CAN YOU USE FIGURE 8.6.4.1.1.3(B) 2013 ?
NOT SURE IF YOU CAN APPLY IT IN YOUR CASE.
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Travis Mack, SET
Sent: January-05-16 1:59 PM
To: sprinklerforum@lists.firesprinkler.org
LOOKING FOR SOMEONE TO GIVE SOME DIRECTION ON LAYING THESE OUT. THE TRUSSES
ARE KIND OF WEIRD SO I AM NOT EVEN SURE IF IT IS POSSIBLE .
WONDERING IF ANYONE WOULD BE ABLE TO LOOK AT A PDF AND TELL ME IF IT CAN BE
DONE.
THANKS
TROY
___
?
John Paulsen - SET
Crown Fire System Design
6282 Seeds Rd.
Grove City, OH 43123
P - 614-782-2438
F - 614-782-2374
C - 614-348-8206
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Trillium Fire Sprinkler Design Inc.
Sent: Tuesday, June 7, 2016
I HAVE A 750 SQFT CLASS ROOM. DUE TO THE CONFIGUARTION OF THE LIGHTS AND A
FEW BUMP OUTS IN THE WALLS. I NEED TO USE FIVE 18x18 EC SPRINKLERS.
IF I READ THE CODE CORRECTLY. I NEED TO CALCULATE 5 TIMES 324 SQFT. WHICH IS
1620 SQFT. WONDERING IF I AM READING THIS RIGHT?
I DON'T SEE THE
tps://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign
Sent from my iPhone
On Jun 27, 2016, at 6:07 PM, Trillium Fire Sprinkler Design Inc.
<trilliumf...@cwisp.ca> wrote:
I HAVE A 750 SQFT CLASS ROOM. DUE TO THE
w.hightail.com/u/MFPDesign
Sent from my iPhone
On Jun 27, 2016, at 6:07 PM, Trillium Fire Sprinkler Design Inc.
<trilliumf...@cwisp.ca> wrote:
I HAVE A 750 SQFT CLASS ROOM. DUE TO THE CONFIGUARTION OF THE LIGHTS AND A FEW
BUMP OUTS IN THE WALLS. I NEED TO USE FIVE 18x18 EC SPRINKLERS.
esign
Sent from my iPhone
On Jun 27, 2016, at 6:07 PM, Trillium Fire Sprinkler Design Inc.
<trilliumf...@cwisp.ca> wrote:
I HAVE A 750 SQFT CLASS ROOM. DUE TO THE CONFIGUARTION OF THE LIGHTS AND A
FEW BUMP OUTS IN THE WALLS. I NEED TO USE FIVE 18x18 EC SPRINKLERS.
IF I REA
what if the 5 ec sprinklers cover less than 900 sqft or in this case since
11`ceilings 923 sqft
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Trillium Fire Sprinkler Design Inc.
Sent: June-27-16 9:38 PM
To: sprinklerforum@lists.firesprinkler.org
...@mfpdesign.com
http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign
LinkedIn: https://www.linkedin.com/in/travismack
On 6/27/2016 6:38 PM, Trillium Fire Sprinkler Design Inc. wrote:
its say on page 598n
ww.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign
LinkedIn: https://www.linkedin.com/in/travismack
On 6/27/2016 6:38 PM, Trillium Fire Sprinkler Design Inc. wrote:
its say on page 598n 2013 handbook. ``
do you think we beat this to death enough.
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Douglas Hicks
Sent: February-02-16 4:33 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Hydromator
No, no, all you need is
QUESTION: AHJ IS TELLING ME I NEED A HOSE CONNECTION ON THE ROOF.
I HAVE A 5 STORY HOTEL. NO STAIR ACCESS TO ROOF, ONLY A HATCH. FLAT ROOF.
THE SYSTEM IS A WET SYSTEM.
I MOVED THE HOSE CONNECTION FROM THE INTERMEDIATE LANDING BETWEEN THE 4TH
AND 5TH TO THE FINSHED 5TH FLOOR LANDING.SINCE IT
website <http://www.parsleyconsulting.com/> *** On 03/25/2016 9:52
AM, Trillium Fire Sprinkler Design Inc. wrote:
>
> QUESTION: AHJ IS TELLING ME I NEED A HOSE CONNECTION ON THE ROOF.
