RE: Mixed-Use Code Question/Wish List

2009-03-17 Thread Thom McMahon
MORE MO!!! We were the wind! I had Ryan drive about 7 hours, now he wants to
know when he'll inherit!

Proposals will be for 2014 cycle for 13.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church
Sent: Monday, March 16, 2009 6:26 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Mixed-Use Code Question/Wish List

I didn't propose it during last cycle on 22 since I considered it a 13
thing. However, you've spurred me- I'll send a proposal in to the 13 TC
tonight. PWYP

Glc
Ps- and the ride home was awesome?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom McMahon
Sent: Monday, March 16, 2009 7:12 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Mixed-Use Code Question/Wish List

See George all you had to do was ask, and in less than 12 hours this forum
has removed one of your 6 bucket list items. Now if those pesky 22 committee
members would just get the tank gradient fixed!

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church
Sent: Monday, March 16, 2009 7:42 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Mixed-Use Code Question/Wish List


Now that we've got the IRC having SFD #13D in it, there's a couple wish list
items I'd also like to see before my time in this business is up:
1. Mandate tank gradient correction for water supplies 2. Stop putting
sprinklers out on decks for the IBC sprinkler whizzes 3. Stop the Heat/Vent
issue in sprinklered buildings so we don't have to go thru the charade of
filing a variance for egress distance 250' by using smoke vents, then
taking them back out because its ESFR. Plus the number of places with ESFR
in non-storage occupancies where they don't belong simply because they
enable omission of vents.
(4. What do we do with Big Ass Fans?) DONE!!! (At least for ESFR's) 5.
Competence increase throughout the industry's facets- PE/EOR, BCO/FCO,
Contractor alike.
6. A Coordination process that works and is enforced.

I'm sure there's a lot more, and others may want to run with this thread.
It'll give us some ideas for topics other than PE bashing, B A Fans, etc.

glc


___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Mixed-Use Code Question

2009-03-16 Thread Chris Cahill
OK I'll play the other side.  Any evidence that these otherwise should have
been 13 buildings have had any losses greater than what would have happened
in a 13?  This 13R where 13 is called for has been going on for at least 20
years.  We should have data by now.  

And FF's are to a large extent responsible for their own safety.  Their
actions largely define their risk not the building. And a majority of FF
deaths occur in non-fire attack mode.  20% die engaged in a fire fight. 

As a retired fire service member I am gravely concerned for the safety of
firefighters too but I certainly don't link 13 vs 13R to this conversation.


Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: chr...@sentryfiremn.com
 
Mail: P.O. Box 69
Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
  Waverly, MN 55390
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of John Drucker
Sent: Friday, March 13, 2009 4:04 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Mixed-Use Code Question

This is almost getting scary Huggins and Layton on the same page as an AHJ !
Yikes

Seriously I'm afraid that we have under protected buildings lurking, worse
some of them may have been built with construction type and separation
allowances under the assumption that compliant sprinkler systems were being
provided.

As a fire service member I am gravely concerned for the safety of
firefighters.

Sincerely

John Drucker
Active Firefighter
Fire Protection Subcode Official (AHJ)
Building/Fire/Electrical Inspector

Safe Buildings Save Lives !


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Roland
Huggins
Sent: Friday, March 13, 2009 4:52 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Mixed-Use Code Question

those have been lenient AHJ/BCO's.  Other than the previously  
discussed EXCEPTION (parking floor to other occupancies), the only way  
a single structure can be two or more buildings is separation by fire  
WALLS.  Walls in a horizontally orientation is called a collapsed  
building.

AS for dancing in the separated occupancy area, some will attempt to  
say that 508.3.3.1 allows each to be designed with total disregard for  
the other occupancy.  What it actual says is simply that each portion  
will be separately identified by its own occupancy.  IN order to apply  
a combination of 13 and 13R, you have to ignore that 903.3.1.2 that  
allows the use of 13R states Where allowed in BUILDINGS of Group R...  
shall be provided throughout.   IT doesn't say portions of buildings   
Now back in the confused past, I think 2003 but maybe older, the IBC  
did say portions of buildings within this section.  Because the older  
IBC was confusing, the 13R TC addressed this issue in the scope (and  
annex).  So in order to embrace the Separated approach, one also has  
to ignore the Scope of 13R.

Bottom line, without a local amendment allowing mixing systems, it is  
not allowed.  The ENTIRE building must satisfy the allowance to use 13R.

To put it another way, 20 yrs from now when I'm retired and looking  
for something to occupy my feeble mind, the first court questions for  
those that have embraced mixing of systems will be something like:   
Now aren't portions of buildings protected per NFPA 13 expected to  
provide property protection which encompasses continuity of business.  
So you agree I see.  Now doesn't a 13R system primarily focus on life  
safety with a much lower level of property protection whereas if you  
burn the roof off but the people get out, it's a success (thus  
allowing the attic to be unprotected).  So you agree again.  Now Mr  
Consultant (because this IS an engineering decision) how is it that  
just because the second floor was residential, you didn't protect the  
attic and you put poor old commercial guy on the first floor out of  
business. Doesn't that conflict with the scope of 13?  So you agree it  
does (well actually I'm sure the defendant would swallow their tongue  
before acknowledging that).

In looking at the big picture, it's an easy evaluation.  Focus just on  
one code section though, and ambiguity rears its ugly head.

Roland




On Mar 13, 2009, at 12:51 PM, Ron Greenman wrote:

 Although I disagree with interpretation for horizontal fire barriers
 that Jamie refers to that has been typical in many jurisdictions out
 on the best coast. As others have mentioned typically the entire lower
 floor is commercial with 13/horizontal fire barrier/13R above.

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word

Re: Mixed-Use Code Question

2009-03-16 Thread Roland Huggins
To repeat that famous quote:  Stupid IS as stupid DOES.

Roland

On Mar 14, 2009, at 7:29 AM, Tom Duross wrote:

  They think that once the other 7 units
 and common basement (OH2 per spec, ok by me) are completed, the  
 changes will
 only apply within the four walls of the unit.  I sent him a good  
 luck email
 an hour ago, I think I'm done even though I really need the work.

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Mixed-Use Code Question

2009-03-16 Thread Tom Duross
Funny...
I just heard second hand a competitor (who many fondly refer to as Gump)
got it and is running with the (deceit) ball.  55K job for 38K.
He also has fashioned a nicet stamp that looks just like a PE stamp, say's
registered sprinkler contractor around the edge with his nicet number in
the center, dumb idiot (some locals might know who I mean).  I saw it on a
set of plans of his once.

Tom

To repeat that famous quote:  Stupid IS as stupid DOES.

Roland

On Mar 14, 2009, at 7:29 AM, Tom Duross wrote:

  They think that once the other 7 units
 and common basement (OH2 per spec, ok by me) are completed, the
 changes will
 only apply within the four walls of the unit.  I sent him a good
 luck email
 an hour ago, I think I'm done even though I really need the work.

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: Mixed-Use Code Question

2009-03-16 Thread ParsleyConsulting
Tom,

Turn him in to NICET, they're awfully cranky about people doing that 
sort of thing, going so far as to pull certifications from individuals. 

Registered Sprinkler Contractor, that's a new one on me.

I bet he thinks it's pretty clever too. 
-- 
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
mailto:parsleyconsult...@cox.net

Tom Duross wrote:
 Funny...
 I just heard second hand a competitor (who many fondly refer to as Gump)
 got it and is running with the (deceit) ball. 55K job for 38K.
 He also has fashioned a nicet stamp that looks just like a PE stamp, say's
 registered sprinkler contractor around the edge with his nicet number in
 the center, dumb idiot (some locals might know who I mean). I saw it on a
 set of plans of his once.
 Tom
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Mixed-Use Code Question

2009-03-16 Thread George Church
I'll echo that completely - Mike will follow up on it.

Doubt you'd even have to have a copy of it, Tommy, I think if you just
emailed Mike Clark at Nicet, he'd just need the name of the guy and he'll
track them down. 

I've attached Mike's email address up at the top of this email, along with
yours, to pave the way for dialogue. Understand NICET is some version of the
National Society of PEs, shares space in the Washington Engineering
Headquarters in Alexandria, so the Board of Directors is likely chockfull of
PEs who aren't going to tolerate someone making a Jr PE seal out of a
NICET registration.

George Church
Rowe Sprinkler

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
ParsleyConsulting
Sent: Monday, March 16, 2009 2:41 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Mixed-Use Code Question

Tom,

Turn him in to NICET, they're awfully cranky about people doing that 
sort of thing, going so far as to pull certifications from individuals. 

Registered Sprinkler Contractor, that's a new one on me.

I bet he thinks it's pretty clever too. 
-- 
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
mailto:parsleyconsult...@cox.net

Tom Duross wrote:
 Funny...
 I just heard second hand a competitor (who many fondly refer to as Gump)
 got it and is running with the (deceit) ball. 55K job for 38K.
 He also has fashioned a nicet stamp that looks just like a PE stamp, say's
 registered sprinkler contractor around the edge with his nicet number in
 the center, dumb idiot (some locals might know who I mean). I saw it on a
 set of plans of his once.
 Tom
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Mixed-Use Code Question

2009-03-16 Thread Todd Williams
If I can help ferret out a copy of this guy's stamp, let me know. It 
still doesn't beat the contractor (same state) who was using the dead 
PE's stamp, but it is close.



