RE: Pre-action abort

2009-04-07 Thread Craig.Prahl
Maybe so but UL is not recognized or an adopted Code Set by any government 
entity so while it's wording may be logical and appropriate it's not 
necessarily enforceable.

But in this case I would still cite it and use it to inform Mr. PE that he's 
totally clueless as to what he has designed and specified.

First a D.I.P.A. for a few computers is gross overkill.  Second with supervised 
piping, area smoke detection and closed sprinkler heads, if someone doesn't 
respond to the first alarm or second then it needs to go off.  There is 
absolutely no good reason to have an abort switch in a P.A. system.

But you would be surprised on how many times I've been asked this very 
question.  Once I've explained the sequence of operation of a P.A. system the 
question will go away.

This sounds like one of those projects that would be a real nightmare since 
you're obviously dealing with an EOR who already has his mind made up on what 
is proper and required and probably won't back down and look foolish to the 
owner.  

If you decide to pass I'd write a nice letter to the owner and explain why you 
did not bid on this project.

If you do bid and win, I'd write another letter explaining the proper operation 
and purpose of a D.I.P.A. system and copy the engineer.  Obviously the owner 
and EOR need some additional educating.


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
craig.pr...@ch2m.com
http://www.ch2m.com 


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Forest Wilson
Sent: Monday, April 06, 2009 11:50 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Pre-action abort

But UL is the entity doing the listing. 
Forest Wilson 

-Original Message-
From: Jay Jay Blocker fire_sprinkler...@yahoo.com

Date: Mon, 6 Apr 2009 20:36:49
To: sprinklerforum@firesprinkler.org
Subject: Re: Pre-action abort


But where does the UL rank in order?  By this I mean if the local area has 
adopted 13 and 25 do they also have to take into account ULs rules or just say 
as long as the device is listed it is good?





From: Mike Henke mi...@pottersignal.com
To: sprinklerforum@firesprinkler.org
Sent: Monday, April 6, 2009 4:45:14 PM
Subject: RE: Pre-action abort

It is prohibited by UL.
UL 864 states: Abort switches shall not be used on systems intended to
perform pre-action or deluge functions.

Regards,

mike

Mike Henke CET
Sprinkler Product Manager
Potter Electric Signal Co. LLC
WWW.POTTERSIGNAL.COM
866-572-3005

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Monday, April 06, 2009 4:29 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pre-action abort

Question one: Why? 
Question two: At what stage of system response do you want to abort?

There is no mention anywhere in NFPA 13 about the allowance or
disallowance of an abort switch.  I just can't see where anyone would be
quick enough to get to it if something in the system started an
operation anyway.  

With all the delays already built in to a double interlock system what
in the world could another interruption accomplish?

I would not be in favor of it.  But for the sake of curiosity, what's
the application and reasoning behind the question?

Craig L. Prahl, CET  
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
craig.pr...@ch2m.com
http://www.ch2m.com 


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Chris
Cahill
Sent: Monday, April 06, 2009 5:15 PM
To: sprinklerforum@firesprinkler.org
Subject: Pre-action abort

Can one have an abort button on a double interlock pre-action
(electric/pneumatic)?  I'm assuming it would be like on a clean agent
system.  PE hasn't got back to us (don't really expect him to, not a
surprise).  



Chris Cahill, P.E.

Fire Protection Engineer

Sentry Fire Protection, Inc.



763-658-4483

763-658-4921 fax



Email: chr...@sentryfiremn.com



Mail: P.O. Box 69

        Waverly, MN 55390



Location: 4439 Hwy 12 SW

              Waverly, MN 55390



___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

RE: Pre-action abort

2009-04-07 Thread John Drucker
Great question.  Listings don't seem to have the effect one would assume. We
often hear must be installed in accordance with the listing, or product
listed for the intended purpose. 

Then we see prescriptive code applications such as deck and balcony
sprinklers and smoke alarms used in other then dwelling units. The
government can pretty much do as it pleases in the pursuit of safeguarding
building occupants and emergency responders  

It's about the hierarchy of code enforcement, it goes something like this;

1. Statutes = The Legislative action, in NJ the Uniform Construction Code
Act
2. Regulations = The Department or Commissioner rule making, in NJ the
Uniform Construction Code 
3. Codes= The where and when side of the equation, in NJ the 2006 IBC/NJ
Edition, amongst many others.
4. Reference Standards = The how side of the equation, in NJ the 2002
Edition of NFPA-13 for example.
5. Manufacturer's Instructions = The specific how for a specific product.
6. Listings = The nationally recognized testing lab that evaluated the
product for fitness.

I'm sure there are variants at municipal, county and even federal levels.

Bottom line if a statute, regulation or code prescribes it then so it shall
be.

Hope that helps,

John Drucker


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jay Jay
Blocker
Sent: Monday, April 06, 2009 11:37 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Pre-action abort

But where does the UL rank in order?  By this I mean if the local area has
adopted 13 and 25 do they also have to take into account ULs rules or just
say as long as the device is listed it is good?





From: Mike Henke mi...@pottersignal.com
To: sprinklerforum@firesprinkler.org
Sent: Monday, April 6, 2009 4:45:14 PM
Subject: RE: Pre-action abort

It is prohibited by UL.
UL 864 states: Abort switches shall not be used on systems intended to
perform pre-action or deluge functions.

Regards,

mike

Mike Henke CET
Sprinkler Product Manager
Potter Electric Signal Co. LLC
WWW.POTTERSIGNAL.COM
866-572-3005

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Monday, April 06, 2009 4:29 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pre-action abort

Question one: Why? 
Question two: At what stage of system response do you want to abort?

There is no mention anywhere in NFPA 13 about the allowance or
disallowance of an abort switch.  I just can't see where anyone would be
quick enough to get to it if something in the system started an
operation anyway.  

With all the delays already built in to a double interlock system what
in the world could another interruption accomplish?

I would not be in favor of it.  But for the sake of curiosity, what's
the application and reasoning behind the question?

Craig L. Prahl, CET  
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
craig.pr...@ch2m.com
http://www.ch2m.com 


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Chris
Cahill
Sent: Monday, April 06, 2009 5:15 PM
To: sprinklerforum@firesprinkler.org
Subject: Pre-action abort

Can one have an abort button on a double interlock pre-action
(electric/pneumatic)?  I'm assuming it would be like on a clean agent
system.  PE hasn't got back to us (don't really expect him to, not a
surprise).  



Chris Cahill, P.E.

Fire Protection Engineer

Sentry Fire Protection, Inc.



763-658-4483

763-658-4921 fax



Email: chr...@sentryfiremn.com



Mail: P.O. Box 69

        Waverly, MN 55390



Location: 4439 Hwy 12 SW

              Waverly, MN 55390



___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field

RE: Pre-action abort

2009-04-07 Thread Tom Duross
Very well spelt out John.
I assume the word statute to also mean General Laws or (local) Ordinances?
Tom



Great question.  Listings don't seem to have the effect one would assume. We
often hear must be installed in accordance with the listing, or product
listed for the intended purpose.

Then we see prescriptive code applications such as deck and balcony
sprinklers and smoke alarms used in other then dwelling units. The
government can pretty much do as it pleases in the pursuit of safeguarding
building occupants and emergency responders

It's about the hierarchy of code enforcement, it goes something like this;

1. Statutes = The Legislative action, in NJ the Uniform Construction Code
Act
2. Regulations = The Department or Commissioner rule making, in NJ the
Uniform Construction Code
3. Codes= The where and when side of the equation, in NJ the 2006 IBC/NJ
Edition, amongst many others.
4. Reference Standards = The how side of the equation, in NJ the 2002
Edition of NFPA-13 for example.
5. Manufacturer's Instructions = The specific how for a specific product.
6. Listings = The nationally recognized testing lab that evaluated the
product for fitness.

