Re: Am I reading this right?

2017-03-27 Thread MPhelps
If what you are saying is true, and I'm not questioning your statement, then this condition would not allow the lower obstruction to be the bottom chord of a steel bar joist or open web wood joist because the range pipe would need to be centered in the web of the joist and parallel to the joist,

RE: Am I reading this right?

2017-03-27 Thread Russell & Carol Gregory
Because an Upright ESFR sprinkler can be connected directly to a Range Pipe of up to 100mm NB thus it is tested with an obstruction to core discharge. The Upright ESFR sprinkler must have the yoke arms aligned with the Range Pipe therefore the obstruction is in the shadow area from the yoke arm

Re: RE: Exposed CPVC

2017-03-27 Thread Mike Cabral
blockquote, div.yahoo_quoted { margin-left: 0 !important; border-left:1px #715FFA solid !important; padding-left:1ex !important; background-color:white !important; } There are UV issues with exposed CPVC in Direct sunlight. Check manufacture limitations.  Sent from Yahoo Mail for iPhone On

RE: Drain Pipe Material

2017-03-27 Thread Jerry Van Kolken
This might actually be PVC pipe, but it has been rate for the drainage flows. Jerry Van Kolken Millennium Fire Protection (760) 722-2722 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Bruce Verhei Sent: Monday, March 27, 2017 1:20 PM To: sprinkl

Re: Drain Pipe Material

2017-03-27 Thread Bruce Verhei
Is this pipe that is reasonable for the pressure? The only time I ever asked about this was use of that very lightweight plastic pipe you see on the lawn irrigation aisle at Home Depot. It's been awhile but when I asked the designers' if this pipe was rated for 90 psi in one case, and 110 psi in

Re: Another NFPA 25 Question - Controllers

2017-03-27 Thread rongreenman .
I think it's out of control in a lot of places. In fact is like to see intent and justification documented for much of the document. Intent equaling what problem is this rule solving and justification delineating how severe and prevalent the risk versus what you gain for the cost. Maybe just the co

Re: Drain Pipe Material

2017-03-27 Thread rongreenman .
More important question. Are you planning to connect to a waste line without a receiver of some sort that provides for an approved air gap? On Mon, Mar 27, 2017 at 11:26 AM Parsley Consulting < parsleyconsult...@cox.net> wrote: > Jerry, > I would refer the fire marshal to NFPA 13, 2016, 6.1.1

Re: Another NFPA 25 Question - Controllers

2017-03-27 Thread Bruce Verhei
As a municipal fire inspector I always made sure I stood well back when the controller door was open. Flash burns are ugly. It's not like getting a simple broken arm or something. But I'm usually witnessing acceptance test. Most annual tests do include amps on each leg. Some have lead this

Re: Drain Pipe Material

2017-03-27 Thread Parsley Consulting
Jerry, I would refer the fire marshal to NFPA 13, 2016, 6.1.1.5: 6.1.1.5 Components that do not affect system performance such as _*drain piping*_, drain valves, and signs _*shall not*_ be required to be listed All the emphasis is mine. sincerely, *Ken Wagoner, SET *Parsley Cons

Drain Pipe Material

2017-03-27 Thread Jerry Van Kolken
Does the drain piping have to conform to NFPA 13-6.3 after the drain valve? I have a system where we have connected to the drain provided by the plumbers, but they provided ABS pipe. Now the Fire Marshal is citing these drains as deficiencies. Jerry Van Kolken Millennium Fire Protection C

RE: Another NFPA 25 Question - Controllers

2017-03-27 Thread Jim Davidson
Roland, If I remember correctly there was an analysis based on OSHA required “ARC” Flash analysis of a typical 440 volt fire pump controller. The analysis found that even with the highest level of PPE the person doing the measurements in the controller would need to be at such a distance from

RE: Another NFPA 25 Question - Controllers

2017-03-27 Thread Tom Duross
What do you mean by out of control? Monthly or weekly runs? I’m still old school but I do wear full PPE (most of the time) during annual testing, even after 3 arc flashes. I know.. I do a flush, 4 points with everything, 3 manual, 3 auto, exercise both disconnects, full run handle, even light

Re: Another NFPA 25 Question - Controllers

2017-03-27 Thread Roland Huggins
Speaking of owner’s don’t care, does any think that NFPA 25 is completely out of control regarding pumps? Roland Huggins, PE - Senior VP Engineering American Fire Sprinkler Assn. Dallas, TX http://www.firesprinkler.org Fire Sprinklers Saves Lives > On Mar

RE: Another NFPA 25 Question - Controllers

2017-03-27 Thread John Irwin
Great answer. John Irwin - CET Division Manager – Fire Sprinklers Critical System Solutions, LLC Licence Number: FPC16-53 Cell: 813.618.2781 Email: jir...@criticalsystemsolutions.com [cid:image003.png@01D2A6F3.ACC0B5A0] From: Sprinklerforum [m