At 02:34 PM 3/16/2009, you wrote:
Funny...
I just heard second hand a competitor (who many fondly refer to as Gump)
got it and is running with the (deceit) ball.  55K job for 38K.
He also has fashioned a nicet stamp that looks just like a PE stamp, say's
registered sprinkler contractor around the edge with his nicet number in
the center, dumb idiot (some locals might know who I mean).  I saw it on a
set of plans of his once.

Tom

To repeat that famous quote:  Stupid IS as stupid DOES.

Roland

On Mar 14, 2009, at 7:29 AM, Tom Duross wrote:

   They think that once the other 7 units
  and common basement (OH2 per spec, ok by me) are completed, the
  changes will
  only apply within the four walls of the unit.  I sent him a good
  luck email
  an hour ago, I think I'm done even though I really need the work.

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Mixed-Use Code Question

2009-03-16 Thread Tom Duross
I think there are a couple of members who know who he is.
Thanks,
I knew a contractor 20 years ago who had folders of sticky backs he had
copied of various PE's signed stamps off of plans.
Some people...


If I can help ferret out a copy of this guy's stamp, let me know. It
still doesn't beat the contractor (same state) who was using the dead
PE's stamp, but it is close.


___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Mixed-Use Code Question/Wish List

2009-03-16 Thread Thom McMahon
See George all you had to do was ask, and in less than 12 hours this forum
has removed one of your 6 bucket list items. Now if those pesky 22 committee
members would just get the tank gradient fixed!

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church
Sent: Monday, March 16, 2009 7:42 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Mixed-Use Code Question/Wish List


Now that we've got the IRC having SFD #13D in it, there's a couple wish list
items I'd also like to see before my time in this business is up:
1. Mandate tank gradient correction for water supplies 2. Stop putting
sprinklers out on decks for the IBC sprinkler whizzes 3. Stop the Heat/Vent
issue in sprinklered buildings so we don't have to go thru the charade of
filing a variance for egress distance 250' by using smoke vents, then
taking them back out because its ESFR. Plus the number of places with ESFR
in non-storage occupancies where they don't belong simply because they
enable omission of vents.
(4. What do we do with Big Ass Fans?) DONE!!! (At least for ESFR's)
5. Competence increase throughout the industry's facets- PE/EOR, BCO/FCO,
Contractor alike.
6. A Coordination process that works and is enforced.

I'm sure there's a lot more, and others may want to run with this thread.
It'll give us some ideas for topics other than PE bashing, B A Fans, etc.

glc


___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Mixed-Use Code Question/Wish List

2009-03-16 Thread George Church
I didn't propose it during last cycle on 22 since I considered it a 13
thing. However, you've spurred me- I'll send a proposal in to the 13 TC
tonight. PWYP

Glc
Ps- and the ride home was awesome?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom McMahon
Sent: Monday, March 16, 2009 7:12 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Mixed-Use Code Question/Wish List

See George all you had to do was ask, and in less than 12 hours this forum
has removed one of your 6 bucket list items. Now if those pesky 22 committee
members would just get the tank gradient fixed!

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church
Sent: Monday, March 16, 2009 7:42 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Mixed-Use Code Question/Wish List


Now that we've got the IRC having SFD #13D in it, there's a couple wish list
items I'd also like to see before my time in this business is up:
1. Mandate tank gradient correction for water supplies 2. Stop putting
sprinklers out on decks for the IBC sprinkler whizzes 3. Stop the Heat/Vent
issue in sprinklered buildings so we don't have to go thru the charade of
filing a variance for egress distance 250' by using smoke vents, then
taking them back out because its ESFR. Plus the number of places with ESFR
in non-storage occupancies where they don't belong simply because they
enable omission of vents.
(4. What do we do with Big Ass Fans?) DONE!!! (At least for ESFR's)
5. Competence increase throughout the industry's facets- PE/EOR, BCO/FCO,
Contractor alike.
6. A Coordination process that works and is enforced.

I'm sure there's a lot more, and others may want to run with this thread.
It'll give us some ideas for topics other than PE bashing, B A Fans, etc.

glc


___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: Mixed-Use Code Question

2009-03-14 Thread jdenhardt
Steve stated it great.  The committee did a good job of clearing any misuse.  I 
agree with John that we have buildings out there that are built to the wrong 
standard.  30 minutes and life safety goals in buildings that should of have a 
full system.

John
Sent from my BlackBerry® smartphone with Nextel Direct Connect

-Original Message-
From: Steve Leyton st...@protectiondesign.com

Date: Fri, 13 Mar 2009 14:11:52 
To: sprinklerforum@firesprinkler.org
Subject: RE: Mixed-Use Code Question


I agree with you, and the TC on Residential Sprinkler Systems has adopted 
language for Chapter 1 of 13R that is intended to finally clarify the 
appropriate application of the standard.   If ratified at the code hearing, the 
standard will be applicable buildings of residential occupancy and their 
accessory non-residential uses only; the only way that a single structure would 
have sprinkler systems designed to different standards is if it is 
fire-separated to the extent that the areas are considered separate buildings 
in accordance with the building code for that construction type.  These 
separations may be horizontal and/or vertical.
 
I've tried to transcribe Log #21, proposal 13R-2 below:

Revise the scope of NFPA 13R to read: 

1.1* Scope. This standard shall cover the design and installation of automatic 
sprinkler systems for protection against fire hazards in residential buildings 
up to and including four stories in height.

Revise A.1.1 as amended by Proposal 13R-58, Proposal 13R-57,  Proposal 13R-56, 
to read as follows: 

A.1.1 NFPA 13R is appropriate for use only in buildings that are entirely 
residential occupancies up to and including four stories in height. Residential 
occupancies are defined in this standard.  The height of the building is as 
defined in the applicable building code. It is the intent of this standard that 
if NFPA 13R is appropriate for use, that it be used throughout the entire 
building. It is recognized that incidental and accessory areas, as defined by 
the applicable building code, might exist within that residential occupancy. 
Such incidental and
accessory areas would typically be considered by the applicable building code 
to be part of the residential occupancy and subject to the requirements for the 
residential occupancy by.  Where buildings are greater than four stories in 
height, or where buildings are of mixed use, such buildings should be protected 
throughout with NFPA 13.  Where structures of mixed use can be totally 
separated so that a residential occupancy is considered a separate building 
under the applicable building code, NFPA 13R can be used in the building of 
entirely residential occupancy while NFPA 13 is used in the other building(s).  
(Examples of incidental and accessory occupancies found in residential 
occupancies can include: management offices,
private parking garages/areas within a dwelling unit, community laundry rooms, 
clubhouses, exercise facilities, tenant
storage within a dwelling unit, etc.).

Note, a separated mixed use structure (separated by fire-resistance rated 
assemblies) is not the same as a structure with separate buildings (separated 
by fire walls). However, there may be applicable building code provisions that 
permit upper and lower portions of a structure, separated by a three hour fire 
rated horizontal assembly, to be considered as separate buildings for certain 
purposes (See 2006 NFPA 5000, Section 7.4.3.6.5 and 2006 IBC Section 509.2).


Steve Leyton
Protection Design  Consulting
San Diego, CA


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman
Sent: Friday, March 13, 2009 12:51 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Mixed-Use Code Question

Although I disagree with interpretation for horizontal fire barriers
that Jamie refers to that has been typical in many jurisdictions out
on the best coast. As others have mentioned typically the entire lower
floor is commercial with 13/horizontal fire barrier/13R above.

On Fri, Mar 13, 2009 at 10:27 AM, Jamie Seidl jse...@affordablefire.com wrote:
 In IBC land, there is Separated and Non-separated mixed use. Non separated, 
 your entire building would be full 13.  In separated mixed use, as long as 
 the ratings meet the required separations or separate buildings of the 
 code, (including horizontal) you can use 13 for the lower area and 13R for 
 the upper.  There has been some contention on the designation of a separate 
 building and a horizontal fire barrier, but this configuration has met the 
 intent of the code in the jurisdictions I've dealt with.
 Jamie Seidl

 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org 
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Tom Duross
 Sent: Friday, March 13, 2009 12:23 PM
 To: sprinklerforum@firesprinkler.org
 Subject: Mixed-Use Code Question

 I have a question about

RE: Mixed-Use Code Question

2009-03-14 Thread John Drucker
The 13R origins and development statement says it all. The standard was
clearly promulgated to facilitate sprinklers in low rise, 4 story or less,
residential facilities. Nowhere is the term mixed use or mixed occupancy
referenced. I believe there's a misconception of what constitutes a
residential or a mixed use.