I'm sure there are variants at municipal, county and even federal levels.

Bottom line if a statute, regulation or code prescribes it then so it shall
be.

Hope that helps,

John Drucker

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Pre-action abort

2009-04-07 Thread Sal Izzo (TECH- 103)
It is true that the laboratory test standards do not fit into the hierarchy of 
code enforcement;; however, NFPA 13 requires the products used in sprinkler 
systems to be listed.  As Mike stated, UL 864 requires that  abort switches 
shall not be used on deluge or preaction systems.  If an abort function is 
provided and is used on such systems, it would not meet the functional 
requirements of the test standard and not be recognized as listed.  

Salvatore Izzo, P.E.
Manager - Reliable Technical Services



From: sprinklerforum-boun...@firesprinkler.org 
[sprinklerforum-boun...@firesprinkler.org] On Behalf Of John Drucker 
[john.druc...@verizon.net]
Sent: Tuesday, April 07, 2009 6:29 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pre-action abort

Great question.  Listings don't seem to have the effect one would assume. We
often hear must be installed in accordance with the listing, or product
listed for the intended purpose.

Then we see prescriptive code applications such as deck and balcony
sprinklers and smoke alarms used in other then dwelling units. The
government can pretty much do as it pleases in the pursuit of safeguarding
building occupants and emergency responders

It's about the hierarchy of code enforcement, it goes something like this;

1. Statutes = The Legislative action, in NJ the Uniform Construction Code
Act
2. Regulations = The Department or Commissioner rule making, in NJ the
Uniform Construction Code
3. Codes= The where and when side of the equation, in NJ the 2006 IBC/NJ
Edition, amongst many others.
4. Reference Standards = The how side of the equation, in NJ the 2002
Edition of NFPA-13 for example.
5. Manufacturer's Instructions = The specific how for a specific product.
6. Listings = The nationally recognized testing lab that evaluated the
product for fitness.

I'm sure there are variants at municipal, county and even federal levels.

Bottom line if a statute, regulation or code prescribes it then so it shall
be.

Hope that helps,

John Drucker


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jay Jay
Blocker
Sent: Monday, April 06, 2009 11:37 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Pre-action abort

But where does the UL rank in order?  By this I mean if the local area has
adopted 13 and 25 do they also have to take into account ULs rules or just
say as long as the device is listed it is good?





From: Mike Henke mi...@pottersignal.com
To: sprinklerforum@firesprinkler.org
Sent: Monday, April 6, 2009 4:45:14 PM
Subject: RE: Pre-action abort

It is prohibited by UL.
UL 864 states: Abort switches shall not be used on systems intended to
perform pre-action or deluge functions.

Regards,

mike

Mike Henke CET
Sprinkler Product Manager
Potter Electric Signal Co. LLC
WWW.POTTERSIGNAL.COM
866-572-3005

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Monday, April 06, 2009 4:29 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pre-action abort

Question one: Why?
Question two: At what stage of system response do you want to abort?

There is no mention anywhere in NFPA 13 about the allowance or
disallowance of an abort switch.  I just can't see where anyone would be
quick enough to get to it if something in the system started an
operation anyway.

With all the delays already built in to a double interlock system what
in the world could another interruption accomplish?

I would not be in favor of it.  But for the sake of curiosity, what's
the application and reasoning behind the question?

Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
craig.pr...@ch2m.com
http://www.ch2m.com


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Chris
Cahill
Sent: Monday, April 06, 2009 5:15 PM
To: sprinklerforum@firesprinkler.org
Subject: Pre-action abort

Can one have an abort button on a double interlock pre-action
(electric/pneumatic)?  I'm assuming it would be like on a clean agent
system.  PE hasn't got back to us (don't really expect him to, not a
surprise).



Chris Cahill, P.E.

Fire Protection Engineer

Sentry Fire Protection, Inc.



763-658-4483

763-658-4921 fax



Email: chr...@sentryfiremn.com



Mail: P.O. Box 69

Waverly, MN 55390



Location: 4439 Hwy 12 SW

  Waverly, MN 55390



___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum

Re: Pre-action abort

2009-04-07 Thread nstong
 
Sent via BlackBerry by ATT

-Original Message-
From: Forest Wilson cherokeefire...@aol.com

Date: Mon, 6 Apr 2009 23:50:27 
To: sprinklerforum@firesprinkler.org
Subject: Re: Pre-action abort


But UL is the entity doing the listing.
 Forest Wilson
 
 -Original Message-
 From: Jay Jay Blocker fire_sprinkler...@yahoo.com
 
 Date: Mon, 6 Apr 2009 20:36:49
 To: sprinklerforum@firesprinkler.org
 Subject: Re: Pre-action abort
 
 
 But where does the UL rank in order?  By this I mean if the local area has 
adopted 13 and 25 do they also have to take into account ULs rules or just say 
as long as the device is listed it is good?
 
 
 
 
 
 From: Mike Henke mi...@pottersignal.com
 To: sprinklerforum@firesprinkler.org
 Sent: Monday, April 6, 2009 4:45:14 PM
 Subject: RE: Pre-action abort
 
 It is prohibited by UL.
 UL 864 states: Abort switches shall not be used on systems intended to
 perform pre-action or deluge functions.
 
 Regards,
 
 mike
 
 Mike Henke CET
 Sprinkler Product Manager
 Potter Electric Signal Co. LLC
 WWW.POTTERSIGNAL.COM
 866-572-3005
 
 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org 
mailto:sprinklerforum-boun...@firesprinkler.org ] On Behalf Of
 craig.pr...@ch2m.com
 Sent: Monday, April 06, 2009 4:29 PM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: Pre-action abort
 
 Question one: Why?
 Question two: At what stage of system response do you want to abort?
 
 There is no mention anywhere in NFPA 13 about the allowance or
 disallowance of an abort switch.  I just can't see where anyone would be
 quick enough to get to it if something in the system started an
 operation anyway. 
 
 With all the delays already built in to a double interlock system what
 in the world could another interruption accomplish?
 
 I would not be in favor of it.  But for the sake of curiosity, what's
 the application and reasoning behind the question?
 
 Craig L. Prahl, CET 
 Fire Protection Specialist
 Mechanical Department
 CH2MHILL
 Lockwood Greene
 1500 International Drive
 PO Box 491, Spartanburg, SC  29304-0491
 Direct - 864.599.4102
 Fax - 864.599.8439
 craig.pr...@ch2m.com
 http://www.ch2m.com http://www.ch2m.com 
 
 
 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org 
mailto:sprinklerforum-boun...@firesprinkler.org ] On Behalf Of Chris
 Cahill
 Sent: Monday, April 06, 2009 5:15 PM
 To: sprinklerforum@firesprinkler.org
 Subject: Pre-action abort
 
 Can one have an abort button on a double interlock pre-action
 (electric/pneumatic)?  I'm assuming it would be like on a clean agent
 system.  PE hasn't got back to us (don't really expect him to, not a
 surprise). 
 
 
 
 Chris Cahill, P.E.
 
 Fire Protection Engineer
 
 Sentry Fire Protection, Inc.
 
 
 
 763-658-4483
 
 763-658-4921 fax
 
 
 
 Email: chr...@sentryfiremn.com
 
 
 
 Mail: P.O. Box 69
 
         Waverly, MN 55390
 
 
 
 Location: 4439 Hwy 12 SW
 
               Waverly, MN 55390
 
 
 
 ___
 Sprinklerforum mailing list
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
 For Technical Assistance, send an email to:
 techsupp...@firesprinkler.org
 
 To Unsubscribe, send an email
 to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)
 ___
 Sprinklerforum mailing list
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
 For Technical Assistance, send an email to:
 techsupp...@firesprinkler.org
 
 To Unsubscribe, send an email
 to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)
 ___
 Sprinklerforum mailing list
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
 For Technical Assistance, send an email to: techsupp...@firesprinkler.org
 
 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)
 
 
 
  
 ___
 Sprinklerforum mailing list
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
 For Technical Assistance, send an email to: techsupp...@firesprinkler.org
 
 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)
 ___
 Sprinklerforum mailing list
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
 For Technical Assistance, send an email

RE: Pre-action abort

2009-04-07 Thread John Drucker
Continuing the discussion, the answer to the question is simple does a
statute, regulation or code prescribe an abort station on a deluge or
preaction system ?