>
> I HAVE A 5 STORY HOTEL. NO STAIR ACCESS TO ROOF, ONLY A HATCH. FLAT ROOF.
> THE SYSTEM I
eenman ." <rongreen...@gmail.com>
> Date: 3/25/2016 11:26 AM (GMT-07:00)
> To: sprinklerforum@lists.firesprinkler.org
> Subject: Re: STANDPIPE
>
> On Fri, Mar 25, 2016 at 10:16 AM, Trillium Fire Sprinkler Design Inc.
> < trilliumf...@cwisp.ca> wrote:
>
> . With
I think you have to meet all the requirements of 11.2.3.3 If you are
applying the room design method.
11.2.3.2.2.2.3 says you must calculate 5 E.C. sprinklers or the minimum
design area that corresponds to the hazard in Figure 11.2.3.1.1
Hope this helps.
-Original Message-
From:
I KNOW FOR 13R YOU NEED TO BE A MINIMUM OF 3'-0" AWAY FROM THE CENTER OF A
CEILING FAN WITH RESIDENTIAL HEADS
I CANNOT FIND WHERE THE SAME APPLIES FOR A 13 SYSTEM USING STANDARD Q.R.
PENDENT OR CONCEALED HEADS.
CAN SOMEONE VERIFY OR EDUCATED ME ON THIS PLEASE?
THANKS
housing unit (motor)
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Trillium Fire Sprinkler Design Inc.
Sent: Monday, January 23, 2017 3:56 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: QR STANDARD SPRAY SPRINKLERS
I KNOW FOR 13R YOU NEED
[mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Trillium Fire Sprinkler Design Inc.
Sent: Monday, January 23, 2017 4:06 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: QR STANDARD SPRAY SPRINKLERS
CAN YOU REFERENCE A CODE FOR ME?
From: Sprinklerforum
I have a project that is a small 2 story building.
It is an office space on the first floor with a residence on the 2nd floor.
The 1st floor ahs a 3 car garage and the residence area goes over top of the
garage.
1st floor designed to nfpa#13
2nd floor designed to nfpa#13r
The
CHECK IBC. I THINK IT WILL REQUIRE THEM.
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Roland Huggins
Sent: November-07-16 11:10 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: 13D Porches
I would say OPEN is to the temperature, not
t a thread that's turning
toward the IBC. If the dwelling(s) in question are being built per the IBC
then I don't think 13D would be the correct standard in the first place.
SL
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Trillium Fire Sprinkler
Send me your email and I can shoot you over a recent project I did so you
have something to look at.
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Brian Harris
Sent: June-06-17 10:37 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Hotels
I do several of these every year.
How tall are you talking.
Are they wanting 13 or 13R?
This determines a few starting factors
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Brian Harris
Sent: June-06-17 10:37 AM
To:
I have a question regarding the design.
They are asking for a deluge systm.
I have a total opening of 48'. I have spaced my sprinklers accordingly.
The code says minimum 3 gpm per lineal foot of water curtain. With no sprinkler
discharging less than 15 gpm.
48 feet x3 gpm =144 gpm
.
6 foot x 3 gpm/ft is 18 gpm per sprinkler for a total of 108 gpm.
On Fri, Nov 3, 2017 at 7:31 AM, Trillium Fire Sprinkler Design Inc.
<trilliumf...@cwisp.ca> wrote:
I have a question regarding the design.
They are asking for a deluge systm.
I have a total opening of 48'. I have
I have a 3 story living condo.
There are 4 units which each have an open parking garage under the 2nd
floor. Along the back wall are 4 (10sqft ) closets.
The engineer is asking for a dry system designed to .15/1950.
