Amen. Our industry needs more folks that would rather do it right than
trying to cut corners.
Good job Greg!
Cliff
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of David de
Vries/Firetech
Sent: Monday, January 08, 2007 9:30 AM
To: sprinklerforum@firesprin
I think it was 32 fps for NFPA 13 and 20 fps for FM. But as Rod noted, it
was taken out of the standard a couple of revisions back. I believe they
determined thru modeling that it actually did not affect the sprinkler
system operation.
Roland or Scott Mitchell could probably discuss this more
Tony,
Wouldn't 8.14.6 (2002) require that this area be sprinklered? Unless I am
missing something in your description of the area.
Cliff
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of A.P.Silva
Sent: Friday, January 26, 2007 8:25 AM
To: sprinklerforum@
That's only if it serves two or more fire divisions. Not always the case
just because it is a multi-story building. Check out the info in the
handbook on this.
Cliff Whitfield, SET
Fire Design, Inc
.-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf O
Mike,
If you have to do a 13 system, you can use the "dwelling unit" design. That
may help some. What about the attic? Do you have to sprinkler it?
Cliff Whitfield, SET
Fire Design, Inc.
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf
d not a spy for
NAHB.
Cliff Whitfield
Fire Design, Inc.
3784 Holly Ridge Trail
Marianna, FL 32448
Phone: 850-526-1886
Fax: 850-526-1884
Cell: 850-557-1886
www.fire-design.com-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum
Check your email. I just sent one that I had scanned a while back.
Hope it helps.
Cliff Whitfield,
Fire Design, Inc.
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Craig Small
Sent: Tuesday, February 10
I think if you look in Webster's, they are synonyms and it is proper to
substitute them for one another.
Cliff
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Steve Leyton
Sent: Thursday, February 26, 2009 11:
George,
It is already Friday somewhere, I'm just not smart enough to figure out the
time zones. So go ahead and have a beer and relax. Get a group hug if you
can.
Cliff
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] O
), but
excludes elevator machine rooms and other rooms that do not contain
fuel-fired equipment (2007- 6.9.6). I have always put heads in water
heater closets but are they actually required per NFPA 13R?
Thanks,
Cliff Whitfield, SET
President
Fire Design, Inc.
cl...@fire-design.com
www.
heater closets but are they actually required per NFPA 13R?
>
>
>
>Thanks,
>
>
>
>Cliff Whitfield, SET
>
>President
>
>Fire Design, Inc.
>
>
>
>cl...@fire-design.com
>
>www.fire-design.com
>
>
>
>
>
>_
gt;excludes elevator machine rooms and other rooms that do not contain
> >fuel-fired equipment (2007- 6.9.6). I have always put heads in water
> >heater closets but are they actually required per NFPA 13R?
> >
> >
> >
> >Thanks,
> >
> >
> >
> >Clif
Nick,
Send me your drawing off-forum and let me see if I can help. It's hard to
know exactly what you are describing without seeing it and you can't put an
attachment on the forum.
Cliff Whitfield, SET
Fire Design, Inc.
cl...@fire-design.com
www.fire-design.com
-Origin
#x27; away from the center line of the heads (away
from the water curtain) even in an ordinary hazard occupancy. But window
heads appear to me a directional spray specialty head and it seems to me
that the standard coverage heads would need to spray to the center line of
the window head.
Any though
though I don't think you have to worry about cold soldering from the
ceiling sprinklers either.
Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ 85024
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Cliff
Whitfield
Sent: Saturday, March 21, 2009 7:20 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Window Sprinklers
Ron,
That's what I was thinking. I just don't see any way around it.
Their data shee
Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel: 970-879-7952
Fax: 970-879-7926
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Cliff
Whitfield
Sent: Saturday, March 21, 2009 11:58 AM
To: sprinkler
you would if they
were separated by 100 ft. It is a completely different standpipe as far as
the code is concerned.