Keep in mind that codes and standards are being written in positive
language, i.e. whats permitted vs negative language, i.e. whats
prohibited. Remember what state I'm from ?, Missouri.

John Drucker 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Sal Izzo
(TECH- 103)
Sent: Tuesday, April 07, 2009 9:04 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pre-action abort

It is true that the laboratory test standards do not fit into the
hierarchy of code enforcement;; however, NFPA 13 requires the products
used in sprinkler systems to be listed.  As Mike stated, UL 864 requires
that  abort switches shall not be used on deluge or preaction systems.
If an abort function is provided and is used on such systems, it would
not meet the functional requirements of the test standard and not be
recognized as listed.  

Salvatore Izzo, P.E.
Manager - Reliable Technical Services



From: sprinklerforum-boun...@firesprinkler.org
[sprinklerforum-boun...@firesprinkler.org] On Behalf Of John Drucker
[john.druc...@verizon.net]
Sent: Tuesday, April 07, 2009 6:29 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pre-action abort

Great question.  Listings don't seem to have the effect one would
assume. We often hear must be installed in accordance with the
listing, or product listed for the intended purpose.

Then we see prescriptive code applications such as deck and balcony
sprinklers and smoke alarms used in other then dwelling units. The
government can pretty much do as it pleases in the pursuit of
safeguarding building occupants and emergency responders

It's about the hierarchy of code enforcement, it goes something like
this;

1. Statutes = The Legislative action, in NJ the Uniform Construction
Code Act
2. Regulations = The Department or Commissioner rule making, in NJ the
Uniform Construction Code
3. Codes= The where and when side of the equation, in NJ the 2006 IBC/NJ
Edition, amongst many others.
4. Reference Standards = The how side of the equation, in NJ the 2002
Edition of NFPA-13 for example.
5. Manufacturer's Instructions = The specific how for a specific
product.
6. Listings = The nationally recognized testing lab that evaluated the
product for fitness.

I'm sure there are variants at municipal, county and even federal
levels.

Bottom line if a statute, regulation or code prescribes it then so it
shall be.

Hope that helps,

John Drucker


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jay Jay
Blocker
Sent: Monday, April 06, 2009 11:37 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Pre-action abort

But where does the UL rank in order?  By this I mean if the local area
has adopted 13 and 25 do they also have to take into account ULs rules
or just say as long as the device is listed it is good?





From: Mike Henke mi...@pottersignal.com
To: sprinklerforum@firesprinkler.org
Sent: Monday, April 6, 2009 4:45:14 PM
Subject: RE: Pre-action abort

It is prohibited by UL.
UL 864 states: Abort switches shall not be used on systems intended to
perform pre-action or deluge functions.

Regards,

mike

Mike Henke CET
Sprinkler Product Manager
Potter Electric Signal Co. LLC
WWW.POTTERSIGNAL.COM
866-572-3005

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Monday, April 06, 2009 4:29 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pre-action abort

Question one: Why?
Question two: At what stage of system response do you want to abort?

There is no mention anywhere in NFPA 13 about the allowance or
disallowance of an abort switch.  I just can't see where anyone would be
quick enough to get to it if something in the system started an
operation anyway.

With all the delays already built in to a double interlock system what
in the world could another interruption accomplish?

I would not be in favor of it.  But for the sake of curiosity, what's
the application and reasoning behind the question?

Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
craig.pr...@ch2m.com
http://www.ch2m.com


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Chris
Cahill
Sent: Monday, April 06, 2009 5:15 PM
To: sprinklerforum@firesprinkler.org
Subject: Pre-action abort

Can one have an abort button on a double interlock pre-action
(electric/pneumatic)?  I'm assuming it would

Re: Pre-action abort

2009-04-07 Thread Justin Reid
I think even in special hazard systems an abort switch is not allowed  
unless it is a deadman abort switch. However, for a pre- action  
system, if the room were large enough, you would need to be concerned  
with too many heads opening even with a deadman abort.


Justin D. Reid, P.E.
RLH Fire Protection
16735 Saticoy St. #110
Van Nuys, CA 91406
213-798-0251

Sent from my iPhone

On Apr 7, 2009, at 6:20 AM, John Drucker jdruc...@redbanknj.org  
wrote:

 Continuing the discussion, the answer to the question is simple does a
 statute, regulation or code prescribe an abort station on a deluge or
 preaction system ?

 Keep in mind that codes and standards are being written in positive
 language, i.e. whats permitted vs negative language, i.e. whats
 prohibited. Remember what state I'm from ?, Missouri.

 John Drucker

 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Sal  
 Izzo
 (TECH- 103)
 Sent: Tuesday, April 07, 2009 9:04 AM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: Pre-action abort

 It is true that the laboratory test standards do not fit into the
 hierarchy of code enforcement;; however, NFPA 13 requires the products
 used in sprinkler systems to be listed.  As Mike stated, UL 864  
 requires
 that  abort switches shall not be used on deluge or preaction systems.
 If an abort function is provided and is used on such systems, it would
 not meet the functional requirements of the test standard and not be
 recognized as listed.

 Salvatore Izzo, P.E.
 Manager - Reliable Technical Services


 
 From: sprinklerforum-boun...@firesprinkler.org
 [sprinklerforum-boun...@firesprinkler.org] On Behalf Of John Drucker
 [john.druc...@verizon.net]
 Sent: Tuesday, April 07, 2009 6:29 AM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: Pre-action abort

 Great question.  Listings don't seem to have the effect one would
 assume. We often hear must be installed in accordance with the
 listing, or product listed for the intended purpose.

 Then we see prescriptive code applications such as deck and balcony
 sprinklers and smoke alarms used in other then dwelling units. The
 government can pretty much do as it pleases in the pursuit of
 safeguarding building occupants and emergency responders

 It's about the hierarchy of code enforcement, it goes something like
 this;

 1. Statutes = The Legislative action, in NJ the Uniform Construction
 Code Act
 2. Regulations = The Department or Commissioner rule making, in NJ the
 Uniform Construction Code
 3. Codes= The where and when side of the equation, in NJ the 2006  
 IBC/NJ
 Edition, amongst many others.
 4. Reference Standards = The how side of the equation, in NJ the 2002
 Edition of NFPA-13 for example.
 5. Manufacturer's Instructions = The specific how for a specific
 product.
 6. Listings = The nationally recognized testing lab that evaluated the
 product for fitness.

 I'm sure there are variants at municipal, county and even federal
 levels.

 Bottom line if a statute, regulation or code prescribes it then so it
 shall be.

 Hope that helps,

 John Drucker


 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jay Jay
 Blocker
 Sent: Monday, April 06, 2009 11:37 PM
 To: sprinklerforum@firesprinkler.org
 Subject: Re: Pre-action abort

 But where does the UL rank in order?  By this I mean if the local area
 has adopted 13 and 25 do they also have to take into account ULs rules
 or just say as long as the device is listed it is good?




 
 From: Mike Henke mi...@pottersignal.com
 To: sprinklerforum@firesprinkler.org
 Sent: Monday, April 6, 2009 4:45:14 PM
 Subject: RE: Pre-action abort

 It is prohibited by UL.
 UL 864 states: Abort switches shall not be used on systems intended to
 perform pre-action or deluge functions.