Just want to know what everyone's thoughts are about not
; NPT or 7.6 K 3/4" NPT
and please check the S x L rule(s) maybe you are 9' off 1 wall and 8' off the
other
for a 18 x 16 spacing = 288 sq ft
Chuck Bamford SET
On Mon, Jan 7, 2019 at 10:02 AM Trillium Fire Sprinkler Design Inc.
wrote:
YES. I HAVE MANY OPTIONS. I JUST WANT
18’ x 18’, but you
would calculate the discharge at 23.45 gpm.
Steve L.
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Trillium Fire Sprinkler Design Inc.
Sent: Monday, January 07, 2019 9:50 AM
To: sprinklerforum@lists.firesprinkler.org
S
I HAVE A HOTEL THAT SAYS NFPA 13 DESIGN.
IF I USE RESIDENTAIL SPRINKLERS IN THE UPPER FLOORS. AM I CORRECT IN SAYING
THAT I MUST USE .10 DESNITY
EXAMPLE . I WAS GOING TO USE 18x18 4.9 K SPRINKLER
REQUIRES 17 GPM @ 12 PSI FOR .05 DENSITY
BUT SINCE NFPA #13 WOULD I BE REQUIRED TO
Drive | St. Cloud, MN 56301
Office: 320.656.0847 | <mailto:tay...@sfsprinkler.com> tay...@sfsprinkler.com
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Trillium Fire Sprinkler Design Inc.
Sent: Monday, January 07, 2019 12:29 PM
To: sp
I have a warehouse that has double row rack storage to 25 feet with 8 foot
aisles. Class II commodity non encapsulated.
21 says that .325 density apply the increase of 175% for the 25 foot
storage. Using CMDA sprinklers
But then says if using CMDA sprinklers use 22.
I am
2/2/2022 9:23 AM, Trillium Fire Sprinkler Design INC wrote:
I have a warehouse that has double row rack storage to 25 feet with 8 foot
aisles. Class II commodity non encapsulated.
21 says that .325 density apply the increase of 175% for the 25 foot storage.
Using CMDA sprinklers
But then sa
Curious how to install the inspector's test connection on this preaction
system.
Any insight would be welcomed.
I have a single interlock preaction system in a file room. All the pipe is
in a conditioned space. Seems from what I can tell I need to use a dry
inspector's test configuration
I am using Table 16.2.3.1. Nowhere does it state what the hose allowance
requirement is?
I only have 18' storage
It is stated in Table 16.3.3.1 Over 25' storage
I know from previous projects it has been 250 gpm but I am just trying to
find it in the code.
Any help would be appreciated.
found it
12.8.6.1
i knew it was somewhere
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Trillium Fire Sprinkler Design Inc. via Sprinklerforum
Sent: February-03-20 6:44 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Trillium Fire Sprinkler
Can someone please direct me? I have a metal building with acoustical
ceiling tiles. Above the ceiling they have framed with metal studs and fire
rated plywood a mezzanine for the AHU's to sit on. These are electric and
not gas fired.
For some reason I recall reading that if the AHU's are not
I need opinions on mattress storage warehouse in furniture store. I have a
furniture store with a 8000sqft storage area with mattresses stacked on the
floor to a maximum height of 12 feet.
Mostly foam mattresses.
Any idea where I would start to look for the design criteria?
Can anyone direct me to design criteria for the manufacturing and storage of
distilled spirits ( Rum)?
Any info would be greatly appreciated.
Thank you
Troy
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
Has anyone installed or have information on a residential upright sprinkler
that can be installed in an open wood truss roof. The owner wants to have
the trusses exposed in the living/dining area.
Troy
___
Sprinklerforum mailing list
Can someone confirm that it is not mandatory to use CCS sprinklers in a
space 36" or less?
I know it allows for larger spacing, but code wise. I don't believe they are
a must and the space can be protected with QR uprights.
Regards
Troy S
; Trillium Fire Sprinkler Design INC
Subject: Re: COMBUSTIBLE CONCEALED SPACE
Troy,
No. NFPA 13, 2019 edition in 9.3.2 is specific that sprinklers are listed
for horizontal combustible concealed spaces. Specifically listed to provide
protection.
On Tue, Jan 11, 2022 at 2:40 PM Trillium Fire