A residential building with a private parking garage serving the residents
and incidental use spaces such as mail rooms, lobbies, exercise rooms, trash
and utility rooms, manager's office is considered a single R Use pursuant to
the IBC/IFC. This is not a mixed use. 13R is the appropriate standard for
this building. The entire system is classified 13R not a 13/13R hybrid
something that simply doesn't exist. Yes you need selected sections of 13 to
sprinkler outside the dwelling units nonetheless its 13R that gets you
there, parts of 13 in effect are a reference, in the end the system is 13R.
(PS, 13R committee, take what you need out of 13 put it in 13R and be done
with it)

A residential building with a public garage, restaurants, offices, retail is
a mixed use building pursuant to the IBC/IFC. This is not a single R Use. 13
is the appropriate standard for this building. The entire system is 13.
Unlike 13R, 13 does not reference 13R. 


Origin and Development of NFPA 13R (Extracted From 2007 NFPA-13R, EMPHASIS
added)

The first edition of NFPA 13R, which was published in 1989, represented a
milestone in the development of sprinkler installation design standards. The
first edition resulted in a standard for the protection of low-rise,
RESIDENTIAL facilities. This standard is intended to provide a higher degree
of life safety and property protection to the INHABITENTS of low-rise,
multifamily DWELLINGS. Promulgated as a document that provides for increased
levels of protection to BUILDING OCCUPANTS, the document also considers the
economic aspects of a sprinklered facility as compared to an unsprinklered
facility. As the number of states and cities that implement sprinkler
ordinances continues to grow, and as the threshold levels for sprinkler
requirements in RESIDENTIAL occupancies in the building codes extend to
certain low-rise structures, it is believed that systems for certain
RESIDENTIAL occupancies can be efficiently and effectively installed in
accordance with this standard. The 1994 edition provided expanded
information on nonmetallic pipe materials, minor changes to clarify the
established design criteria, and a new recommendation on underground pipe
materials. The 1996 edition included several changes that paralleled
amendments in the 1996 edition of NFPA 13, Standard for the Installation of
Sprinkler Systems. Other changes included a number of clarifications
concerning the selection of sprinklers as well as the proper use of
sprinklers. The 1999 edition clarified criteria for nonmetallic pipe and
fittings and established a minimum operating pressure for sprinklers.
Guidance on providing freeze protection using insulation in attics and
antifreeze systems was provided, as was information on the application of
solvent cement for nonmetallic piping. Exceptions for omitting sprinkler
coverage in closets on balconies and underneath garage doors were added. The
2002 edition incorporated revisions to update the standard to comply with
the 2000 edition of the Manual of Style for NFPA Technical Committee
Documents. These revisions included editorially rewording any exceptions as
requirements. The 2002 edition also included changes that further clarified
the scope of the standard, established a minimum design discharge density,
and added protection requirements specifically for garages. The section
addressing spaces where sprinklers are permitted to be omitted was changed
so that the area of full-height tub/shower enclosures would be included in
the area determination for bathrooms, sprinklers would be provided in
concealed spaces with fuel-fired equipment, and the omission of sprinklers
in elevator machine rooms would not be dependent on the room's location.
This 2007 edition now includes spacing and obstruction rules addressing
sloped ceilings, ceiling pockets, ceiling fans, and kitchen cabinets. For
this edition, the requirements for utilizing quick-response sprinklers
within NFPA 13R regulations were clarified, and new requirements addressing
architectural features within dwelling units were added. Additionally, the
requirements covering closets, including obstructions within closets and
protection of mechanical closets, were clarified. Finally, new requirements
were added that are applicable from NFPA 13 to NFPA 13R, to ensure proper
administration of those requirements where relevant. 

Hope that helps.

Sincerely

John Drucker
Fire Protection Subcode Official
Building/Fire/Electrical Inspector

Safe Buildings Save Lives !


___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, 

RE: Mixed-Use Code Question

2009-03-14 Thread Tom Duross
I'm going to lose this job for one reason only but I'm doing right by the
code, my liability and my conscience (if that matters).
It's staying as a residential building for the long form application.  At
some point, they plan to apply for another permit for changing one unit from
residential to commercial use (they told me short form, but I think the
chart says the indexes require a long, not certain) but this will be done
after all the rough inspections have been received and they begin finish.  I
told them the use of pvc and certain types of residential wiring cannot be
used within the unit if it becomes commercial and all the ramifications of
the sprinkler work, but I prefaced it as I thought so not to appear as
some kind of expert more so they wouldn't keep asking me free questions for
free info (don't you HATE that?).  They think that once the other 7 units
and common basement (OH2 per spec, ok by me) are completed, the changes will
only apply within the four walls of the unit.  I sent him a good luck email
an hour ago, I think I'm done even though I really need the work.  I am
though, gonna be a sneaky pr*ck and copy the AHJ who's a friend..  ;)

I have to say I don't mean to seem like the guy who gets all these type of
jobs, what with the knucklehead who reviewed my plans last month but I think
they might seek me out and find me sometimes.  Maybe my sprinkler karma is
low or something.

Also not to digress but another I lost last summer that got around the
code I drove bye the other day, empty and all for sale and I smiled.
This guy (owner/builder/bank/self-titled expert) built a eight-unit
four-building attached four story condo with four one-and-two-family
residential permits, each building was two units, one over the other with
fire walls continuous from foundation to roof with air space ( he said he
was an expert holding his USG book) with the sole purpose of getting out
of standpipes and using 13D.  Separate 1 1/2 services into each 2 family
building.  It got built, it's done, 4 story stairs front and back, but at
least he's having trouble selling them ($599K each).

Tom


___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: Mixed-Use Code Question

2009-03-14 Thread Ron Greenman
Tom,

Let your conscious be your guide. I once told a contractor I was
working for I wouldn't design a building that was aboveground public
parking (1 level) with a horizontal fire wall (type I), then four
stories of type V apartments, all designed to 13R even though the
architect said it was OK because the parking was just for tenants and
there was a separation between the I and the V and there were only
four stories of apartments. I told the contractor he'd need to find
another designer and why I wouldn't do it. Props to him for also
refusing to do it even though approved by the architect and the AHJ.
And by the way that same contractor recently had another thread on
this forum because that same AHJ (jurisdiction-not individual although
that may also be the case) is refusing to allow for limited
combustibility in an unoccupied attic space because IBC doesn't
directly address limited combustibility in section X (I forget and
don't want to look it up) nor recognize that limited combustibility in
13 is just as much a part of IBC as any other part. So there you go--V
over I is OK, five stories of 13R is OK if you separate every four
with a horizontal fire wall (13R high rise condos anyone?), but
there is no such thing allowed as limited combustibility. Go figure.

On Sat, Mar 14, 2009 at 7:29 AM, Tom Duross tduro...@comcast.net wrote:
 I'm going to lose this job for one reason only but I'm doing right by the
 code, my liability and my conscience (if that matters).
 It's staying as a residential building for the long form application.  At
 some point, they plan to apply for another permit for changing one unit from
 residential to commercial use (they told me short form, but I think the
 chart says the indexes require a long, not certain) but this will be done
 after all the rough inspections have been received and they begin finish.  I
 told them the use of pvc and certain types of residential wiring cannot be
 used within the unit if it becomes commercial and all the ramifications of
 the sprinkler work, but I prefaced it as I thought so not to appear as
 some kind of expert more so they wouldn't keep asking me free questions for
 free info (don't you HATE that?).  They think that once the other 7 units
 and common basement (OH2 per spec, ok by me) are completed, the changes will
 only apply within the four walls of the unit.  I sent him a good luck email
 an hour ago, I think I'm done even though I really need the work.  I am
 though, gonna be a sneaky pr*ck and copy the AHJ who's a friend..  ;)

 I have to say I don't mean to seem like the guy who gets all these type of
 jobs, what with the knucklehead who reviewed my plans last month but I think
 they might seek me out and find me sometimes.  Maybe my sprinkler karma is
 low or something.

 Also not to digress but another I lost last summer that got around the
 code I drove bye the other day, empty and all for sale and I smiled.
 This guy (owner/builder/bank/self-titled expert) built a eight-unit
 four-building attached four story condo with four one-and-two-family
 residential permits, each building was two units, one over the other with
 fire walls continuous from foundation to roof with air space ( he said he
 was an expert holding his USG book) with the sole purpose of getting out
 of standpipes and using 13D.  Separate 1 1/2 services into each 2 family
 building.  It got built, it's done, 4 story stairs front and back, but at
 least he's having trouble selling them ($599K each).

 Tom


 ___
 Sprinklerforum mailing list
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
 For Technical Assistance, send an email to: techsupp...@firesprinkler.org

 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)




-- 
Ron Greenman
at home
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Mixed-Use Code Question

2009-03-13 Thread Steve Leyton
What we've done in the past is provide OH-2 at the lower (commercial)
level to allow for retail and then residential above.  But the entire
design has been per 13, albeit with the residential provisions of the
standard.

Steve Leyton
Protection Design  Consulting
San Diego, CA




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Tom
Duross
Sent: Friday, March 13, 2009 9:23 AM
To: sprinklerforum@firesprinkler.org
Subject: Mixed-Use Code Question

I have a question about a small project I'm bidding and how it relates
to
other's building codes.
Four storey 8 unit residential building, in bid stage, just got
notification
that one unit, half the ground floor, will be zoned for commercial use.
I'm at odds if this changes the building to mixed-use or not.  I've
asked
the gc if he's still applying as an R2 and he's not sure, architect in
on
vacation (go figure).  I'm leafing through our building code (ICC-03)
right
now to see if this qualifies as ancillary with regards to design (13 vs.
13R) but I just thought I'd ask the masses with a little time on their
hands
how this would resolve under their current codes.  Often we have similar
provisions and interpretations and I don't have the workbook, tabs or
supplement yet for ours.  We're new to this edition.