Cliff Whitfield, SET
President
Fire Design, Inc.
cl...@fire-design.com
www.fire-design.com
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:spri
ifficult and
challenging designs to keep the easier stuff for their in-house people.
Cliff Whitfield, SET
President
Fire Design, Inc.
cl...@fire-design.com
www.fire-design.com
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprink
e the mezz.
I meet the requirements for roof level protection with ESFR heads table d.
The question is what needs to be done below the mezzanine?
Thanks all.
Keith Pepin
Thanks,
Cliff Whitfield, SET
President
Fire Design, Inc.
cl...@fire-design.com
www.fire-
Art,
If the rooms are not considered "dwelling units" you can use a dry system,
you just have to use QR heads. If it is truly a nursing home the rooms
should be "patient rooms" and not "dwelling units". Then it is not really
different than a hospital.
Cliff Whitfi
other good choice.
That way you can use residential heads in the dwelling units.
Cliff Whitfield, SET
President
Fire Design, Inc.
cl...@fire-design.com
www.fire-design.com
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On
A.5.3.1 - 2007 ed Ordinary Group I
Cliff
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Charles
Thurston
Sent: Wednesday, July 28, 2010 8:53 AM
To: sprinklerforum
Subject: Commercial Laundry
Hello sprinkle
Has anyone heard if we will have a get-together for the 'forumites' at this
year's convention? It's been several years now since we've had it but I
think Dr. Muncy said it could happen again this year. It would be nice to
see everyone again.
Cliff Whitfield, SET
Presid
Brian,
That's one of the things you have to take into consideration. You can often
times pay for larger pipe easier than paying for K25's. You just have to
run the numbers both ways to make the right decision. There are usually
several things to factor into the process. Pipe, fittings, hangers
I agree whole-heartedly with Travis. It is so obvious that AFSA is more
concerned with training and helping out the industry than they are trying to
make $$ or they would not make the membership fees so affordable for
designers and design firms. Even in the tough times we are currently
experienci
Brian,
I believe It's for design firms/ companies or individuals that work
independently of sprinkler companies. If I understand it correctly if you
work as an employee of a sprinkler contractor your company has to become a
contractor member, not the individual designer as a designer member, but
And Vegas has never been the same since he left!
Cliff
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman
Sent: Wednesday, October 06, 2010 1:54 PM
To: sprinklerforum@firesprinkler.org; bcasterl...@f
Jamie,
Before I started using the AutoSprink software, I would climb up in the
attic of my house and look at the structure. I had a tough time visualizing
some of these complex roof structures and at least I had a hip roof on the
house that I could study. Then I would go out in the newest subdiv
Todd,
Contact me off-forum. I may be able to help. cl...@fire-design.com
Cliff
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd Williams
Sent: Monday, October 18, 2010 10:51 AM
To: sprinklerforum@fires
Todd,
I believe the obstruction rules apply to a sloped roof since the sprinkler
deflector has to be parallel to the slope of the roof anyway. I also
believe that the intent of the code is that the overhang you have described
would meet the criteria of 8.15.7.1 since it is less than 4'. To me it
Brian,
I believe that 2½" hose valves are pretty much governed by NFPA 14. You
might look there for some guidance.
Cliff
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brian Harris
Sent: Wednesday, October
1:18 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: 1-1/2" & 2-1/2" Hose Connections
Cliff-
Thanks, will do.
Brian Harris
FDFP Inc.
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Cl
Todd,
If this is residential, 6.8.1.5.3.1 specifically addresses this concern.
2007 ed.
Cliff
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd Williams
Sent: Monday, November 01, 2010 1:22 PM
To: sprinkle
Todd,
I understand that you are using 2002 but I still believe a credible argument
exists in presenting the info from 2007. The heads that are approved for
this condition are no different than the heads that you have installed.
Besides the section I already gave you (6.8.1.5.3.1) there is anothe
Thom
Congrats!! It makes you feel good don't it?
