RE: EQ Bracing

2013-12-11 Thread Byron Weisz
Here on the left coast we are required to earthquake brace so when the building falls down the fire sprinkler system will still be in the air and fully operational. Byron Weisz Cen-Cal Fire Systems, Inc. 1615 So. Stockton St. Lodi, CA. 95240 Ph. (209) 334-9119 Fax (209) 334-2923 by

RE: Sloped Roof in ESFR system

2017-05-10 Thread Byron Weisz
I guess just me but I would never design an unused attic space above a 30’-0 flat ceiling to Light Hazard. Especially in a warehouse where there is going to be rack storage below. [ccfs_LOGO (2)] Byron Weisz Cen-Cal Fire Systems, Inc. P.O. Box 1284 Lodi, CA 95241 Phone (209) 334-9119 Fax

RE: Fabric ventilation ducts

2017-08-11 Thread Byron Weisz
Our experience with fabric - retraceable ducts is that the same obstruction rules apply as hard duct, especially when dealing with ESFR sprinklers [ccfs_LOGO (2)] Byron Weisz Cen-Cal Fire Systems, Inc. P.O. Box 1284 Lodi, CA 95241 Phone (209) 334-9119 Fax (209) 334-2923 by...@cen

[Sprinklerforum] Re: [EXTERNAL] Re: Velocity - Rant

2022-03-15 Thread Byron Weisz
sense at all is to take “doctored” water flow information and use that information to size a fire pump to design an ESFR fire sprinkler system. Again, the best person to answer the questions of velocity and safety margin in the design of a fire sprinkler system gracefully would be Bob. Byron

RE: NFPA 13 & FM Mix

2015-02-12 Thread Byron Weisz
have read this commentary and have interesting interpretations that we are working through. Thanks, Byron Weisz Cen-Cal Fire Systems, Inc. 1615 So. Stockton St. Lodi, CA. 95240 Ph. (209) 334-9119 Fax (209) 334-2923 by...@cen-calfire.com This message is intended only for the use of

RE: Dry valve response time calculation

2016-01-13 Thread Byron Weisz
We have had good look with it as well. Even better when the piping installed up to the Inspector's Test Valve is run the same size as the branch line. Byron Weisz   Cen-Cal Fire Systems, Inc. 1615 So. Stockton St. Lodi, CA. 95240 Ph.   (209) 334-9119 Fax   (209) 334-2923 by...@cen-calfir

RE: RV Storage

2021-01-08 Thread Byron Weisz via Sprinklerforum
Multiple Projects - Extra Hazard Group II Byron Weisz Cen-Cal Fire Systems, Inc. P.O. Box 1284 Lodi,  CA   95241 Phone (209)  334-9119 Fax (209)  334-2923 by...@cen-calfire.com   This and any attached documents are for the use of the intended recipient(s) only and may contain information

RE: [EXTERNAL] Fire Pump Sprk & Fire Flow Demand

2021-04-23 Thread Byron Weisz via Sprinklerforum
simply up to the local AHJ? Byron Weisz Cen-Cal Fire Systems, Inc. P.O. Box 1284 Lodi,  CA   95241 Phone (209)  334-9119 Fax (209)  334-2923 by...@cen-calfire.com   This and any attached documents are for the use of the intended recipient(s) only and may contain information that is privileged

Bushings

2008-09-16 Thread Byron Weisz - Cen-Cal Fire Systems
tuation or not. What do the troops think? Byron Weisz Cen-Cal Fire Systems, Inc. 11780 N. Hwy 99 Lodi, CA. 95240 Ph. (209) 334-9119 Fax (209) 334-2923 [EMAIL PROTECTED] ___ Sprinklerforum mailing list http://lists.firesprinkler.org/ma

RE: [Sprinklerforum] What'ds up with the forum?

2009-08-25 Thread Byron Weisz - Cen-Cal Fire Systems
Please remove my name from the lists and get me back to where I was yesterday. Byron Weisz Cen-Cal Fire Systems, Inc. 11780 N. Hwy 99 Lodi, CA. 95240 Ph. (209) 334-9119 Fax (209) 334-2923 by...@cen-calfire.com This message is intended only for the use of the individual or

RE: Draft curtain

2012-09-20 Thread Byron Weisz - Cen-Cal Fire Systems
That is a Building Code issue Byron Weisz Cen-Cal Fire Systems, Inc. 1615 So. Stockton St. Lodi, CA. 95240 Ph. (209) 334-9119 Fax (209) 334-2923 by...@cen-calfire.com This message is intended only for the use of the individual or entity to which it is addressed and may contain

RE: Brewery Occupancy Classification

2013-04-26 Thread Byron Weisz - Cen-Cal Fire Systems
should be. Byron Weisz Cen-Cal Fire Systems, Inc. 1615 So. Stockton St. Lodi, CA. 95240 Ph. (209) 334-9119 Fax (209) 334-2923 by...@cen-calfire.com This message is intended only for the use of the individual or entity to which it is addressed and may contain information that is privileged

RE: Ordinary Hazard Attic

2011-09-08 Thread Byron Weisz - Cen-Cal Fire Systems
There may be cost implications but the owner of the property should ultimately have the opportunity to decide how his issue with the fire lane will be handled. Byron Weisz Cen-Cal Fire Systems, Inc. 1615 So. Stockton St. Lodi, CA. 95240 Ph. (209) 334-9119 Fax (209) 334-2923 by...@cen-calfire.

RE: Pump supplying water storage tanks

2011-10-07 Thread Byron Weisz - Cen-Cal Fire Systems
are not part of the fire protection system. The valve which maintains the level of water in the tank should be listed. Byron Weisz Cen-Cal Fire Systems, Inc. 1615 So. Stockton St. Lodi, CA. 95240 Ph. (209) 334-9119 Fax (209) 334-2923 by...@cen-calfire.com This message is intended only for

water supplies

2012-02-23 Thread Byron Weisz - Cen-Cal Fire Systems
s'. I went through the responses in the achieves and I am not really finding where the question was answered one way or the other. Thanks Byron Weisz Cen-Cal Fire Systems, Inc. 1615 So. Stockton St. Lodi, CA. 95240 Ph. (209) 334-9119 Fax (209) 334-2923 by...@cen-calfi