I'm able to refer to 13 for design in areas like Basements but still
base
the remainder of the system under 13R requirements and our old code gave
little guidance as to percentages with regards to areas outside of the
use
group.  I'm wondering if, disregarding permit application for now, the
addition of one of the 8 units from residential use to commercial use
(will
be a store) will effect the design.

Tom

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
 

__ Information from ESET NOD32 Antivirus, version of virus
signature database 3935 (20090313) __

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__ Information from ESET NOD32 Antivirus, version of virus
signature database 3935 (20090313) __

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Mixed-Use Code Question

2009-03-13 Thread John Drucker
Tom,

IBC Section 508. Incidental uses are those provided for in Table 508.2
pursuant to 508.2.1. and include private parking garages (406.2), otherwise
it's a mixed (occupancy) use and not a residential (occupancy) use.  13R
Residential Occupancies up to and Including Four Stories in Height , is not
the appropriate standard for mixed use occupancies.   

Keep in mind that the residential provisions of 13 can be applied in the
dwelling units.

Hope that helps

John Drucker

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Tom Duross
Sent: Friday, March 13, 2009 12:23 PM
To: sprinklerforum@firesprinkler.org
Subject: Mixed-Use Code Question

I have a question about a small project I'm bidding and how it relates to
other's building codes.
Four storey 8 unit residential building, in bid stage, just got notification
that one unit, half the ground floor, will be zoned for commercial use.
I'm at odds if this changes the building to mixed-use or not.  I've asked
the gc if he's still applying as an R2 and he's not sure, architect in on
vacation (go figure).  I'm leafing through our building code (ICC-03) right
now to see if this qualifies as ancillary with regards to design (13 vs.
13R) but I just thought I'd ask the masses with a little time on their hands
how this would resolve under their current codes.  Often we have similar
provisions and interpretations and I don't have the workbook, tabs or
supplement yet for ours.  We're new to this edition.

I'm able to refer to 13 for design in areas like Basements but still base
the remainder of the system under 13R requirements and our old code gave
little guidance as to percentages with regards to areas outside of the use
group.  I'm wondering if, disregarding permit application for now, the
addition of one of the 8 units from residential use to commercial use (will
be a store) will effect the design.

Tom

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Mixed-Use Code Question

2009-03-13 Thread Chappell, Carl
There are a few design directions the project may go.  One option is to
identify it as a separated mixed-use building, which requires fire-rated
separations between occupancy types and incidental use areas.  A second
option is non-separated mixed use where the architect / engineer need to
verify the type of construction and building height and areas are
compliant.  If utilizing non-separated mixed use, the incidental use
table does not apply.  Also, the inclusion of the retail / commercial
use will require NFPA 13.  

To go a little further, whether using separated mixed-use of
non-separated mixed-use, separate systems are not required per building
code, but may be advisable to keep the commercial and residential areas
separate.  


 
Carl Chappell


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Steve
Leyton
Sent: Friday, March 13, 2009 10:02 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Mixed-Use Code Question

What we've done in the past is provide OH-2 at the lower (commercial)
level to allow for retail and then residential above.  But the entire
design has been per 13, albeit with the residential provisions of the
standard.

Steve Leyton
Protection Design  Consulting
San Diego, CA




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Tom
Duross
Sent: Friday, March 13, 2009 9:23 AM
To: sprinklerforum@firesprinkler.org
Subject: Mixed-Use Code Question

I have a question about a small project I'm bidding and how it relates
to
other's building codes.
Four storey 8 unit residential building, in bid stage, just got
notification
that one unit, half the ground floor, will be zoned for commercial use.
I'm at odds if this changes the building to mixed-use or not.  I've
asked
the gc if he's still applying as an R2 and he's not sure, architect in
on
vacation (go figure).  I'm leafing through our building code (ICC-03)
right
now to see if this qualifies as ancillary with regards to design (13 vs.
13R) but I just thought I'd ask the masses with a little time on their
hands
how this would resolve under their current codes.  Often we have similar
provisions and interpretations and I don't have the workbook, tabs or
supplement yet for ours.  We're new to this edition.

I'm able to refer to 13 for design in areas like Basements but still
base
the remainder of the system under 13R requirements and our old code gave
little guidance as to percentages with regards to areas outside of the
use
group.  I'm wondering if, disregarding permit application for now, the
addition of one of the 8 units from residential use to commercial use
(will
be a store) will effect the design.

Tom

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
 

__ Information from ESET NOD32 Antivirus, version of virus
signature database 3935 (20090313) __

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__ Information from ESET NOD32 Antivirus, version of virus
signature database 3935 (20090313) __

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Mixed-Use Code Question

2009-03-13 Thread Jamie Seidl
In IBC land, there is Separated and Non-separated mixed use. Non separated, 
your entire building would be full 13.  In separated mixed use, as long as the 
ratings meet the required separations or separate buildings of the code, 
(including horizontal) you can use 13 for the lower area and 13R for the upper. 
 There has been some contention on the designation of a separate building and a 
horizontal fire barrier, but this configuration has met the intent of the code 
in the jurisdictions I've dealt with.
Jamie Seidl

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Tom Duross
Sent: Friday, March 13, 2009 12:23 PM
To: sprinklerforum@firesprinkler.org
Subject: Mixed-Use Code Question

I have a question about a small project I'm bidding and how it relates to
other's building codes.
Four storey 8 unit residential building, in bid stage, just got notification
that one unit, half the ground floor, will be zoned for commercial use.
I'm at odds if this changes the building to mixed-use or not.  I've asked
the gc if he's still applying as an R2 and he's not sure, architect in on
vacation (go figure).  I'm leafing through our building code (ICC-03) right
now to see if this qualifies as ancillary with regards to design (13 vs.
13R) but I just thought I'd ask the masses with a little time on their hands
how this would resolve under their current codes.  Often we have similar
provisions and interpretations and I don't have the workbook, tabs or
supplement yet for ours.  We're new to this edition.

I'm able to refer to 13 for design in areas like Basements but still base
the remainder of the system under 13R requirements and our old code gave
little guidance as to percentages with regards to areas outside of the use
group.  I'm wondering if, disregarding permit application for now, the
addition of one of the 8 units from residential use to commercial use (will
be a store) will effect the design.

Tom

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Mixed-Use Code Question

2009-03-13 Thread Tom Duross
Thanks.  My take is the owner got the chance for an early sale as a
commercial condo and wants to take it.
I wrote the gc that I thought the implications to spkr. and fa design might
effect the rest of the building and they might want to reconsider the quick
sale and factor in the details.  I just wrote them back and referred to
John's (and others) clarifications (thanks again) and put together a fast
budget of density, concealed space, and pipe size changes (type v
construction btw) and also a heads up for the plumber and electrician's
changes.  Looks like a go even with the additional costs associated.

Tom

For you seasoned users of this code, new to us 3/1/09, where did you get
your tabs and supplements?  I'm still at the highlighter and dog-ear stage
and trying to bone-up quick.


In IBC land, there is Separated and Non-separated mixed use. Non separated,
your entire building would be full 13.  In separated mixed use, as long as
the ratings meet the required separations or separate buildings of the
code, (including horizontal) you can use 13 for the lower area and 13R for
the upper.  There has been some contention on the designation of a separate
building and a horizontal fire barrier, but this configuration has met the
intent of the code in the jurisdictions I've dealt with.
Jamie Seidl

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Mixed-Use Code Question

2009-03-13 Thread Jamie Seidl
Eh, you don't need the tabs they're over rated... and they fall off... I think 
mine are still in the bottom of a box some where... a 6 pack get's em!
Jamie

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Tom Duross
Sent: Friday, March 13, 2009 1:50 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Mixed-Use Code Question

Thanks.  My take is the owner got the chance for an early sale as a
commercial condo and wants to take it.
I wrote the gc that I thought the implications to spkr. and fa design might
effect the rest of the building and they might want to reconsider the quick
sale and factor in the details.  I just wrote them back and referred to
John's (and others) clarifications (thanks again) and put together a fast
budget of density, concealed space, and pipe size changes (type v
construction btw) and also a heads up for the plumber and electrician's
changes.  Looks like a go even with the additional costs associated.

Tom

For you seasoned users of this code, new to us 3/1/09, where did you get
your tabs and supplements?  I'm still at the highlighter and dog-ear stage
and trying to bone-up quick.


In IBC land, there is Separated and Non-separated mixed use. Non separated,
your entire building would be full 13.  In separated mixed use, as long as
the ratings meet the required separations or separate buildings of the
code, (including horizontal) you can use 13 for the lower area and 13R for
the upper.  There has been some contention on the designation of a separate
building and a horizontal fire barrier, but this configuration has met the
intent of the code in the jurisdictions I've dealt with.
Jamie Seidl

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Mixed-Use Code Question

2009-03-13 Thread John Drucker
Careful on the IBC 509 provisions, i.e. so called horizontal
firewalls. 