 Regards,

 mike

 Mike Henke CET
 Sprinkler Product Manager
 Potter Electric Signal Co. LLC
 WWW.POTTERSIGNAL.COM
 866-572-3005

 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
 craig.pr...@ch2m.com
 Sent: Monday, April 06, 2009 4:29 PM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: Pre-action abort

 Question one: Why?
 Question two: At what stage of system response do you want to abort?

 There is no mention anywhere in NFPA 13 about the allowance or
 disallowance of an abort switch.  I just can't see where anyone  
 would be
 quick enough to get to it if something in the system started an
 operation anyway.

 With all the delays already built in to a double interlock system what
 in the world could another interruption accomplish?

 I would not be in favor of it.  But for the sake of curiosity, what's
 the application and reasoning behind the question?

 Craig L. Prahl, CET
 Fire Protection

RE: Pre-action abort

2009-04-07 Thread Mike Henke
John,

Potter manufactures a release panel that has a zone that can be
programmed as an abort circuit or a supervisory zone. As part of our
listing we were required by UL to state that the abort circuit on
pre-action and deluge systems is not permitted by UL 864.

In my opinion that means that programming the zone to be an abort
circuit for a pre-action system would mean the panel would not be in
compliance with UL  not be listed for that system.

The statue, regulation or code requiring the abort circuit probably also
requires a listed panel. So the statue, regulation or code would require
something that cannot be accomplished, an abort switch on a listed
pre-action panel.

Regards

mike

Mike Henke CET
Sprinkler Product Manager
Potter Electric Signal Co. LLC
WWW.POTTERSIGNAL.COM
866-572-3005

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of John
Drucker
Sent: Tuesday, April 07, 2009 8:20 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pre-action abort

Continuing the discussion, the answer to the question is simple does a
statute, regulation or code prescribe an abort station on a deluge or
preaction system ?

Keep in mind that codes and standards are being written in positive
language, i.e. whats permitted vs negative language, i.e. whats
prohibited. Remember what state I'm from ?, Missouri.

John Drucker 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Sal Izzo
(TECH- 103)
Sent: Tuesday, April 07, 2009 9:04 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pre-action abort

It is true that the laboratory test standards do not fit into the
hierarchy of code enforcement;; however, NFPA 13 requires the products
used in sprinkler systems to be listed.  As Mike stated, UL 864 requires
that  abort switches shall not be used on deluge or preaction systems.
If an abort function is provided and is used on such systems, it would
not meet the functional requirements of the test standard and not be
recognized as listed.  

Salvatore Izzo, P.E.
Manager - Reliable Technical Services



From: sprinklerforum-boun...@firesprinkler.org
[sprinklerforum-boun...@firesprinkler.org] On Behalf Of John Drucker
[john.druc...@verizon.net]
Sent: Tuesday, April 07, 2009 6:29 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pre-action abort

Great question.  Listings don't seem to have the effect one would
assume. We often hear must be installed in accordance with the
listing, or product listed for the intended purpose.

Then we see prescriptive code applications such as deck and balcony
sprinklers and smoke alarms used in other then dwelling units. The
government can pretty much do as it pleases in the pursuit of
safeguarding building occupants and emergency responders

It's about the hierarchy of code enforcement, it goes something like
this;

1. Statutes = The Legislative action, in NJ the Uniform Construction
Code Act
2. Regulations = The Department or Commissioner rule making, in NJ the
Uniform Construction Code
3. Codes= The where and when side of the equation, in NJ the 2006 IBC/NJ
Edition, amongst many others.
4. Reference Standards = The how side of the equation, in NJ the 2002
Edition of NFPA-13 for example.
5. Manufacturer's Instructions = The specific how for a specific
product.
6. Listings = The nationally recognized testing lab that evaluated the
product for fitness.

I'm sure there are variants at municipal, county and even federal
levels.

Bottom line if a statute, regulation or code prescribes it then so it
shall be.

Hope that helps,

John Drucker


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jay Jay
Blocker
Sent: Monday, April 06, 2009 11:37 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Pre-action abort

But where does the UL rank in order?  By this I mean if the local area
has adopted 13 and 25 do they also have to take into account ULs rules
or just say as long as the device is listed it is good?





From: Mike Henke mi...@pottersignal.com
To: sprinklerforum@firesprinkler.org
Sent: Monday, April 6, 2009 4:45:14 PM
Subject: RE: Pre-action abort

It is prohibited by UL.
UL 864 states: Abort switches shall not be used on systems intended to
perform pre-action or deluge functions.

Regards,

mike

Mike Henke CET
Sprinkler Product Manager
Potter Electric Signal Co. LLC
WWW.POTTERSIGNAL.COM
866-572-3005

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Monday, April 06, 2009 4:29 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pre-action abort

Question one: Why?
Question two: At what stage of system response do you want to abort

RE: Pre-action abort

2009-04-07 Thread Craig.Prahl
Obviously the spec for this project was for a gaseous system that the EOR used 
and just changed any reference from gas to P.A.  First clue that someone is 
practicing outside their area of expertise.  Imagine the fun when he tries to 
review shop drawings.

Typically the first signal with be the smoke detectors, if they are cross zoned 
you have two distinct devices that agree that there is smoke present.  Alarms 
are going off, who's responding?

If the fire event continues then you will ultimately have a sprinkler open, 
releasing pressure in the system and allowing the P.A. valve to open, now 
you've got a fire, who's responding?

In the D.I.P.A. system there's no real justification for an abort sequence.  
The owner has multiple alarms notifying him of an event in progress.  Within 
the time frame of the first S.D. he has time to take corrective measures to 
manually correct the situation.  




Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
craig.pr...@ch2m.com
http://www.ch2m.com 


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Justin Reid
Sent: Tuesday, April 07, 2009 10:17 AM
To: sprinklerforum@firesprinkler.org
Cc: sprinklerforum@firesprinkler.org
Subject: Re: Pre-action abort

I think even in special hazard systems an abort switch is not allowed unless it 
is a deadman abort switch. However, for a pre- action system, if the room were 
large enough, you would need to be concerned with too many heads opening even 
with a deadman abort.


Justin D. Reid, P.E.
RLH Fire Protection
16735 Saticoy St. #110
Van Nuys, CA 91406
213-798-0251

Sent from my iPhone

On Apr 7, 2009, at 6:20 AM, John Drucker jdruc...@redbanknj.org
wrote:

 Continuing the discussion, the answer to the question is simple does a 
 statute, regulation or code prescribe an abort station on a deluge or 
 preaction system ?

 Keep in mind that codes and standards are being written in positive 
 language, i.e. whats permitted vs negative language, i.e. whats 
 prohibited. Remember what state I'm from ?, Missouri.

 John Drucker

 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Sal 
 Izzo
 (TECH- 103)
 Sent: Tuesday, April 07, 2009 9:04 AM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: Pre-action abort

 It is true that the laboratory test standards do not fit into the 
 hierarchy of code enforcement;; however, NFPA 13 requires the products 
 used in sprinkler systems to be listed.  As Mike stated, UL 864 
 requires that  abort switches shall not be used on deluge or preaction 
 systems.
 If an abort function is provided and is used on such systems, it would 
 not meet the functional requirements of the test standard and not be 
 recognized as listed.

 Salvatore Izzo, P.E.
 Manager - Reliable Technical Services


 
 From: sprinklerforum-boun...@firesprinkler.org
 [sprinklerforum-boun...@firesprinkler.org] On Behalf Of John Drucker 
 [john.druc...@verizon.net]
 Sent: Tuesday, April 07, 2009 6:29 AM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: Pre-action abort

 Great question.  Listings don't seem to have the effect one would 
 assume. We often hear must be installed in accordance with the 
 listing, or product listed for the intended purpose.