Cliff
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom
Sent: Saturday, November 06, 2010 11:46 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Anot
ft exposed even after spaces are
finished.
Thanks,
Cliff Whitfield, SET
President
Fire Design, Inc.
850-526-1886
cl...@fire-design.com
www.fire-design.com
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firespr
forum-boun...@firesprinkler.org] On Behalf Of Cliff
Whitfield
Sent: Monday, November 08, 2010 9:06 AM
To: sprinklerforum@firesprinkler.org
Subject: CPVC question
Hi folks
Can CPVC be installed exposed in a light hazard occupancy with 'pan
type'
construction?
Just for the record, I am n
ty sure than pan
slab or metal deck is okay, but you'll have to get it from the
manufacturer.
SML
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Cliff
Whitfield
Sent: Monday, November 08, 2010 9:23 AM
T
:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Cliff
Whitfield
Sent: Monday, November 08, 2010 9:06 AM
To: sprinklerforum@firesprinkler.org
Subject: CPVC question
Hi folks
Can CPVC be installed exposed in a light hazard occupancy with 'pan
type'
construction?
Just for the record, I am
ow what is your opinion?
Thanks,
Cliff Whitfield, SET
President
Fire Design, Inc.
850-526-1886
cl...@fire-design.com
www.fire-design.com
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailma
resprinkler.org
Subject: Re: Seismic Question
Define "blast protection."
On Wed, Nov 10, 2010 at 2:58 PM, Cliff Whitfield
wrote:
> I have an unusual situation on a project and would like some opinions.
>
> We are currently doing a project where seismic bracing has been spec
straining straps required to be installed on the beam clamps?
>
>Now before you answer, consider this - NFPA 13 2007 - 9.3.7.1 - C-type
>clamps ... used to attach hangers to the building structure IN AREAS
SUBJECT
>TO EARTHQUAKES shall be equipped with a retraining strap.
>
>Ok
Todd,
I've seen this done in the past. In fact, there are a lot of times when
it's done by the water purveyors during a tap on the main underground line.
Not sure of a specific code reference. If common sense is an option you can
point to NFPA 20 that allows a smaller size supply to feed a fire
ce he figures
you're the contractor and should be all knowing in this matter.
Geez
Craig Prahl
CH2MHILL/SPB
864-599-4102
From: sprinklerforum-boun...@firesprinkler.org
[sprinklerforum-boun...@firesprinkler.org] On Behalf Of Clif
Thom,
You hit the nail on the head except it is not Mission Critical. I like your
idea about the structural seismic calcs. I'll use that on the next one if
there is one.
Thanks,
Cliff
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@fires
Ken,
Who wants to do math when I can look at a graph? And Brad, you need to get
a life if you go home thinking about calculations and such! :) Take up
fishing or hunting or something relaxing.
Cliff
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforu
Bob,
With most of the software today peaking is just a push of the button. If
you don't shift your remote area to the next head how are you 100% sure that
what you have calculated is the most demanding? Common sense would seem to
say that what you have is the most demanding but I would not submi
Bob,
I'm not sure on this so let's see what others say but I would think that if
11.2.3.1.4 (4) (d) was acceptable with solid wood joists spaces not
exceeding 160 cu.ft. that it should be acceptable with steel beams (purlins)
as you have described. That looks to me like the only exception that ma
Duane,
I don't think so. You would need to defer to the sprinkler manufacturer's
listing to be sure.
Cliff
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Dewayne
Martinez
Sent: Wednesday, December 01, 2010
Greg,
Todd uses AutoSprink. You should just shoot him a copy of the area. He
might be better able to see it and give you an opinion.
Cliff
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Greg McGahan
Sent:
there and I'm not
sure some of them understand seismic very well either.
Maybe Ken W will chime in here. He is the grand pooba of sway!
Cliff Whitfield, SET
Fire Design, Inc.
3784 Holly Ridge Trail
Marianna, FL 32448
Phone: 850-526-1886
Fax: 850-526-1884
Cell: 850-557-1886
www.