First and foremost anything horizontal isn't termed a wall. Second
firewalls must meet the criteria of being able to collapse on either
side, but not both, without effecting the opposite side. As Scotty once
said Captain I cant defy the laws of physics !  When the lower floor
goes, well I guess you know what happens next. So much for horizontal
firewalls and separate buildings created by them.

Lets take a closer look at 509, 509.2 to be exact.  Heres what it
says; 

A basement and/or the first story above grade plane of a building shall
be considered as a separate and distinct building for the purpose of
determining area limitations, continuity of fire walls, limitation of
number of stories and type of construction.

The commentary hits the nail on the head; The subsections of Section
509 are EXCEPTIONS to the general HEIGHT AND AREA limitations of Chapter
5.  Nothing in there about exceptions for Chapter 9, Mixed Uses and
Sprinklers.  

 In the end its still a mixed use building where an allowance for
height, area and construction type has been made for a 3 Hr horizontal
assembly. Back in the day we called this taxpayer buildings making good
use of available land, parking below, commercial/mercantile at grade and
residential above the first floor. The IBC merely accomodates this with
regards to building construction.

So in the end if its mixed its 13.

Hope that helps

John Drucker
Fire Protection Subcode Official




 
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jamie
Seidl
Sent: Friday, March 13, 2009 1:28 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Mixed-Use Code Question

In IBC land, there is Separated and Non-separated mixed use. Non
separated, your entire building would be full 13.  In separated mixed
use, as long as the ratings meet the required separations or separate
buildings of the code, (including horizontal) you can use 13 for the
lower area and 13R for the upper.  There has been some contention on the
designation of a separate building and a horizontal fire barrier, but
this configuration has met the intent of the code in the jurisdictions
I've dealt with.
Jamie Seidl

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Tom
Duross
Sent: Friday, March 13, 2009 12:23 PM
To: sprinklerforum@firesprinkler.org
Subject: Mixed-Use Code Question

I have a question about a small project I'm bidding and how it relates
to other's building codes.
Four storey 8 unit residential building, in bid stage, just got
notification that one unit, half the ground floor, will be zoned for
commercial use.
I'm at odds if this changes the building to mixed-use or not.  I've
asked the gc if he's still applying as an R2 and he's not sure,
architect in on vacation (go figure).  I'm leafing through our building
code (ICC-03) right now to see if this qualifies as ancillary with
regards to design (13 vs.
13R) but I just thought I'd ask the masses with a little time on their
hands how this would resolve under their current codes.  Often we have
similar provisions and interpretations and I don't have the workbook,
tabs or supplement yet for ours.  We're new to this edition.

I'm able to refer to 13 for design in areas like Basements but still
base the remainder of the system under 13R requirements and our old code
gave little guidance as to percentages with regards to areas outside of
the use group.  I'm wondering if, disregarding permit application for
now, the addition of one of the 8 units from residential use to
commercial use (will be a store) will effect the design.

Tom

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or entity to 
which it is addressed and may contain information that is privileged and 
confidential, nor is it, unless specifically stated, intended to be relied upon 
by any person or persons other than the individual or entity named above and no 
warranties or representations are made or intended to persons or entities not 
named above.  If the reader is not the intended recipient, you are hereby 
notified that any dissemination

Re: Mixed-Use Code Question

2009-03-13 Thread Ron Greenman
Although I disagree with interpretation for horizontal fire barriers
that Jamie refers to that has been typical in many jurisdictions out
on the best coast. As others have mentioned typically the entire lower
floor is commercial with 13/horizontal fire barrier/13R above.

On Fri, Mar 13, 2009 at 10:27 AM, Jamie Seidl jse...@affordablefire.com wrote:
 In IBC land, there is Separated and Non-separated mixed use. Non separated, 
 your entire building would be full 13.  In separated mixed use, as long as 
 the ratings meet the required separations or separate buildings of the 
 code, (including horizontal) you can use 13 for the lower area and 13R for 
 the upper.  There has been some contention on the designation of a separate 
 building and a horizontal fire barrier, but this configuration has met the 
 intent of the code in the jurisdictions I've dealt with.
 Jamie Seidl

 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org 
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Tom Duross
 Sent: Friday, March 13, 2009 12:23 PM
 To: sprinklerforum@firesprinkler.org
 Subject: Mixed-Use Code Question

 I have a question about a small project I'm bidding and how it relates to
 other's building codes.
 Four storey 8 unit residential building, in bid stage, just got notification
 that one unit, half the ground floor, will be zoned for commercial use.
 I'm at odds if this changes the building to mixed-use or not.  I've asked
 the gc if he's still applying as an R2 and he's not sure, architect in on
 vacation (go figure).  I'm leafing through our building code (ICC-03) right
 now to see if this qualifies as ancillary with regards to design (13 vs.
 13R) but I just thought I'd ask the masses with a little time on their hands
 how this would resolve under their current codes.  Often we have similar
 provisions and interpretations and I don't have the workbook, tabs or
 supplement yet for ours.  We're new to this edition.

 I'm able to refer to 13 for design in areas like Basements but still base
 the remainder of the system under 13R requirements and our old code gave
 little guidance as to percentages with regards to areas outside of the use
 group.  I'm wondering if, disregarding permit application for now, the
 addition of one of the 8 units from residential use to commercial use (will
 be a store) will effect the design.

 Tom

 ___
 Sprinklerforum mailing list
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
 For Technical Assistance, send an email to: techsupp...@firesprinkler.org

 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)
 ___
 Sprinklerforum mailing list
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
 For Technical Assistance, send an email to: techsupp...@firesprinkler.org

 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)




-- 
Ron Greenman
at home
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Mixed-Use Code Question

2009-03-13 Thread Jamie Seidl
As always, I should have clarified...  I was looking at the North Carolina IBC. 
Table 302.3.2 in the NCIBC (table 508.3.3 in the 2006 IBC) omitted the (S) and 
(NS) designations for the required separation of occupancies. Which basically 
means you don't necessarily have to stick to 903.3.1.1 for sprinkler system 
type.  Thus in North Carolina, you can have a separated mixed use building, 
I.E. group R above an S, B, M, ect... where the sprinkler system only needs to 
meet the requirements for the occupancy as long as you comply with the 
separation requirements.
So in NC, non separated mixed use... full 13. Separated mixed use, system per 
occupancy classification as long as you haven't exceeded height, area, open 
area, fire lane ect. limitations and the AHJ is ok with it.  When did Dixie 
become so progressive?

John, I would agree whole heartedly that anything horizontal isn't termed a 
wall.  It's a fire barrier.  I've gotten called out on the carpet for that 
verbiage before :)
Jamie Seidl
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of John Drucker
Sent: Friday, March 13, 2009 2:35 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Mixed-Use Code Question

Careful on the IBC 509 provisions, i.e. so called horizontal
firewalls.

First and foremost anything horizontal isn't termed a wall. Second
firewalls must meet the criteria of being able to collapse on either
side, but not both, without effecting the opposite side. As Scotty once
said Captain I cant defy the laws of physics !  When the lower floor
goes, well I guess you know what happens next. So much for horizontal
firewalls and separate buildings created by them.

Lets take a closer look at 509, 509.2 to be exact.  Heres what it
says;

A basement and/or the first story above grade plane of a building shall
be considered as a separate and distinct building for the purpose of
determining area limitations, continuity of fire walls, limitation of
number of stories and type of construction.

The commentary hits the nail on the head; The subsections of Section
509 are EXCEPTIONS to the general HEIGHT AND AREA limitations of Chapter
5.  Nothing in there about exceptions for Chapter 9, Mixed Uses and
Sprinklers.

 In the end its still a mixed use building where an allowance for
height, area and construction type has been made for a 3 Hr horizontal
assembly. Back in the day we called this taxpayer buildings making good
use of available land, parking below, commercial/mercantile at grade and
residential above the first floor. The IBC merely accomodates this with
regards to building construction.

So in the end if its mixed its 13.

Hope that helps

John Drucker
Fire Protection Subcode Official





-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jamie
Seidl
Sent: Friday, March 13, 2009 1:28 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Mixed-Use Code Question

In IBC land, there is Separated and Non-separated mixed use. Non
separated, your entire building would be full 13.  In separated mixed
use, as long as the ratings meet the required separations or separate
buildings of the code, (including horizontal) you can use 13 for the
lower area and 13R for the upper.  There has been some contention on the
designation of a separate building and a horizontal fire barrier, but
this configuration has met the intent of the code in the jurisdictions
I've dealt with.
Jamie Seidl

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Tom
Duross
Sent: Friday, March 13, 2009 12:23 PM
To: sprinklerforum@firesprinkler.org
Subject: Mixed-Use Code Question

I have a question about a small project I'm bidding and how it relates
to other's building codes.
Four storey 8 unit residential building, in bid stage, just got
notification that one unit, half the ground floor, will be zoned for
commercial use.
I'm at odds if this changes the building to mixed-use or not.  I've
asked the gc if he's still applying as an R2 and he's not sure,
architect in on vacation (go figure).  I'm leafing through our building
code (ICC-03) right now to see if this qualifies as ancillary with
regards to design (13 vs.
13R) but I just thought I'd ask the masses with a little time on their
hands how this would resolve under their current codes.  Often we have
similar provisions and interpretations and I don't have the workbook,
tabs or supplement yet for ours.  We're new to this edition.