 Then we see prescriptive code applications such as deck and balcony 
 sprinklers and smoke alarms used in other then dwelling units. The 
 government can pretty much do as it pleases in the pursuit of 
 safeguarding building occupants and emergency responders

 It's about the hierarchy of code enforcement, it goes something like 
 this;

 1. Statutes = The Legislative action, in NJ the Uniform Construction 
 Code Act
 2. Regulations = The Department or Commissioner rule making, in NJ the 
 Uniform Construction Code
 3. Codes= The where and when side of the equation, in NJ the 2006 
 IBC/NJ Edition, amongst many others.
 4. Reference Standards = The how side of the equation, in NJ the 2002 
 Edition of NFPA-13 for example.
 5. Manufacturer's Instructions = The specific how for a specific 
 product.
 6. Listings = The nationally recognized testing lab that evaluated the 
 product for fitness.

 I'm sure there are variants at municipal, county and even federal 
 levels.

 Bottom line if a statute, regulation or code prescribes it then so it 
 shall be.

 Hope that helps,

 John Drucker


 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jay Jay 
 Blocker
 Sent: Monday, April 06, 2009 11:37 PM
 To: sprinklerforum@firesprinkler.org
 Subject: Re: Pre-action abort

 But where does the UL rank in order?  By this I mean if the local

RE: Pre-action abort

2009-04-07 Thread John Drucker
Mike,

Here are two examples;

N.J.A.C. 5:23-3.14 - 2006 IBC/NJ 903.3.1.2.1 Balconies and decks. 
Sprinkler protection shall be provided for exterior balconies, decks and
ground floor patios of dwelling units where the building is of Type V
construction. Sidewall sprinklers that are used to protect such areas
shall be permitted to be located such that their deflectors are within 1
inch (25mm) to 6 inches (152 mm) below the structural members and a
maximum distance of 14 inches (356 mm) below the deck of the exterior
balconies and decks that are constructed of open wood joist
construction.

N.J.A.C. 5:23-6.29 Mixed use buildings (c) Alarms: In any nonresidential
use located below one or more dwelling units (including single room
occupancies), when the work area exceeds 50 percent of the gross
enclosed floor area of the nonresidential use, single or multiple
station smoke alarms shall be installed in the nonresidential portion(s)
of the building in accordance with NFPA 72 and provided with an audible
alarm located within each dwelling unit of the residential portion of
the building. The alarms shall be AC powered with battery back-up.
Hard-wired, interconnected smoke alarms installed throughout the
building shall be accepted as meeting this requirement.

Are either of these applications compliant with the listing standard and
or listing ?

So in essence if the promulgating authority prescribes it so it shall
be, obviously they have that authority. In the case of the
Preaction/Deluge Abort I am not aware of a prescriptive regulation or
code section that requires this. In other words we fall back on the
adopted standards, listings etc, i.e. its not permitted.

Hope that helps

John Drucker
Fire Protection Subcode Official

Disclaimer-This is only my opinion, is not binding on anyone. Consult
with the authority having jurisdiction.


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Mike
Henke
Sent: Tuesday, April 07, 2009 10:27 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pre-action abort

John,

Potter manufactures a release panel that has a zone that can be
programmed as an abort circuit or a supervisory zone. As part of our
listing we were required by UL to state that the abort circuit on
pre-action and deluge systems is not permitted by UL 864.

In my opinion that means that programming the zone to be an abort
circuit for a pre-action system would mean the panel would not be in
compliance with UL  not be listed for that system.

The statue, regulation or code requiring the abort circuit probably also
requires a listed panel. So the statue, regulation or code would require
something that cannot be accomplished, an abort switch on a listed
pre-action panel.

Regards

mike

Mike Henke CET
Sprinkler Product Manager
Potter Electric Signal Co. LLC
WWW.POTTERSIGNAL.COM
866-572-3005

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of John
Drucker
Sent: Tuesday, April 07, 2009 8:20 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pre-action abort

Continuing the discussion, the answer to the question is simple does a
statute, regulation or code prescribe an abort station on a deluge or
preaction system ?

Keep in mind that codes and standards are being written in positive
language, i.e. whats permitted vs negative language, i.e. whats
prohibited. Remember what state I'm from ?, Missouri.

John Drucker 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Sal Izzo
(TECH- 103)
Sent: Tuesday, April 07, 2009 9:04 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pre-action abort

It is true that the laboratory test standards do not fit into the
hierarchy of code enforcement;; however, NFPA 13 requires the products
used in sprinkler systems to be listed.  As Mike stated, UL 864 requires
that  abort switches shall not be used on deluge or preaction systems.
If an abort function is provided and is used on such systems, it would
not meet the functional requirements of the test standard and not be
recognized as listed.  

Salvatore Izzo, P.E.
Manager - Reliable Technical Services



From: sprinklerforum-boun...@firesprinkler.org
[sprinklerforum-boun...@firesprinkler.org] On Behalf Of John Drucker
[john.druc...@verizon.net]
Sent: Tuesday, April 07, 2009 6:29 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pre-action abort

Great question.  Listings don't seem to have the effect one would
assume. We often hear must be installed in accordance with the
listing, or product listed for the intended purpose.

Then we see prescriptive code applications such as deck and balcony
sprinklers and smoke alarms used in other then dwelling units. The
government can pretty much do as it pleases in the pursuit of
safeguarding

RE: Pre-action abort

2009-04-07 Thread Thom McMahon
This appears to be a poorly worded or badly written/copied spec. Not an
unusual occurrence when non FPE's are involved with the Fire Protection. I'd
bid the job as I would normally install it, and where is say's Per plans
and spec's I note Exceptions taken If you are the low bidder, they'll
call and ask what your exceptions are. If you're not low bidder, they won't
be calling anyway.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Chris Cahill
Sent: Monday, April 06, 2009 4:09 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pre-action abort

Reasoning from a non-sprinkler proficient PE?  That's self explanatory.  I
haven't the foggiest idea why one would want it.  As I said won't return
calls, bid due shortly.  We're talking 10 PC's in a training classroom,
college like, 2400 sq.ft.  Then there is a second PA in a comm. room that is
300 sq.ft. which I imagine is the servers to run said PC's and connect to
the WWW.  Why both rooms aren't on the same PA I don't know that either.
Suspect PE is working of % of contract.  Also, local gov't work isn't
allowed to be cheap so when wet system prices fall something has to be added
so we last few taxpayers get our moneys worth? This ain't no billion dollar
server farm. There is also a clean agent someplace but I don't know where
and not my scope of work so I really don't care.  But adds to the oddity of
it all.  

Spec reads like a FM-200 or the like but is clearly for the double interlock
PA.  1. Upon activation of smoke detector energize predischarge strobe and
bell.  2. Activate a time delay sequence and enable abort sequence.  3.
Abort station shall reset the 30 second time delay.

Now technically he never specs an electric/pneumatic.  Could always do
pneumatic/pneumatic to solve the problem.  

I don't like it either but before I start a fight I want to know which side
I'm on. (And just because I might be on the losing side code wise doesn't
mean I won't start it anyway).   

Chris Cahill, P.E.

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: Pre-action abort

2009-04-07 Thread Ron Greenman
Then there's the alternative means and methods clause which pretty
much allows someone to decide gasoline in the pipes to keep them new
and shiny is OK as long as the AHJ approves it. Now gasoline is an
obvious no-no even when the AHJ is the dog catcher by day, crime
fighter by night  AHJ by hobby, but what about an abort switch if Mr.
PE says it's OK? Even a semi-savvy, over-worked AHJ might think water
damage in this server room might be devastating. The double
interlock pre-action system is obviously better than single (even
though designed originally for freezer warehouses--essentially an
extra slow dry pipe) and way superior to wet--that is if your goal is
to not stop fires but rather stop water damage. Then the abort switch
makes even more sense and allows the stockroom clerk, who is, after
all, on the scene, to make decisions about fire protection during an
emergency situation. And then there's the precedence of an abort
switch on the wonder gas system. Isn't the presence of the wonder gas
successfully used over and over to argue against the need for
sprinklers in rooms containing computers? The AHJ described above, not
savvy to UL 864 (after all, what does a fire alarm panel listing
protocol have to do with fire sprinklers?), just might be happy to
defer to the educational and professional credentials of Mr. PE.

