So if the max. velocity is only 2fps there's no issue? > &

Re: Underground flushing velocities

2010-03-31 Thread Ron Greenman
From: sprinklerforum-boun...@firesprinkler.org >> [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Roland Huggins >> Sent: Wednesday, March 31, 2010 12:51 PM >> To: sprinklerforum@firesprinkler.org >> Subject: Re: Underground flushing velocities >> >> Th

RE: Underground flushing velocities

2010-03-31 Thread lamarvaughn
4.599.4102 > Fax - 864.599.8439 > craig.pr...@ch2m.com > http://www.ch2m.com > > > -Original Message- > From: sprinklerforum-boun...@firesprinkler.org > [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Roland Huggins > Sent: Wednesday, March 31,

RE: Underground flushing velocities

2010-03-31 Thread Law, Kevin W
...@ch2m.com Sent: Wednesday, March 31, 2010 10:20 AM To: sprinklerforum@firesprinkler.org Subject: RE: Underground flushing velocities So if the max. velocity is only 2fps there's no issue? Then why the talk of 10fps in the appendix with mention of high velocity and Table relating to 10fps? If any vel

RE: Underground flushing velocities

2010-03-31 Thread Craig.Prahl
inkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Roland Huggins Sent: Wednesday, March 31, 2010 12:51 PM To: sprinklerforum@firesprinkler.org Subject: Re: Underground flushing velocities The 10 fps applies only to option 2, not all the options. As long as you meet any ONE of the options, w

Re: Underground flushing velocities

2010-03-31 Thread Roland Huggins
The 10 fps applies only to option 2, not all the options. As long as you meet any ONE of the options, where's the beef? The objective is to keep loose objects in the main from potentially blocking the sprinkler system. Option 2 assures us that we will remove the loose objects. The other o

RE: Underground flushing velocities

2010-03-31 Thread Thom McMahon
95% of the population, than we can by improving the protection we give that small part we call our customers. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 Subject: Re: Underground flushing velocities S

Re: Underground flushing velocities

2010-03-30 Thread Ron Greenman
trell > > (763) 425-1001 Office > (612) 759-5556 Cell > > -Original Message- > From: sprinklerforum-boun...@firesprinkler.org > [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman > Sent: Tuesday, March 30, 2010 4:03 PM > To: sprinklerforum@f

RE: Underground flushing velocities

2010-03-30 Thread Scott A. Futrell
001 Office (612) 759-5556 Cell -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman Sent: Tuesday, March 30, 2010 4:03 PM To: sprinklerforum@firesprinkler.org Subject: Re: Underground flushing velocities The

RE: Underground flushing velocities

2010-03-30 Thread Tom Duross
Getting that kind of scour is rare and very dependent on available pressure. When is it supposed to be flushed? When it's installed, right? How does it, us? Who witnesses the pressure test, us? What If wide open, bagged or not, you can't achieve the 10 fps rate? I wrote #20 years ago about hav

RE: Underground flushing velocities

2010-03-30 Thread George Church
From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Law, Kevin W Sent: Tuesday, March 30, 2010 5:44 PM To: sprinklerforum@firesprinkler.org Subject: RE: Underground flushing velocities We had a problem with our construction group wanting to allow a l

RE: Underground flushing velocities

2010-03-30 Thread Law, Kevin W
-Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom McMahon Sent: Tuesday, March 30, 2010 2:16 PM To: sprinklerforum@firesprinkler.org Subject: RE: Underground flushing velocities I think what #3 is saying is that let&#

RE: Underground flushing velocities

2010-03-30 Thread Craig.Prahl
bject: RE: Underground flushing velocities I think what #3 is saying is that let's say you have a 6" underground, but reduce at the riser to 3" because that is all of the system demand you have, you can flow a 3" open outlet at the riser to flush the underground, and that is

RE: Underground flushing velocities

2010-03-30 Thread Thom McMahon
I think what #3 is saying is that let's say you have a 6" underground, but reduce at the riser to 3" because that is all of the system demand you have, you can flow a 3" open outlet at the riser to flush the underground, and that is equal to the maximum flow rate available to the system under fire

Re: Underground flushing velocities

2010-03-30 Thread Ron Greenman
The objective is to move the water fast enough to move the crap and to move enough water that there's enough flow to get the stuff to the outlet so I think (dangerous) flow rate is more important. If I put my big thumb over the end of your 24" pipe I'll get good velocity but stuff might get hung u

Re: Underground flushing velocities

2010-03-30 Thread Matthew J. Willis
If you have a pump, flows in 20 are higher. Matt Sent on the Sprint® Now Network from my BlackBerry® -Original Message- From: "craig.pr...@ch2m.com" Date: Tue, 30 Mar 2010 16:47:12 To: sprinklerforum@firesprinkler.org Subject: Underground flushing velocities NFPA 24 says the following