I'm able to refer to 13 for design in areas like Basements but still
base the remainder of the system under 13R requirements and our old code
gave little guidance as to percentages with regards to areas outside of
the use group.  I'm wondering if, disregarding permit application for
now, the addition of one of the 8 units from residential use

Re: Mixed-Use Code Question

2009-03-13 Thread Roland Huggins
those have been lenient AHJ/BCO's.  Other than the previously  
discussed EXCEPTION (parking floor to other occupancies), the only way  
a single structure can be two or more buildings is separation by fire  
WALLS.  Walls in a horizontally orientation is called a collapsed  
building.

AS for dancing in the separated occupancy area, some will attempt to  
say that 508.3.3.1 allows each to be designed with total disregard for  
the other occupancy.  What it actual says is simply that each portion  
will be separately identified by its own occupancy.  IN order to apply  
a combination of 13 and 13R, you have to ignore that 903.3.1.2 that  
allows the use of 13R states Where allowed in BUILDINGS of Group R...  
shall be provided throughout.   IT doesn't say portions of buildings   
Now back in the confused past, I think 2003 but maybe older, the IBC  
did say portions of buildings within this section.  Because the older  
IBC was confusing, the 13R TC addressed this issue in the scope (and  
annex).  So in order to embrace the Separated approach, one also has  
to ignore the Scope of 13R.

Bottom line, without a local amendment allowing mixing systems, it is  
not allowed.  The ENTIRE building must satisfy the allowance to use 13R.

To put it another way, 20 yrs from now when I'm retired and looking  
for something to occupy my feeble mind, the first court questions for  
those that have embraced mixing of systems will be something like:   
Now aren't portions of buildings protected per NFPA 13 expected to  
provide property protection which encompasses continuity of business.  
So you agree I see.  Now doesn't a 13R system primarily focus on life  
safety with a much lower level of property protection whereas if you  
burn the roof off but the people get out, it's a success (thus  
allowing the attic to be unprotected).  So you agree again.  Now Mr  
Consultant (because this IS an engineering decision) how is it that  
just because the second floor was residential, you didn't protect the  
attic and you put poor old commercial guy on the first floor out of  
business. Doesn't that conflict with the scope of 13?  So you agree it  
does (well actually I'm sure the defendant would swallow their tongue  
before acknowledging that).

In looking at the big picture, it's an easy evaluation.  Focus just on  
one code section though, and ambiguity rears its ugly head.

Roland




On Mar 13, 2009, at 12:51 PM, Ron Greenman wrote:

 Although I disagree with interpretation for horizontal fire barriers
 that Jamie refers to that has been typical in many jurisdictions out
 on the best coast. As others have mentioned typically the entire lower
 floor is commercial with 13/horizontal fire barrier/13R above.

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Mixed-Use Code Question

2009-03-13 Thread John Drucker
Jamie,

However 2006 IBC  2006 IFC provides;

[F] 903.2.7 Group R.
An automatic sprinkler system installed in accordance with Section 903.3
shall be PROVIDED THROUGHOUT all buildings with a Group R fire area.

Emphasis on throughout all buildings. 

Let's take a look at 2006 IBC 508, particularly Table 508.3.3 REQUIRED
SEPARATION OF OCCUPANCIES (HOURS) and the footnotes.

Footnote S=Buildings EQUIPPED THROUGHOUT with an automatic sprinkler system
installed in accordance with Section 903.3.1.1.

[F] 903.3.1.1 NFPA 13 sprinkler systems.
Where the provisions of this code require that a building or portion thereof
be EQUIPPED THROUGHOUT with an automatic sprinkler system in accordance with
this section, sprinklers shall be installed throughout in accordance with
NFPA 13 except as provided in Section 903.3.1.1.1.

And just for extra measure;

F] 903.3.1.2 NFPA 13R sprinkler systems.
Where ALLOWED in buildings of GROUP R, up to and including four stories in
height, automatic sprinkler systems shall be installed throughout in
accordance with NFPA 13R.


In summary mixed use buildings, even separated mixed use buildings require
NFPA-13 complaint systems throughout.

Hope that helps

Sincerely

John Drucker
Fire Protection Subcode Official
Building/Fire/Electrical Inspector

Safe Buildings Save Lives !

 


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jamie Seidl
Sent: Friday, March 13, 2009 3:57 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Mixed-Use Code Question

As always, I should have clarified...  I was looking at the North Carolina
IBC. Table 302.3.2 in the NCIBC (table 508.3.3 in the 2006 IBC) omitted the
(S) and (NS) designations for the required separation of occupancies. Which
basically means you don't necessarily have to stick to 903.3.1.1 for
sprinkler system type.  Thus in North Carolina, you can have a separated
mixed use building, I.E. group R above an S, B, M, ect... where the
sprinkler system only needs to meet the requirements for the occupancy as
long as you comply with the separation requirements.
So in NC, non separated mixed use... full 13. Separated mixed use, system
per occupancy classification as long as you haven't exceeded height, area,
open area, fire lane ect. limitations and the AHJ is ok with it.  When did
Dixie become so progressive?

John, I would agree whole heartedly that anything horizontal isn't termed a
wall.  It's a fire barrier.  I've gotten called out on the carpet for that
verbiage before :)
Jamie Seidl
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of John Drucker
Sent: Friday, March 13, 2009 2:35 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Mixed-Use Code Question

Careful on the IBC 509 provisions, i.e. so called horizontal
firewalls.

First and foremost anything horizontal isn't termed a wall. Second
firewalls must meet the criteria of being able to collapse on either
side, but not both, without effecting the opposite side. As Scotty once
said Captain I cant defy the laws of physics !  When the lower floor
goes, well I guess you know what happens next. So much for horizontal
firewalls and separate buildings created by them.

Lets take a closer look at 509, 509.2 to be exact.  Heres what it
says;

A basement and/or the first story above grade plane of a building shall
be considered as a separate and distinct building for the purpose of
determining area limitations, continuity of fire walls, limitation of
number of stories and type of construction.

The commentary hits the nail on the head; The subsections of Section
509 are EXCEPTIONS to the general HEIGHT AND AREA limitations of Chapter
5.  Nothing in there about exceptions for Chapter 9, Mixed Uses and
Sprinklers.

 In the end its still a mixed use building where an allowance for
height, area and construction type has been made for a 3 Hr horizontal
assembly. Back in the day we called this taxpayer buildings making good
use of available land, parking below, commercial/mercantile at grade and
residential above the first floor. The IBC merely accomodates this with
regards to building construction.

So in the end if its mixed its 13.

Hope that helps

John Drucker
Fire Protection Subcode Official





-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jamie
Seidl
Sent: Friday, March 13, 2009 1:28 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Mixed-Use Code Question

In IBC land, there is Separated and Non-separated mixed use. Non
separated, your entire building would be full 13.  In separated mixed
use, as long as the ratings meet the required separations or separate
buildings of the code, (including horizontal) you can use 13 for the
lower area and 13R for the upper.  There has been some contention on the
designation of a separate

RE: Mixed-Use Code Question

2009-03-13 Thread John Drucker
This is almost getting scary Huggins and Layton on the same page as an AHJ !
Yikes

Seriously I'm afraid that we have under protected buildings lurking, worse
some of them may have been built with construction type and separation
allowances under the assumption that compliant sprinkler systems were being
provided.

As a fire service member I am gravely concerned for the safety of
firefighters.

Sincerely

John Drucker
Active Firefighter
Fire Protection Subcode Official (AHJ)
Building/Fire/Electrical Inspector

Safe Buildings Save Lives !


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Roland
Huggins
Sent: Friday, March 13, 2009 4:52 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Mixed-Use Code Question

those have been lenient AHJ/BCO's.  Other than the previously  
discussed EXCEPTION (parking floor to other occupancies), the only way  
a single structure can be two or more buildings is separation by fire  
WALLS.  Walls in a horizontally orientation is called a collapsed  
building.

AS for dancing in the separated occupancy area, some will attempt to  
say that 508.3.3.1 allows each to be designed with total disregard for  
the other occupancy.  What it actual says is simply that each portion  
will be separately identified by its own occupancy.  IN order to apply  
a combination of 13 and 13R, you have to ignore that 903.3.1.2 that  
allows the use of 13R states Where allowed in BUILDINGS of Group R...  
shall be provided throughout.   IT doesn't say portions of buildings   
Now back in the confused past, I think 2003 but maybe older, the IBC  
did say portions of buildings within this section.  Because the older  
IBC was confusing, the 13R TC addressed this issue in the scope (and  
annex).  So in order to embrace the Separated approach, one also has  
to ignore the Scope of 13R.

Bottom line, without a local amendment allowing mixing systems, it is  
not allowed.  The ENTIRE building must satisfy the allowance to use 13R.

