*Sent:* Thursday, February 28, 2019 2:33 PM
> *To:* sprinklerforum@lists.firesprinkler.org
> *Subject:* RE: Suction Tank Question
>
>
>
> Maybe this is a dumb question, but much like the return line for a relief,
> if the fill line is piped below the lowest level of water after system
: Thursday, February 28, 2019 2:33 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Suction Tank Question
Maybe this is a dumb question, but much like the return line for a relief, if
the fill line is piped below the lowest level of water after system demand is
satisfied, is there any way
@lists.firesprinkler.org'"
Date: 02/28/2019 03:25 PM
Subject:RE: Suction Tank Question
Sent by:"Sprinklerforum"
BE ADVISED - This email originated outside EMCOR.
IMHO the intent of the rule is to get the inlet away from the suction so
as to minimize th
9 9:42 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Suction Tank Question
NFPA 22 states the following:
14.4.10.1 Pipes for the automatic filling of suction tanks shall discharge into
the opposite half of the tanks from the pump suction pipe.
Does that mean that the fill line has
roup Lead – Fire Protection | 864.676.5252 |
> craig.pr...@jacobs.com <mailto:craig.pr...@jacobs.com> | www.jacobs.com
> <http://www.jacobs.com/>
>
> From: Sprinklerforum On
> Behalf Of Kyle.Montgomery
> Sent: Thursday, February 28, 2019 10:42 AM
> To: sprinkl
rinklerforum@lists.firesprinkler.org
Subject: [EXTERNAL] Suction Tank Question
NFPA 22 states the following:
14.4.10.1 Pipes for the automatic filling of suction tanks shall discharge into
the opposite half of the tanks from the pump suction pipe.
Does that mean that the fill line has to be directly acro
7 fax
From: Sprinklerforum on behalf
of Kyle.Montgomery
Sent: Thursday, February 28, 2019 10:10 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Suction Tank Question
That’s the situation we’ve got. Is that considered acceptable? Technically the
pump suction is on the b
7 fax
From: Sprinklerforum on behalf
of Kyle.Montgomery
Sent: Thursday, February 28, 2019 10:10 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Suction Tank Question
That’s the situation we’ve got. Is that considered acceptable? Technically the
pump suction is on the b
: Thursday, February 28, 2019 9:08 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: [EXTERNAL] Re: Suction Tank Question
If I remember correctly, I have seen the automatic fill lines enter near the
discharge. However, it would pipe up the inside of the tank near the top with a
turn down and
-3899 cell
850-836-2288 office
850-836-2277 fax
From: Sprinklerforum on behalf
of Kyle.Montgomery
Sent: Thursday, February 28, 2019 9:42 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Suction Tank Question
NFPA 22 states the following:
14.4.10.1 Pipes
Fort Wayne, IN • 46825
direct 260.487.7824 / cell 260.417.0625 / fax 260.487.7991
email mmo...@shambaugh.com
From: Kyle.Montgomery
To: "sprinklerforum@lists.firesprinkler.org"
Date: 02/28/2019 10:45 AM
Subject:Suction Tank Question
Sent by:"
NFPA 22 states the following:
14.4.10.1 Pipes for the automatic filling of suction tanks shall discharge into
the opposite half of the tanks from the pump suction pipe.
Does that mean that the fill line has to be directly across (opposite) the tank
from the pump suction? If I’ve got a tank with