23 PM
To: Scott A. Futrell; sprinklerforum@firesprinkler.org
Subject: Re: Underground flushing velocities
If the underground contractor does not have his act together and your
contract requires you to wait for him, inform the owner/GC that you regard
this as a delay and give timely notice of a
If the underground contractor does not have his act together and your contract
requires you to wait for him, inform the owner/GC that you regard this as a
delay and give timely notice of a claim.
That usually gets them moving for me!
Forest Wilson
Cherokee Fire
Sent from my Verizon Wireless
ew it, flush and fill. Last resort kinda thing, or at least
> I wish it were more often.
>
> -Original Message-
> From: sprinklerforum-boun...@firesprinkler.org
> [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman
> Sent: Monday, April 05, 2010 1:20
On Behalf Of Ron Greenman
Sent: Monday, April 05, 2010 1:20 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Underground flushing velocities
Put a disclaimer in the proposal/contract that you aren't responsible
for the UG and that you can't connect until the guy that is does his
job.
Our spec tells the sprinkler contractor not to connect to the ug until
they've received the completed ug test papers and we have a copy. We
also, in writing, inform the MEP of the requirement, including the 13/24
flush and test requirements. Sprinkler contractors almost always (very
high percenta
Copper Ridge Dr
> P.O. Box 882136
> Steamboat Springs, CO 80488
> Tel: 970-879-7952
> Fax: 970-879-7926
>
>
> George Church
> Subject: RE: Underground flushing velocities
>
> We put it on a U certif. noted we did flushing
> only, and we put it in the file. If t
Same rule in Texas
Rahe Loftin
- Original Message -
From: "Thom McMahon" [tmcma...@firetechinc.com]
Sent: 04/05/2010 10:37 AM CST
To:
Subject: RE: Underground flushing velocities
Nice for you, unfortunately our state Div. of Fire Safety has made this rule
that y
o know 24, but often they are not, often they don't know
anything about 24 and guess who the owner blames.
Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel: 970-879-7952
Fax: 970-879-7926
George Church
Subject: RE: Underground flushing vel
um@firesprinkler.org
Subject: RE: Underground flushing velocities
Art,
The flushing should be done before the valve is set. It should be done at
the spigot flange. Typically, a pipe of the same size as the underground
is attached to the floor flange and aimed out a door. Pitoting the output
sh
Behalf Of
rahe.lof...@gsa.gov
Sent: Thursday, April 01, 2010 10:39 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Underground flushing velocities
Craig,
Pretty simple in order to not confuse us poor uneducated AHJs. I have no idea
how we have been able to figure out anything considering how co
Art,
The flushing should be done before the valve is set. It should be done at
the spigot flange. Typically, a pipe of the same size as the underground
is attached to the floor flange and aimed out a door. Pitoting the output
should tell you if the prescribed amount of water is discharged.
Than
x 882136
Steamboat Springs, CO 80488
Tel: 970-879-7952
Fax: 970-879-7926
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Art Tiroly
Sent: Friday, April 02, 2010 10:30 AM
To: sprinklerforum@firesprinkle
warrant attention?
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Roland
Huggins
Sent: Wednesday, March 31, 2010 2:06 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Underground flushing velocities
What it
arch 31, 2010 2:06 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Underground flushing velocities
What it actually says is: shall not be less than ONE of the following. So
as long as you meet ANY one of the following you comply.
As for why all the discussion on 10 ft/s, that is the golde
Herrick
-Original Message-
From: Matthew J. Willis [mailto:m...@norredfire.com]
Sent: Tuesday, March 30, 2010 3:57 PM
To: Afsa Tech Forum
Subject: Re: Underground flushing velocities
If you have a pump, flows in 20 are higher.
Matt
Sent on the Sprint(r) Now Network from my BlackBerry(r)
-
The reason #3 is so popular is that it is so simple to apply in the field.
Step#1: Open supply valve to riser. (Always direct water flow to a safe
location.)
Step#2: Allow full flow until water runs clear or for at least 2 minutes.
Step#3: Close supply valve and cap riser, you're done flushing.
No
n, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel: 970-879-7952
Fax: 970-879-7926
Subject: RE: Underground flushing velocities
Oh come on Craig, any AHJ knows that a Velociraptor is
Bob K
___
Sprinkl
2010 2:26 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Underground flushing velocities
You are correct the word any does not appear in the text. I guess my
comment was slanted from the view that in the text for NFPA 24-1995.
"The minimum rate of flow shall be not less than the
wate
> From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-
> boun...@firesprinkler.org] On Behalf Of Law, Kevin W
> Sent: Wednesday, March 31, 2010 11:38 AM
> To: sprinklerforum@firesprinkler.org
> Subject: RE: Underground flushing velocities
>
> The key is the req
forum@firesprinkler.org
Subject: Re: Underground flushing velocities
What it actually says is: shall not be less than ONE of the following.
So as long as you meet ANY one of the following you comply.
As for why all the discussion on 10 ft/s, that is the golden rule and
they had to talk about something so they t
Now you don't really mean that. These are three reasonable criteria
and even the option (3) ensures you don't simply open an 1 inch ITV
and say that's all I can flow. Conversely, option 3 cn also flow way
beyond what is needed. The DOE plant where I served a long term
sentence had a kill
...@ch2m.com
Sent: Wednesday, March 31, 2010 12:15 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Underground flushing velocities
The local AHJ wouldn't know the difference between Velocity and Velociraptor
so no point even going there.