To put it another way, 20 yrs from now when I'm retired and looking  
for something to occupy my feeble mind, the first court questions for  
those that have embraced mixing of systems will be something like:   
Now aren't portions of buildings protected per NFPA 13 expected to  
provide property protection which encompasses continuity of business.  
So you agree I see.  Now doesn't a 13R system primarily focus on life  
safety with a much lower level of property protection whereas if you  
burn the roof off but the people get out, it's a success (thus  
allowing the attic to be unprotected).  So you agree again.  Now Mr  
Consultant (because this IS an engineering decision) how is it that  
just because the second floor was residential, you didn't protect the  
attic and you put poor old commercial guy on the first floor out of  
business. Doesn't that conflict with the scope of 13?  So you agree it  
does (well actually I'm sure the defendant would swallow their tongue  
before acknowledging that).

In looking at the big picture, it's an easy evaluation.  Focus just on  
one code section though, and ambiguity rears its ugly head.

Roland




On Mar 13, 2009, at 12:51 PM, Ron Greenman wrote:

 Although I disagree with interpretation for horizontal fire barriers
 that Jamie refers to that has been typical in many jurisdictions out
 on the best coast. As others have mentioned typically the entire lower
 floor is commercial with 13/horizontal fire barrier/13R above.

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Mixed-Use Code Question

2009-03-13 Thread Jamie Seidl
John, that was my point.  North Carolina has eliminated the S  NS designations 
in that chart. Thus placing the sprinkler protection requirements back to the 
occupancy classifications. So if the required separation is in place you can 
reduce the sprinkler protection back to the minimum required for the occupancy, 
once again as long as you haven't hit another trigger in the code for full 13.

I'm trying to remember where I've read it, but if it's sprinklered per NFPA 13R 
and the code allows NFPA 13R then it shall be considered to be sprinklered 
throughout. throughout doesn't necessarily mean everywhere, just where the 
standard requires it.

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of John Drucker
Sent: Friday, March 13, 2009 4:53 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Mixed-Use Code Question

Jamie,

However 2006 IBC  2006 IFC provides;

[F] 903.2.7 Group R.
An automatic sprinkler system installed in accordance with Section 903.3
shall be PROVIDED THROUGHOUT all buildings with a Group R fire area.

Emphasis on throughout all buildings.

Let's take a look at 2006 IBC 508, particularly Table 508.3.3 REQUIRED
SEPARATION OF OCCUPANCIES (HOURS) and the footnotes.

Footnote S=Buildings EQUIPPED THROUGHOUT with an automatic sprinkler system
installed in accordance with Section 903.3.1.1.

[F] 903.3.1.1 NFPA 13 sprinkler systems.
Where the provisions of this code require that a building or portion thereof
be EQUIPPED THROUGHOUT with an automatic sprinkler system in accordance with
this section, sprinklers shall be installed throughout in accordance with
NFPA 13 except as provided in Section 903.3.1.1.1.

And just for extra measure;

F] 903.3.1.2 NFPA 13R sprinkler systems.
Where ALLOWED in buildings of GROUP R, up to and including four stories in
height, automatic sprinkler systems shall be installed throughout in
accordance with NFPA 13R.


In summary mixed use buildings, even separated mixed use buildings require
NFPA-13 complaint systems throughout.

Hope that helps

Sincerely

John Drucker
Fire Protection Subcode Official
Building/Fire/Electrical Inspector

Safe Buildings Save Lives !




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jamie Seidl
Sent: Friday, March 13, 2009 3:57 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Mixed-Use Code Question

As always, I should have clarified...  I was looking at the North Carolina
IBC. Table 302.3.2 in the NCIBC (table 508.3.3 in the 2006 IBC) omitted the
(S) and (NS) designations for the required separation of occupancies. Which
basically means you don't necessarily have to stick to 903.3.1.1 for
sprinkler system type.  Thus in North Carolina, you can have a separated
mixed use building, I.E. group R above an S, B, M, ect... where the
sprinkler system only needs to meet the requirements for the occupancy as
long as you comply with the separation requirements.
So in NC, non separated mixed use... full 13. Separated mixed use, system
per occupancy classification as long as you haven't exceeded height, area,
open area, fire lane ect. limitations and the AHJ is ok with it.  When did
Dixie become so progressive?

John, I would agree whole heartedly that anything horizontal isn't termed a
wall.  It's a fire barrier.  I've gotten called out on the carpet for that
verbiage before :)
Jamie Seidl
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of John Drucker
Sent: Friday, March 13, 2009 2:35 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Mixed-Use Code Question

Careful on the IBC 509 provisions, i.e. so called horizontal
firewalls.

First and foremost anything horizontal isn't termed a wall. Second
firewalls must meet the criteria of being able to collapse on either
side, but not both, without effecting the opposite side. As Scotty once
said Captain I cant defy the laws of physics !  When the lower floor
goes, well I guess you know what happens next. So much for horizontal
firewalls and separate buildings created by them.

Lets take a closer look at 509, 509.2 to be exact.  Heres what it
says;

A basement and/or the first story above grade plane of a building shall
be considered as a separate and distinct building for the purpose of
determining area limitations, continuity of fire walls, limitation of
number of stories and type of construction.

The commentary hits the nail on the head; The subsections of Section
509 are EXCEPTIONS to the general HEIGHT AND AREA limitations of Chapter
5.  Nothing in there about exceptions for Chapter 9, Mixed Uses and
Sprinklers.

 In the end its still a mixed use building where an allowance for
height, area and construction type has been made for a 3 Hr horizontal
assembly. Back in the day we called this taxpayer buildings making good
use

RE: Mixed-Use Code Question

2009-03-13 Thread Steve Leyton
I agree with you, and the TC on Residential Sprinkler Systems has adopted 
language for Chapter 1 of 13R that is intended to finally clarify the 
appropriate application of the standard.   If ratified at the code hearing, the 
standard will be applicable buildings of residential occupancy and their 
accessory non-residential uses only; the only way that a single structure would 
have sprinkler systems designed to different standards is if it is 
fire-separated to the extent that the areas are considered separate buildings 
in accordance with the building code for that construction type.  These 
separations may be horizontal and/or vertical.
 
I've tried to transcribe Log #21, proposal 13R-2 below:

Revise the scope of NFPA 13R to read: 

1.1* Scope. This standard shall cover the design and installation of automatic 
sprinkler systems for protection against fire hazards in residential buildings 
up to and including four stories in height.

Revise A.1.1 as amended by Proposal 13R-58, Proposal 13R-57,  Proposal 13R-56, 
to read as follows: 

A.1.1 NFPA 13R is appropriate for use only in buildings that are entirely 
residential occupancies up to and including four stories in height. Residential 
occupancies are defined in this standard.  The height of the building is as 
defined in the applicable building code. It is the intent of this standard that 
if NFPA 13R is appropriate for use, that it be used throughout the entire 
building. It is recognized that incidental and accessory areas, as defined by 
the applicable building code, might exist within that residential occupancy. 
Such incidental and
accessory areas would typically be considered by the applicable building code 
to be part of the residential occupancy and subject to the requirements for the 
residential occupancy by.  Where buildings are greater than four stories in 
height, or where buildings are of mixed use, such buildings should be protected 
throughout with NFPA 13.  Where structures of mixed use can be totally 
separated so that a residential occupancy is considered a separate building 
under the applicable building code, NFPA 13R can be used in the building of 
entirely residential occupancy while NFPA 13 is used in the other building(s).  
(Examples of incidental and accessory occupancies found in residential 
occupancies can include: management offices,
private parking garages/areas within a dwelling unit, community laundry rooms, 
clubhouses, exercise facilities, tenant
storage within a dwelling unit, etc.).

Note, a separated mixed use structure (separated by fire-resistance rated 
assemblies) is not the same as a structure with separate buildings (separated 
by fire walls). However, there may be applicable building code provisions that 
permit upper and lower portions of a structure, separated by a three hour fire 
rated horizontal assembly, to be considered as separate buildings for certain 
purposes (See 2006 NFPA 5000, Section 7.4.3.6.5 and 2006 IBC Section 509.2).


Steve Leyton
Protection Design  Consulting
San Diego, CA


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman
Sent: Friday, March 13, 2009 12:51 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Mixed-Use Code Question

Although I disagree with interpretation for horizontal fire barriers
that Jamie refers to that has been typical in many jurisdictions out
on the best coast. As others have mentioned typically the entire lower
floor is commercial with 13/horizontal fire barrier/13R above.