Re: Another NFPA 25 Question - Controllers

2017-03-27 Thread Jeremy Blocker
The only ones we do in house are diesel drivers. This decision was only made when the insurance agent explained everything we would need to do to cover our rear. Also we found out that local licensing requires a master electrician be the one to touch high voltage. So the scenario presented to

RE: Another NFPA 25 Question - Controllers

2017-03-27 Thread John Irwin
You say 440 volt … So you do the 208v yourself? John Irwin - CET Division Manager – Fire Sprinklers Critical System Solutions, LLC Licence Number: FPC16-53 Cell: 813.618.2781 Email: jir...@criticalsystemsolutions.com [cid:image003.png@01D2A6F0.

RE: Another NFPA 25 Question - Controllers

2017-03-27 Thread John Irwin
I just checked our own report, and looked at a few others that I have on file. All ask for voltage and amps. John Irwin - CET Division Manager – Fire Sprinklers Critical System Solutions, LLC Licence Number: FPC16-53 Cell: 813.618.2781 Email: jir...@criticalsystemsolutions.com

RE: Another NFPA 25 Question - Controllers

2017-03-27 Thread John Irwin
I love the sentiment. But that’s a lot of up-selling when it comes to selling an inspection. We’re still competing with bottom feeders. And most property managers just don’t care. John Irwin - CET Division Manager – Fire Sprinklers Critical System Solutions, LLC Licence Number: FPC16-53 Cell

Re: Another NFPA 25 Question - Controllers

2017-03-27 Thread Jeremy Blocker
The easiest solution we found when faced with this very problem was to call in the experts. When we asked our insurance agent about this we discovered that we could end up needing to change our policy to cover high voltage exposure. So we now use manufacturers recommended pump service compani

RE: Another NFPA 25 Question - Controllers

2017-03-27 Thread Matthew J Willis
IS voltage a required item on the report? Along with amps? I always had the PPE and shook hands within.. R/ Matt Matthew J. Willis Project Manager Rapid Fire Protection Inc. 1530 Samco Road Rapid City, SD 57702 Office-605.348.2342 Direct Line-605.593.5063 Cell-605.391.2

Re: Another NFPA 25 Question - Controllers

2017-03-27 Thread Roland Huggins
There is a TIA to NFPA 25 effectively saying stay the hell out of it. We’ll see where it goes but it makes sense considering the hazard. What do our pump inspectors herein think? Roland Roland Huggins, PE - Senior VP Engineering American Fire Sprinkler Assn. Dallas, TX http://www.firespr

Re: Am I reading this right?

2017-03-27 Thread Roland Huggins
Lets assume he was typing too fast and meant to say that ESFR are NOT a control mode sprinkler. Upright ESFRs have a very different discharge pattern. The pendents have a very strong thrust zone in the middle of the pattern that play havoc with obstructions. Uprights do NOT. The penalty is t

Re: Am I reading this right?

2017-03-27 Thread MPhelps
There are upright ESFR sprinklers. They are K 19 (point something) and I believe they are metric and are popular in Europe. I could be mistaken about the metric part, but they are listed in the protection schemes for storage occupancy protection in NFPA 13 as ESFR. Mark at Aero 602 820-7894 S

Re: Another NFPA 25 Question - Controllers

2017-03-27 Thread John Denhardt
My personal opinion - no. John August Denhardt, P.E. Strickland Fire Protection On Mar 27, 2017, at 6:34 AM, John Irwin mailto:jir...@criticalsystemsolutions.com>> wrote: What are an inspector’s responsibilities when it comes to opening up a fire pump controller? One of our inspector’s wants

Re: Am I reading this right?

2017-03-27 Thread Mark Phillips
Short story is yes. Long version is an ESFR is not an upright it's a control mode sprinkler and has its own rules. Beyond that if you are using them then you usually have an insurance underwriter who also had their own rules Sent from my Verizon 4G LTE Droid On Mar 27, 2017 6:54 AM, Vince Sabol

Am I reading this right?

2017-03-27 Thread Vince Sabolik
NFPA 13, 2013 8.12.5.3.2.1 The requirements of 8.12.5.3.2 shall not apply where upright sprinklers are located over the bottom chords of bar joists or open trusses that are 4 in. (102 mm) maximum in width. Does this mean that an upright ESFR can be at or near center of a bar joist? Thanks,

Another NFPA 25 Question - Controllers

2017-03-27 Thread John Irwin
What are an inspector's responsibilities when it comes to opening up a fire pump controller? One of our inspector's wants me to buy him some PPE so he can comfortably open up the fire pump controller. I am certainly not opposed to this but I have talked to a number of inspectors at other compani