On Tue, Apr 7, 2009 at 8:20 AM, Thom McMahon tmcma...@firetechinc.com wrote:
 This appears to be a poorly worded or badly written/copied spec. Not an
 unusual occurrence when non FPE's are involved with the Fire Protection. I'd
 bid the job as I would normally install it, and where is say's Per plans
 and spec's I note Exceptions taken If you are the low bidder, they'll
 call and ask what your exceptions are. If you're not low bidder, they won't
 be calling anyway.

 Thom McMahon, SET
 Firetech, Inc.
 2560 Copper Ridge Dr
 P.O. Box 882136
 Steamboat Springs, CO 80488
 Tel:  970-879-7952
 Fax: 970-879-7926


 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Chris Cahill
 Sent: Monday, April 06, 2009 4:09 PM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: Pre-action abort

 Reasoning from a non-sprinkler proficient PE?  That's self explanatory.  I
 haven't the foggiest idea why one would want it.  As I said won't return
 calls, bid due shortly.  We're talking 10 PC's in a training classroom,
 college like, 2400 sq.ft.  Then there is a second PA in a comm. room that is
 300 sq.ft. which I imagine is the servers to run said PC's and connect to
 the WWW.  Why both rooms aren't on the same PA I don't know that either.
 Suspect PE is working of % of contract.  Also, local gov't work isn't
 allowed to be cheap so when wet system prices fall something has to be added
 so we last few taxpayers get our moneys worth? This ain't no billion dollar
 server farm. There is also a clean agent someplace but I don't know where
 and not my scope of work so I really don't care.  But adds to the oddity of
 it all.

 Spec reads like a FM-200 or the like but is clearly for the double interlock
 PA.  1. Upon activation of smoke detector energize predischarge strobe and
 bell.  2. Activate a time delay sequence and enable abort sequence.  3.
 Abort station shall reset the 30 second time delay.

 Now technically he never specs an electric/pneumatic.  Could always do
 pneumatic/pneumatic to solve the problem.

 I don't like it either but before I start a fight I want to know which side
 I'm on. (And just because I might be on the losing side code wise doesn't
 mean I won't start it anyway).

 Chris Cahill, P.E.

 ___
 Sprinklerforum mailing list
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
 For Technical Assistance, send an email to: techsupp...@firesprinkler.org

 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)




-- 
Ron Greenman
at home
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Pre-action abort

2009-04-07 Thread Craig.Prahl
Aw Ron, you're just being cynical.  None of that would ever happen.wink 


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
craig.pr...@ch2m.com
http://www.ch2m.com 


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman
Sent: Tuesday, April 07, 2009 12:00 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Pre-action abort

Then there's the alternative means and methods clause which pretty much allows 
someone to decide gasoline in the pipes to keep them new and shiny is OK as 
long as the AHJ approves it. Now gasoline is an obvious no-no even when the AHJ 
is the dog catcher by day, crime fighter by night  AHJ by hobby, but what 
about an abort switch if Mr.
PE says it's OK? Even a semi-savvy, over-worked AHJ might think water damage in 
this server room might be devastating. The double interlock pre-action system 
is obviously better than single (even though designed originally for freezer 
warehouses--essentially an extra slow dry pipe) and way superior to wet--that 
is if your goal is to not stop fires but rather stop water damage. Then the 
abort switch makes even more sense and allows the stockroom clerk, who is, 
after all, on the scene, to make decisions about fire protection during an 
emergency situation. And then there's the precedence of an abort switch on the 
wonder gas system. Isn't the presence of the wonder gas successfully used over 
and over to argue against the need for sprinklers in rooms containing 
computers? The AHJ described above, not savvy to UL 864 (after all, what does a 
fire alarm panel listing protocol have to do with fire sprinklers?), just might 
be happy to defer to the educational and professional credentials of Mr. PE.

On Tue, Apr 7, 2009 at 8:20 AM, Thom McMahon tmcma...@firetechinc.com wrote:
 This appears to be a poorly worded or badly written/copied spec. Not 
 an unusual occurrence when non FPE's are involved with the Fire 
 Protection. I'd bid the job as I would normally install it, and where 
 is say's Per plans and spec's I note Exceptions taken If you are 
 the low bidder, they'll call and ask what your exceptions are. If 
 you're not low bidder, they won't be calling anyway.

 Thom McMahon, SET
 Firetech, Inc.
 2560 Copper Ridge Dr
 P.O. Box 882136
 Steamboat Springs, CO 80488
 Tel:  970-879-7952
 Fax: 970-879-7926


 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Chris 
 Cahill
 Sent: Monday, April 06, 2009 4:09 PM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: Pre-action abort

 Reasoning from a non-sprinkler proficient PE?  That's self 
 explanatory.  I haven't the foggiest idea why one would want it.  As I 
 said won't return calls, bid due shortly.  We're talking 10 PC's in a 
 training classroom, college like, 2400 sq.ft.  Then there is a second 
 PA in a comm. room that is 300 sq.ft. which I imagine is the servers 
 to run said PC's and connect to the WWW.  Why both rooms aren't on the same 
 PA I don't know that either.
 Suspect PE is working of % of contract.  Also, local gov't work isn't 
 allowed to be cheap so when wet system prices fall something has to be 
 added so we last few taxpayers get our moneys worth? This ain't no 
 billion dollar server farm. There is also a clean agent someplace but 
 I don't know where and not my scope of work so I really don't care.  
 But adds to the oddity of it all.

 Spec reads like a FM-200 or the like but is clearly for the double 
 interlock PA.  1. Upon activation of smoke detector energize 
 predischarge strobe and bell.  2. Activate a time delay sequence and enable 
 abort sequence.  3.
 Abort station shall reset the 30 second time delay.

 Now technically he never specs an electric/pneumatic.  Could always do 
 pneumatic/pneumatic to solve the problem.

 I don't like it either but before I start a fight I want to know which 
 side I'm on. (And just because I might be on the losing side code wise 
 doesn't mean I won't start it anyway).

 Chris Cahill, P.E.

 ___
 Sprinklerforum mailing list
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
 For Technical Assistance, send an email to: 
 techsupp...@firesprinkler.org

 To Unsubscribe, send an email 
 to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)




--
Ron Greenman
at home
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field

RE: Pre-action abort

2009-04-07 Thread Thom McMahon
The better answer might be Firecycle type system by Viking.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



Ron Greenman
Sent: Tuesday, April 07, 2009 10:00 AM

if your goal is to not stop fires but rather stop water damage. Then the
abort switch makes even more sense and allows the stockroom clerk, who is,
after all, on the scene, to make decisions about fire protection during an
emergency situation. 

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Pre-action abort

2009-04-07 Thread Craig.Prahl
And here's your stock room guy, yes capable of making even the most critical of 
decisions in any emergency situation.

http://www.youtube.com/watch?v=2tma-zFkDEY

I feel better now... 

Anyone got an umbrella?


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
craig.pr...@ch2m.com
http://www.ch2m.com 



Ron Greenman
Sent: Tuesday, April 07, 2009 10:00 AM

if your goal is to not stop fires but rather stop water damage. Then the abort 
switch makes even more sense and allows the stockroom clerk, who is, after all, 
on the scene, to make decisions about fire protection during an emergency 
situation. 