On Fri, Mar 13, 2009 at 10:27 AM, Jamie Seidl jse...@affordablefire.com wrote:
 In IBC land, there is Separated and Non-separated mixed use. Non separated, 
 your entire building would be full 13.  In separated mixed use, as long as 
 the ratings meet the required separations or separate buildings of the 
 code, (including horizontal) you can use 13 for the lower area and 13R for 
 the upper.  There has been some contention on the designation of a separate 
 building and a horizontal fire barrier, but this configuration has met the 
 intent of the code in the jurisdictions I've dealt with.
 Jamie Seidl

 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org 
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Tom Duross
 Sent: Friday, March 13, 2009 12:23 PM
 To: sprinklerforum@firesprinkler.org
 Subject: Mixed-Use Code Question

 I have a question about a small project I'm bidding and how it relates to
 other's building codes.
 Four storey 8 unit residential building, in bid stage, just got notification
 that one unit, half the ground floor, will be zoned for commercial use.
 I'm at odds if this changes the building to mixed-use or not.  I've asked
 the gc if he's still applying as an R2 and he's not sure, architect in on
 vacation (go figure).  I'm leafing through our building code (ICC-03) right
 now to see if this qualifies as ancillary

RE: Mixed-Use Code Question

2009-03-13 Thread John Drucker
Steve,

As you pointed out, for certain purposes. 509.2 stipulates the purposes;

509.2 Group S-2 enclosed or open parking garage with Group A, B, M, R or S
above.

A basement and/or the first story above grade plane of a building shall be
considered AS A SEPARATE AND DISTINCT BUIDLING FOR THE PURPOSE OF
determining AREA LIMITATIONS, CONTINUITY OF FIRE WALLS, LIMITATION OF NUMBER
OF STORIES and TYPE OF CONSTRUCTION when all of the following conditions are
met;

IBC 509.2 does not state for the purpose of occupancy classification, thus
it is still a mixed use building. Only two things separate structures into
wholly separate buildings 1) Fire Walls, 2) Distance.

With that said 903.3.1.2 is clear; 

[F] 903.3.1.2 NFPA 13R sprinkler systems.
WHERE ALLOWED in BUILDINGS of GROUP R, up to and including four stories in
height, automatic sprinkler systems shall be installed throughout in
accordance with NFPA 13R.

What we are speaking of is Buildings of Group R and something else other
than an incidental use.

The proposed scope of 13R makes it clear that 13R is not for mixed use
buildings;

1.1* Scope. This standard shall cover the design and installation of
automatic sprinkler systems for protection against fire hazards in
residential buildings up to and including four stories in height.

If the intent is to allow 13R systems in the residential portions of a mixed
use building, whether a 508 or 509, then the IBC needs to be amended
accordingly. 

Sincerely

John Drucker
Fire Protection Subcode Official
Building/Fire/Electrical Inspector

Safe Buildings Save Lives !


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Steve Leyton
Sent: Friday, March 13, 2009 5:12 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Mixed-Use Code Question

I agree with you, and the TC on Residential Sprinkler Systems has adopted
language for Chapter 1 of 13R that is intended to finally clarify the
appropriate application of the standard.   If ratified at the code hearing,
the standard will be applicable buildings of residential occupancy and their
accessory non-residential uses only; the only way that a single structure
would have sprinkler systems designed to different standards is if it is
fire-separated to the extent that the areas are considered separate
buildings in accordance with the building code for that construction type.
These separations may be horizontal and/or vertical.
 
I've tried to transcribe Log #21, proposal 13R-2 below:

Revise the scope of NFPA 13R to read: 

1.1* Scope. This standard shall cover the design and installation of
automatic sprinkler systems for protection against fire hazards in
residential buildings up to and including four stories in height.

Revise A.1.1 as amended by Proposal 13R-58, Proposal 13R-57,  Proposal
13R-56, to read as follows: 

A.1.1 NFPA 13R is appropriate for use only in buildings that are entirely
residential occupancies up to and including four stories in height.
Residential occupancies are defined in this standard.  The height of the
building is as defined in the applicable building code. It is the intent of
this standard that if NFPA 13R is appropriate for use, that it be used
throughout the entire building. It is recognized that incidental and
accessory areas, as defined by the applicable building code, might exist
within that residential occupancy. Such incidental and
accessory areas would typically be considered by the applicable building
code to be part of the residential occupancy and subject to the requirements
for the residential occupancy by.  Where buildings are greater than four
stories in height, or where buildings are of mixed use, such buildings
should be protected throughout with NFPA 13.  Where structures of mixed use
can be totally separated so that a residential occupancy is considered a
separate building under the applicable building code, NFPA 13R can be used
in the building of entirely residential occupancy while NFPA 13 is used in
the other building(s).  (Examples of incidental and accessory occupancies
found in residential occupancies can include: management offices,
private parking garages/areas within a dwelling unit, community laundry
rooms, clubhouses, exercise facilities, tenant
storage within a dwelling unit, etc.).

Note, a separated mixed use structure (separated by fire-resistance rated
assemblies) is not the same as a structure with separate buildings
(separated by fire walls). However, there may be applicable building code
provisions that permit upper and lower portions of a structure, separated by
a three hour fire rated horizontal assembly, to be considered as separate
buildings for certain purposes (See 2006 NFPA 5000, Section 7.4.3.6.5 and
2006 IBC Section 509.2).


Steve Leyton
Protection Design  Consulting
San Diego, CA


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org

Re: Mixed-Use Code Question

2009-03-13 Thread Ron Greenman
Cut to the chase. 13R exists solely to get sprinklers into buildings
of residential construction where the hazard is not too great (four
stories and less) at a cost that made it attractive to do, a
compromise if you will, back in the days when sprinklers were only in
commercial buildings and sprinklering cracker-box apartments, migrant
labor dormitories and cheap hotels was,to coin an NAHB phrase, too
expensive. Well, it's done its job and it's high time we just bid it
a fond farewell and sprinkler all Rs (except SFDs of course because
they're mostly protected by fire alarms anyways) to 13.

On Fri, Mar 13, 2009 at 2:34 PM, John Drucker john.druc...@verizon.net wrote:
 Steve,

 As you pointed out, for certain purposes. 509.2 stipulates the purposes;

 509.2 Group S-2 enclosed or open parking garage with Group A, B, M, R or S
 above.

 A basement and/or the first story above grade plane of a building shall be
 considered AS A SEPARATE AND DISTINCT BUIDLING FOR THE PURPOSE OF
 determining AREA LIMITATIONS, CONTINUITY OF FIRE WALLS, LIMITATION OF NUMBER
 OF STORIES and TYPE OF CONSTRUCTION when all of the following conditions are
 met;

 IBC 509.2 does not state for the purpose of occupancy classification, thus
 it is still a mixed use building. Only two things separate structures into
 wholly separate buildings 1) Fire Walls, 2) Distance.

 With that said 903.3.1.2 is clear;

 [F] 903.3.1.2 NFPA 13R sprinkler systems.
 WHERE ALLOWED in BUILDINGS of GROUP R, up to and including four stories in
 height, automatic sprinkler systems shall be installed throughout in
 accordance with NFPA 13R.

 What we are speaking of is Buildings of Group R and something else other
 than an incidental use.

 The proposed scope of 13R makes it clear that 13R is not for mixed use
 buildings;

 1.1* Scope. This standard shall cover the design and installation of
 automatic sprinkler systems for protection against fire hazards in
 residential buildings up to and including four stories in height.

 If the intent is to allow 13R systems in the residential portions of a mixed
 use building, whether a 508 or 509, then the IBC needs to be amended
 accordingly.

 Sincerely

 John Drucker
 Fire Protection Subcode Official
 Building/Fire/Electrical Inspector

 Safe Buildings Save Lives !


 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Steve Leyton
 Sent: Friday, March 13, 2009 5:12 PM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: Mixed-Use Code Question

 I agree with you, and the TC on Residential Sprinkler Systems has adopted
 language for Chapter 1 of 13R that is intended to finally clarify the
 appropriate application of the standard.   If ratified at the code hearing,
 the standard will be applicable buildings of residential occupancy and their
 accessory non-residential uses only; the only way that a single structure
 would have sprinkler systems designed to different standards is if it is
 fire-separated to the extent that the areas are considered separate
 buildings in accordance with the building code for that construction type.
 These separations may be horizontal and/or vertical.

 I've tried to transcribe Log #21, proposal 13R-2 below:

 Revise the scope of NFPA 13R to read:

 1.1* Scope. This standard shall cover the design and installation of
 automatic sprinkler systems for protection against fire hazards in
 residential buildings up to and including four stories in height.

 Revise A.1.1 as amended by Proposal 13R-58, Proposal 13R-57,  Proposal
 13R-56, to read as follows:

 A.1.1 NFPA 13R is appropriate for use only in buildings that are entirely
 residential occupancies up to and including four stories in height.
 Residential occupancies are defined in this standard.  The height of the
 building is as defined in the applicable building code. It is the intent of
 this standard that if NFPA 13R is appropriate for use, that it be used
 throughout the entire building. It is recognized that incidental and
 accessory areas, as defined by the applicable building code, might exist
 within that residential occupancy. Such incidental and
 accessory areas would typically be considered by the applicable building
 code to be part of the residential occupancy and subject to the requirements
 for the residential occupancy by.  Where buildings are greater than four
 stories in height, or where buildings are of mixed use, such buildings
 should be protected throughout with NFPA 13.  Where structures of mixed use
 can be totally separated so that a residential occupancy is considered a
 separate building under the applicable building code, NFPA 13R can be used
 in the building of entirely residential occupancy while NFPA 13 is used in
 the other building(s).  (Examples of incidental and accessory occupancies
 found in residential occupancies can include: management offices,
 private parking garages/areas within a dwelling unit, community