Roland,
I agree with your assessment. A floor does not constitute a 'system' in my
opinion. One system can supply a 10-story building. If not, why would a
mezzanine not be included in the sq. footage of a 'system'?
Cliff
-Original Message-
From: sprinklerforum-boun...@firesprinkler.o
David,
My understanding is that any pump installed for the purposes of fire
protection for 13R has the same requirements as for 13 so it has to be per
NFPA 20. Only in 13D can a 'pump' not be listed for fire protection per 20.
Cliff
-Original Message-
From: sprinklerforum-boun...@fires
Greg,
I believe there is a definite difference in a combustible concealed space
and what you have described here. I would consider this an attic or a
storage room but not a CCS.
Cliff
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesp
Folks,
Here is a link to an excellent article from the PME eNewsletter 2/3/11. I
wish more PEs felt this way.
http://www.pmengineer.com/Articles/Ballanco/2011/01/01/The-Engineering-Dilem
ma
Cliff Whitfield, SET
President
Fire Design, Inc.
cl...@fire-design.com
www.fire-design.com
Craig,
My guess is 'Commissioning'.
Cliff Whitfield, SET
President
Fire Design, Inc.
3784 Holly Ridge Trail
Marianna, FL 32448
Ph: 850-526-1886
Fx: 850-526-1884
cl...@fire-design.com
www.fire-design.com
-Original Message-
From: sprinklerforum-boun...@firespr
Brian,
This text is clearly under the subsection 8.4.7 for "Large Drop Sprinklers".
If your AHJ can't clearly see that you may have a problem unless you can get
someone in his office to explain how to read a standard.
Cliff
-Original Message-
From: sprinklerforum-boun...@firesprinkler.o
George,
You are showing your age on this one! I doubt many of these guys will have
a clue what your reply means!
Cliff
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church
Sent: Monday, March 07,
n the
specs or drawings that you need to put sprinklers up there? If you put them
in your bid, you miss the job. If you leave them out like most folks do,
you have to eat them because, unlike your competitors, you are supposed to
know that it was wrong and do it anyway!
Cliff Whitfield, SET
Pres
esprinkler.org] On Behalf Of Cliff
Whitfield
Sent: Thursday, March 10, 2011 8:41 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: top five list
Along with what Greg says, if we could ever get this actually done correctly
it would make everyone's life much easier when it comes to bidding a
Unless something has changed that I'm not aware of, the measurement is not
from the eave (outside edge of the fascia) but from the point where the
trusses set on the structure/wall. Many times on wood attics the trusses
actually hang over 16" to 24" but they edge is not where the 5' begins.
Look c
Nick,
It has always been my belief that unless there was some reason to remove an
existing system, I always leave it in place. Naturally there are some
instances that would require removal but many times they are fine left in
place.If you leave them, this owner may one day sell the bldg and
Chris,
You got my curiosity up on this one. Can you explain a little further?
Cliff
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Chris Cahill
Sent: Wednesday, August 05, 2009 1:58 PM
To: sprinklerforum@fi
J,
I think the big issue with non-metallic piping would be if it will meet code
from a building code standpoint. There are some cases where plastic is not
acceptable in an exposed condition. Check with your local plumbing and/or
building inspector.
Cliff Whitfield, SET
Fire Design, Inc.
cl
I don't think they were 'required' until sometime (I think '96) when they
took the pipe schedule option out of the standard (for all intents and
purposes). Until then, calcs were allowed but not required since the pipe
schedule system was still an option. .
Cliff
-Original Message---
he 50 psi caveat for systems greater than 5,000 sf kills the use
of pipe schedule? I ask since many inaccurately believe that PS is
not ALLOWED beyond 5,000 SF.
Roland
On Aug 26, 2009, at 7:05 PM, Cliff Whitfield wrote:
> I don't think they were 'required' until sometime
realize this, so I think you were just fishing
for a rise from one of us freelance guys:)
Cliff Whitfield, SET
Fire Design, Inc.