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: Pre-action abort

2009-04-07 Thread Ron Greenman
I know this guy. He's brilliant. He's managed to clone himself many times over.

On Tue, Apr 7, 2009 at 9:22 AM,  craig.pr...@ch2m.com wrote:
 And here's your stock room guy, yes capable of making even the most critical 
 of decisions in any emergency situation.

 http://www.youtube.com/watch?v=2tma-zFkDEY

 I feel better now...

 Anyone got an umbrella?


 Craig L. Prahl, CET
 Fire Protection Specialist
 Mechanical Department
 CH2MHILL
 Lockwood Greene
 1500 International Drive
 PO Box 491, Spartanburg, SC  29304-0491
 Direct - 864.599.4102
 Fax - 864.599.8439
 craig.pr...@ch2m.com
 http://www.ch2m.com



 Ron Greenman
 Sent: Tuesday, April 07, 2009 10:00 AM

 if your goal is to not stop fires but rather stop water damage. Then the 
 abort switch makes even more sense and allows the stockroom clerk, who is, 
 after all, on the scene, to make decisions about fire protection during an 
 emergency situation.

 ___
 Sprinklerforum mailing list
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
 For Technical Assistance, send an email to: techsupp...@firesprinkler.org

 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)
 ___
 Sprinklerforum mailing list
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
 For Technical Assistance, send an email to: techsupp...@firesprinkler.org

 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)




-- 
Ron Greenman
at home
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Pre-action abort

2009-04-07 Thread John Drucker
Tom,

Statute: A law enacted by a legislature.  The NJ State Legislature
consists of two Houses: a 40-member Senate and an 80-member General
Assembly. The Senate and Assembly chambers are located in the State
House in Trenton. The chief function of the Legislature is to enact
laws. A proposal to make a new law, or to change or repeal an existing
law, is presented to the Legislature as a bill. To become law, a bill
must pass both Houses by a majority vote and be approved by the
Governor. At the general election in November 1992, the voters approved
a constitutional amendment permitting the Legislature to review
administrative rules and regulations.

Ordinance; An ordinance is a local law. The State of NJ is made up of
566 municipalities each with its own governing ring body. Although the
method of enacting an ordinance will vary from municipality to
municipality, they are generally passed by the governing body and signed
by the municipal executive or mayor and subsequently enforced by local
police, code enforcement and municipal prosecutors.

The NJ Uniform Construction Code is administered at the state level,
municipalities are conveyed enforcement powers if they so choose. The
municipality then becomes the Local Enforcing agency. Inspectors and
Plan Reviewers are licensed by the state government. Municipalities do
not have the authority to modify, amend or suspend the provisions of the
NJ Uniform Construction Code.

Hope that helps
John Drucker



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Tom
Duross
Sent: Tuesday, April 07, 2009 6:53 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pre-action abort

Very well spelt out John.
I assume the word statute to also mean General Laws or (local)
Ordinances?
Tom



Great question.  Listings don't seem to have the effect one would
assume. We often hear must be installed in accordance with the
listing, or product listed for the intended purpose.

Then we see prescriptive code applications such as deck and balcony
sprinklers and smoke alarms used in other then dwelling units. The
government can pretty much do as it pleases in the pursuit of
safeguarding building occupants and emergency responders

It's about the hierarchy of code enforcement, it goes something like
this;

1. Statutes = The Legislative action, in NJ the Uniform Construction
Code Act
2. Regulations = The Department or Commissioner rule making, in NJ the
Uniform Construction Code
3. Codes= The where and when side of the equation, in NJ the 2006 IBC/NJ
Edition, amongst many others.
4. Reference Standards = The how side of the equation, in NJ the 2002
Edition of NFPA-13 for example.
5. Manufacturer's Instructions = The specific how for a specific
product.
6. Listings = The nationally recognized testing lab that evaluated the
product for fitness.

I'm sure there are variants at municipal, county and even federal
levels.

Bottom line if a statute, regulation or code prescribes it then so it
shall be.

Hope that helps,

John Drucker

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or entity to 
which it is addressed and may contain information that is privileged and 
confidential, nor is it, unless specifically stated, intended to be relied upon 
by any person or persons other than the individual or entity named above and no 
warranties or representations are made or intended to persons or entities not 
named above.  If the reader is not the intended recipient, you are hereby 
notified that any dissemination, distribution or copying of this communication 
is strictly prohibited.  If you have received this communication in error, 
please notify us immediately by telephone, return this message to the address 
above and delete all copies.  Thank you.

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: Pre-action abort

2009-04-06 Thread Ron Greenman
Chris,

In jails I've seen electrically operated zone valves with a 90 second
time delay before the valves were opened, an open now override, and
an abort to each valve but that required CCTV and a constantly manned
station wherein the operator had complete control over the cameras and
operation of the valves. These are always on wet systems and I'd
suspect that they required a PE to bless them.

On Mon, Apr 6, 2009 at 2:15 PM, Chris Cahill chr...@sentryfiremn.com wrote:
 Can one have an abort button on a double interlock pre-action
 (electric/pneumatic)?  I'm assuming it would be like on a clean agent
 system.  PE hasn't got back to us (don't really expect him to, not a
 surprise).



 Chris Cahill, P.E.

 Fire Protection Engineer

 Sentry Fire Protection, Inc.



 763-658-4483

 763-658-4921 fax



 Email: chr...@sentryfiremn.com



 Mail: P.O. Box 69

        Waverly, MN 55390



 Location: 4439 Hwy 12 SW

              Waverly, MN 55390



 ___
 Sprinklerforum mailing list
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
 For Technical Assistance, send an email to: techsupp...@firesprinkler.org

 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)




-- 
Ron Greenman
at home
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Pre-action abort

2009-04-06 Thread Craig.Prahl
Question one: Why? 
Question two: At what stage of system response do you want to abort?

There is no mention anywhere in NFPA 13 about the allowance or disallowance of 
an abort switch.  I just can't see where anyone would be quick enough to get to 
it if something in the system started an operation anyway.  

With all the delays already built in to a double interlock system what in the 
world could another interruption accomplish?

I would not be in favor of it.  But for the sake of curiosity, what's the 
application and reasoning behind the question?

Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
craig.pr...@ch2m.com
http://www.ch2m.com 


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Chris Cahill
Sent: Monday, April 06, 2009 5:15 PM
To: sprinklerforum@firesprinkler.org
Subject: Pre-action abort

Can one have an abort button on a double interlock pre-action 
(electric/pneumatic)?  I'm assuming it would be like on a clean agent system.  
PE hasn't got back to us (don't really expect him to, not a surprise).  

 

Chris Cahill, P.E.

Fire Protection Engineer

Sentry Fire Protection, Inc.

 

763-658-4483

763-658-4921 fax

 

Email: chr...@sentryfiremn.com

 

Mail: P.O. Box 69

Waverly, MN 55390

 

Location: 4439 Hwy 12 SW

  Waverly, MN 55390

 

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Pre-action abort

2009-04-06 Thread Chris Cahill
Reasoning from a non-sprinkler proficient PE?  That's self explanatory.  I
haven't the foggiest idea why one would want it.  As I said won't return
calls, bid due shortly.  We're talking 10 PC's in a training classroom,
college like, 2400 sq.ft.  Then there is a second PA in a comm. room that is
300 sq.ft. which I imagine is the servers to run said PC's and connect to
the WWW.  Why both rooms aren't on the same PA I don't know that either.
Suspect PE is working of % of contract.  Also, local gov't work isn't
allowed to be cheap so when wet system prices fall something has to be added
so we last few taxpayers get our moneys worth? This ain't no billion dollar
server farm. There is also a clean agent someplace but I don't know where
and not my scope of work so I really don't care.  But adds to the oddity of
it all.  