So for the next NFPA 24 go-round they need to chang
Subject: RE: Underground flushing velocities
With all due respect, I don't see the word 'any' anywhere in 10.10.2.1.3.
I'm looking at the 2010 version, maybe older versions contain the word 'any'.
Ed Kramer
Littleton, CO
> -Original Message-
> From: spri
9
craig.pr...@ch2m.com
http://www.ch2m.com
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ed Kramer
Sent: Wednesday, March 31, 2010 2:09 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Underground flushing
sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Roland Huggins
Sent: Wednesday, March 31, 2010 2:06 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Underground flushing velocities
What it actually says is: shall not be less than ONE o
nklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-
> boun...@firesprinkler.org] On Behalf Of Law, Kevin W
> Sent: Wednesday, March 31, 2010 11:38 AM
> To: sprinklerforum@firesprinkler.org
> Subject: RE: Underground flushing velocities
>
> The key is the requirement state
r.org [mailto:sprinklerforum-
> boun...@firesprinkler.org] On Behalf Of Law, Kevin W
> Sent: Wednesday, March 31, 2010 11:38 AM
> To: sprinklerforum@firesprinkler.org
> Subject: RE: Underground flushing velocities
>
> The key is the requirement states it shall not be less than ANY one of
lto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
> craig.pr...@ch2m.com
> Sent: Wednesday, March 31, 2010 10:20 AM
> To: sprinklerforum@firesprinkler.org
> Subject: RE: Underground flushing velocities
>
> So if the max. velocity is only 2fps there's no issue?
>
&
From: sprinklerforum-boun...@firesprinkler.org
>> [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Roland Huggins
>> Sent: Wednesday, March 31, 2010 12:51 PM
>> To: sprinklerforum@firesprinkler.org
>> Subject: Re: Underground flushing velocities
>>
>> Th
4.599.4102
> Fax - 864.599.8439
> craig.pr...@ch2m.com
> http://www.ch2m.com
>
>
> -Original Message-
> From: sprinklerforum-boun...@firesprinkler.org
> [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Roland Huggins
> Sent: Wednesday, March 31,
...@ch2m.com
Sent: Wednesday, March 31, 2010 10:20 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Underground flushing velocities
So if the max. velocity is only 2fps there's no issue?
Then why the talk of 10fps in the appendix with mention of high velocity
and Table relating to 10fps?
If any vel
inkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Roland Huggins
Sent: Wednesday, March 31, 2010 12:51 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Underground flushing velocities
The 10 fps applies only to option 2, not all the options. As long as you meet
any ONE of the options, w
The 10 fps applies only to option 2, not all the options. As long as
you meet any ONE of the options, where's the beef?
The objective is to keep loose objects in the main from potentially
blocking the sprinkler system. Option 2 assures us that we will
remove the loose objects. The other o
95% of the
population, than we can by improving the protection we give that small part
we call our customers.
Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel: 970-879-7952
Fax: 970-879-7926
Subject: Re: Underground flushing velocities
S
trell
>
> (763) 425-1001 Office
> (612) 759-5556 Cell
>
> -Original Message-
> From: sprinklerforum-boun...@firesprinkler.org
> [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman
> Sent: Tuesday, March 30, 2010 4:03 PM
> To: sprinklerforum@f
001 Office
(612) 759-5556 Cell
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman
Sent: Tuesday, March 30, 2010 4:03 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Underground flushing velocities
The
Getting that kind of scour is rare and very dependent on available pressure.
When is it supposed to be flushed? When it's installed, right? How does
it, us? Who witnesses the pressure test, us? What If wide open, bagged or
not, you can't achieve the 10 fps rate? I wrote #20 years ago about hav
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Law, Kevin W
Sent: Tuesday, March 30, 2010 5:44 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Underground flushing velocities
We had a problem with our construction group wanting to allow a l
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom
McMahon
Sent: Tuesday, March 30, 2010 2:16 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Underground flushing velocities
I think what #3 is saying is that let
bject: RE: Underground flushing velocities
I think what #3 is saying is that let's say you have a 6" underground, but
reduce at the riser to 3" because that is all of the system demand you have,
you can flow a 3" open outlet at the riser to flush the underground, and that
is
I think what #3 is saying is that let's say you have a 6" underground, but
reduce at the riser to 3" because that is all of the system demand you have,
you can flow a 3" open outlet at the riser to flush the underground, and
that is equal to the maximum flow rate available to the system under fire
The objective is to move the water fast enough to move the crap and to
move enough water that there's enough flow to get the stuff to the
outlet so I think (dangerous) flow rate is more important. If I put my
big thumb over the end of your 24" pipe I'll get good velocity but
stuff might get hung u
If you have a pump, flows in 20 are higher.
Matt
Sent on the Sprint® Now Network from my BlackBerry®
-Original Message-
From: "craig.pr...@ch2m.com"
Date: Tue, 30 Mar 2010 16:47:12
To: sprinklerforum@firesprinkler.org
Subject: Underground flushing velocities
NFPA 24 says the following