3784 Holly Ridge Trail
Marianna, FL 32448
Phone: 850-526-1886
Fax: 850-526-1884
Cell: 850-557-1886
www.fire-design.com
-Original Message-
From:
Richard,
Depending on your occupancy, you will probably be better off with EC heads
throughout. Assuming you are working with light hazard since you mentioned
spacing a standard head at 14 x 14, you will need 19.6 psi for your flow on
these heads so you may be better off by using EC heads. You j
te to be in a courtroom one day
and try to convince a judge or jury that this really was a 'room'. It's not
worth saving a head or two for me or my clients.
Cliff Whitfield, SET
President
Fire Design, Inc.
cl...@fire-design.com
www.fire-design.com
-
-
Todd,
Would this not fall under 8.15.6 "Spaces under Ground Floors, Exterior
Docks, and Platforms"? If it met all of the requirements I would think you
could exclude heads under the platform. Don't forget to apply the 3000 sf
remote area if you elect to not sprinkler that
of wiring under them. I didn't consider
using 8.15.6, due to the wiring and access panels.
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
j...@inlandfireprotection.com
-Original Message-
From:
Geoff,
Most of the trash chute rooms that I have seen in this type scenario is
unheated. You may want to verify before you go too far on this.
I agree with the other guys about the manual dry standpipe. Since this is
not a high rise you should be okay with it.
Cliff Whitfield, SET
Fire
George,
Somehow I failed to meet Ron. When I saw the post yesterday I couldn't
believe I had missed him but based on his comments I'll see him next year in
Providence. I understand that there may even be a "forum get together" like
we had a few years ago. Not sure why they stopped having them.
Todd,
You need to come as a member. It's only $200 for a designer to join AFSA
and the convention only cost around $500 per person. It's one of the best
values around these days. With all of the excellent speakers and topics and
the evening events you can't spend your hard earned $$ any better.
s a space where protection
could be eliminated.
I believe I would need to calc 3000sf since the area is not completely
filled with insulation.
Any thoughts?
Cliff Whitfield, SET
Fire Design, Inc.
3784 Holly Ridge Trail
Marianna, FL 32448
Phone: 850-526-1886
Fax: 850-526-1
rol or zone the floors but
it is sometimes the best approach for the building owner to keep everything
wet and avoid A/F which is more labor intensive and costly to maintain.
If this is not what you were asking, sorry.
Cliff Whitfield, SET
Fire Design, Inc.
3784 Holly Ridge Trail
Marianna, FL 324
piping on each floor. Since this reference is out of 13 I didn't think
it applied to a 13R system.
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Cliff
Whitfield
Sent: Tuesday, November 10, 2009 9:03
gt; Subject: RE: System subdivision
>
> Yes this is a 13R birdcage system that the AHJ is telling us that it
is
> not allowed. He stated 8.15.21 as his basis for requiring horizontal
> piping on each floor. Since this reference is out of 13 I didn't
think
> it applied to a 13R sys
s. I would not think of
designing a system around here and not have freeze protection if it were not
in a conditioned space.
Cliff Whitfield, SET
President
Fire Design, Inc.
cl...@fire-design.com
www.fire-design.com
-Original Message-
From: sprinklerforum-boun...@fi
on
Consulting Engineers
4880 Sadler Road Suite 300
Glen Allen, VA 23060
v: (804) 521.7105 f: (804) 217.8520
http://www.haengineers.com
Do you really need to print this e-mail?
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkle
Where I'm from (Marianna, FL), LA stands for "Lower Alabama".
Cliff
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Thursday, November 12, 2009 3:52 PM
To: sprinklerforum@firesprink
What do you do then when the calcs don't work and the system is installed?
I know I've gotten pretty conservative in my old age but I can picture
George Church reciting his judge and lawyer story and I would not want to be
on the stand for that one.
I agree with Steve, if there is no other safety
.