Spec reads like a FM-200 or the like but is clearly for the double interlock
PA.  1. Upon activation of smoke detector energize predischarge strobe and
bell.  2. Activate a time delay sequence and enable abort sequence.  3.
Abort station shall reset the 30 second time delay.

Now technically he never specs an electric/pneumatic.  Could always do
pneumatic/pneumatic to solve the problem.  

I don't like it either but before I start a fight I want to know which side
I'm on. (And just because I might be on the losing side code wise doesn't
mean I won't start it anyway).   

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: chr...@sentryfiremn.com
 
Mail: P.O. Box 69
Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
  Waverly, MN 55390

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Monday, April 06, 2009 4:29 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pre-action abort

Question one: Why? 
Question two: At what stage of system response do you want to abort?

There is no mention anywhere in NFPA 13 about the allowance or disallowance
of an abort switch.  I just can't see where anyone would be quick enough to
get to it if something in the system started an operation anyway.  

With all the delays already built in to a double interlock system what in
the world could another interruption accomplish?

I would not be in favor of it.  But for the sake of curiosity, what's the
application and reasoning behind the question?

Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
craig.pr...@ch2m.com
http://www.ch2m.com 


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Chris Cahill
Sent: Monday, April 06, 2009 5:15 PM
To: sprinklerforum@firesprinkler.org
Subject: Pre-action abort

Can one have an abort button on a double interlock pre-action
(electric/pneumatic)?  I'm assuming it would be like on a clean agent
system.  PE hasn't got back to us (don't really expect him to, not a
surprise).  

 

Chris Cahill, P.E.

Fire Protection Engineer

Sentry Fire Protection, Inc.

 

763-658-4483

763-658-4921 fax

 

Email: chr...@sentryfiremn.com

 

Mail: P.O. Box 69

Waverly, MN 55390

 

Location: 4439 Hwy 12 SW

  Waverly, MN 55390

 

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Pre-action abort

2009-04-06 Thread Mike Henke
It is prohibited by UL.
UL 864 states: Abort switches shall not be used on systems intended to
perform pre-action or deluge functions.

Regards,

mike

Mike Henke CET
Sprinkler Product Manager
Potter Electric Signal Co. LLC
WWW.POTTERSIGNAL.COM
866-572-3005

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Monday, April 06, 2009 4:29 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pre-action abort

Question one: Why? 
Question two: At what stage of system response do you want to abort?

There is no mention anywhere in NFPA 13 about the allowance or
disallowance of an abort switch.  I just can't see where anyone would be
quick enough to get to it if something in the system started an
operation anyway.  

With all the delays already built in to a double interlock system what
in the world could another interruption accomplish?

I would not be in favor of it.  But for the sake of curiosity, what's
the application and reasoning behind the question?

Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
craig.pr...@ch2m.com
http://www.ch2m.com 


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Chris
Cahill
Sent: Monday, April 06, 2009 5:15 PM
To: sprinklerforum@firesprinkler.org
Subject: Pre-action abort

Can one have an abort button on a double interlock pre-action
(electric/pneumatic)?  I'm assuming it would be like on a clean agent
system.  PE hasn't got back to us (don't really expect him to, not a
surprise).  

 

Chris Cahill, P.E.

Fire Protection Engineer

Sentry Fire Protection, Inc.

 

763-658-4483

763-658-4921 fax

 

Email: chr...@sentryfiremn.com

 

Mail: P.O. Box 69

Waverly, MN 55390

 

Location: 4439 Hwy 12 SW

  Waverly, MN 55390

 

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: Pre-action abort

2009-04-06 Thread Jay Jay Blocker
But where does the UL rank in order?  By this I mean if the local area has 
adopted 13 and 25 do they also have to take into account ULs rules or just say 
as long as the device is listed it is good?





From: Mike Henke mi...@pottersignal.com
To: sprinklerforum@firesprinkler.org
Sent: Monday, April 6, 2009 4:45:14 PM
Subject: RE: Pre-action abort

It is prohibited by UL.
UL 864 states: Abort switches shall not be used on systems intended to
perform pre-action or deluge functions.

Regards,

mike

Mike Henke CET
Sprinkler Product Manager
Potter Electric Signal Co. LLC
WWW.POTTERSIGNAL.COM
866-572-3005

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Monday, April 06, 2009 4:29 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pre-action abort

Question one: Why? 
Question two: At what stage of system response do you want to abort?

There is no mention anywhere in NFPA 13 about the allowance or
disallowance of an abort switch.  I just can't see where anyone would be
quick enough to get to it if something in the system started an
operation anyway.  

With all the delays already built in to a double interlock system what
in the world could another interruption accomplish?

I would not be in favor of it.  But for the sake of curiosity, what's
the application and reasoning behind the question?

Craig L. Prahl, CET  
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
craig.pr...@ch2m.com
http://www.ch2m.com 


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Chris
Cahill
Sent: Monday, April 06, 2009 5:15 PM
To: sprinklerforum@firesprinkler.org
Subject: Pre-action abort

Can one have an abort button on a double interlock pre-action
(electric/pneumatic)?  I'm assuming it would be like on a clean agent
system.  PE hasn't got back to us (don't really expect him to, not a
surprise).  



Chris Cahill, P.E.

Fire Protection Engineer

Sentry Fire Protection, Inc.



763-658-4483

763-658-4921 fax



Email: chr...@sentryfiremn.com



Mail: P.O. Box 69

        Waverly, MN 55390



Location: 4439 Hwy 12 SW

              Waverly, MN 55390



___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)



  
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: Pre-action abort

2009-04-06 Thread Forest Wilson
But UL is the entity doing the listing. 
Forest Wilson 

-Original Message-
From: Jay Jay Blocker fire_sprinkler...@yahoo.com

Date: Mon, 6 Apr 2009 20:36:49 
To: sprinklerforum@firesprinkler.org
Subject: Re: Pre-action abort


But where does the UL rank in order?  By this I mean if the local area has 
adopted 13 and 25 do they also have to take into account ULs rules or just say 
as long as the device is listed it is good?





From: Mike Henke mi...@pottersignal.com
To: sprinklerforum@firesprinkler.org
Sent: Monday, April 6, 2009 4:45:14 PM
Subject: RE: Pre-action abort

It is prohibited by UL.
UL 864 states: Abort switches shall not be used on systems intended to
perform pre-action or deluge functions.

Regards,

mike

Mike Henke CET
Sprinkler Product Manager
Potter Electric Signal Co. LLC
WWW.POTTERSIGNAL.COM
866-572-3005

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Monday, April 06, 2009 4:29 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pre-action abort

Question one: Why? 
Question two: At what stage of system response do you want to abort?

There is no mention anywhere in NFPA 13 about the allowance or
disallowance of an abort switch.  I just can't see where anyone would be
quick enough to get to it if something in the system started an
operation anyway.  

With all the delays already built in to a double interlock system what
in the world could another interruption accomplish?

I would not be in favor of it.  But for the sake of curiosity, what's
the application and reasoning behind the question?

Craig L. Prahl, CET  
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
craig.pr...@ch2m.com
http://www.ch2m.com 


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Chris
Cahill
Sent: Monday, April 06, 2009 5:15 PM
To: sprinklerforum@firesprinkler.org
Subject: Pre-action abort

Can one have an abort button on a double interlock pre-action
(electric/pneumatic)?  I'm assuming it would be like on a clean agent
system.  PE hasn't got back to us (don't really expect him to, not a
surprise).  



Chris Cahill, P.E.

Fire Protection Engineer

Sentry Fire Protection, Inc.



763-658-4483

763-658-4921 fax



Email: chr...@sentryfiremn.com



Mail: P.O. Box 69

        Waverly, MN 55390



Location: 4439 Hwy 12 SW

              Waverly, MN 55390



___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)



  
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)