But after reading it now, I can see where they could be speaking of multiple
levels of heads.
Cliff Whitfield
Fire Design, Inc.
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams
- FPDC
Sent: Wednesday, October 31, 2007 2:10 PM
To
have to
include all of those heads in your calcs.
Regarding your earlier email, it is difficult for me to make a comment on
your question because I don't have enough information. It's hard for me to
visualize with the sketch you made.
Cliff Whitfield
Fire Design, Inc.
-Origin
teria would be treated like a duct or a table as described
in the standard.
Am I wrong in this interpretation?
Cliff Whitfield
Fire Design, Inc.
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams
- FPDC
Sent: Tuesday, November 06, 2007 2:
range from 4' to 8' wide, I'm using ECLH 20X20 heads.
Brian Harris
FDFP INC.
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Cliff
Whitfield
Sent: Tuesday, November 06, 2007 4:10 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Ver
---Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Cliff
Whitfield
Sent: Tuesday, November 06, 2007 4:35 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Vertical Change in ceiling height
Brian,
Without looking it up, I would doubt that you could get far e
criteria would be treated like a duct or a table as described
>in the standard.
>
>Am I wrong in this interpretation?
>
>Cliff Whitfield
>Fire Design, Inc.
>
>-Original Message-
>From: [EMAIL PROTECTED]
>[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams
>- FP
level and space your
heads. Then see if the "beam blocking rule" is met. If you can spray under
the next lowest level, you are fine. If not, you will need heads at that
level also.
Just my opinion. Like I said earlier, without a drawing to look at, it's
hard to give you a
elping out some of my
crews) so this isn't an old "field hand" talking.
Cliff Whitfield
Fire Design, Inc.
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Wednesday, February 06, 2008 11:35 AM
To: sprinklerforum@fire
John,
At least half of my clients require a separate ceiling plan. I don't know
of anything in the code but it generally makes the prints much cleaner for
the field guys. I think it is more of a personal preference.
Cliff Whitfield
Fire Design, Inc.
-Original Message-
From: [
Todd,
Could you not use the Room Design method for your calcs? That should
eliminate the need to include those heads in the closets. I don't think a
closet is considered a "communicating space" in this instance.
Cliff
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED]
the doors, then exclude them.
Roland
On Feb 12, 2008, at 1:01 PM, Cliff Whitfield wrote:
> Todd,
>
> Could you not use the Room Design method for your calcs? That should
> eliminate the need to include those heads in the closets. I don't
> think a
> closet is considered
municating spaces are not egress paths but
simply adjacent offices, closets, etc.
The primary goal of 13D is to maintain tenability in the room of
origin for at least 10 minutes so people can escape but that's a
different beast.
Roland
On Feb 12, 2008, at 2:48 PM, Cliff Whitfield wrote:
x27;t high
enough to require a standpipe.
I understand that it would be a good idea for the same reasons it is
required on a standpipe but is it actually a requirement?
Cliff Whitfield, SET
Fire Design, Inc.
___
Sprinklerforum mailing
help
speed things up.
Cliff Whitfield, SET
Fire Design, Inc.
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris
Sent: Tuesday, February 19, 2008 9:04 AM
To: sprinklerforum@firesprinkler.org
Subject: Delta Flows
I am working on a job and the calc&
ion, thanks for your time.
Brian Harris
FDFP INC.
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Cliff
Whitfield
Sent: Tuesday, February 19, 2008 11:01 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Delta Flows
Brian,
Apparently the person in
Okay. Let's not get another one started today! He said "unless omission of
sprinklers is permitted".
I still can't picture what Bob has described. From what I see (at least in
my mind), it looks to me like the void would not require sprinklers.
Cliff
-Original Message-
From: [EMAIL
Another problem with going AF is now we have to use Darcy Weisbach for
calculations which then opens an additional can of worms.
Cliff
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan
Sent: Friday, February 22, 2008 10:50 AM
To: sprinklerforum@