RE: FM and Concealed Sprinklers

2017-10-07 Thread Rod DiBona
nkler.org> Subject: Re: FM and Concealed Sprinklers I still don’t see why you’d need a variance, real world example, my apologies for not being brand agnostic but for this exercise its hard to avoid but I think most brands have similar offerings: Reliable G5-56 with G4 plate, UL listed Quick

RE: [EXTERNAL] RE: FM and Concealed Sprinklers

2016-10-11 Thread Brad Casterline
1, 2016 1:14 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: [EXTERNAL] RE: FM and Concealed Sprinklers And "quick response" is just a listing classification that could have been called yellow and standard response elephant. If you meet the criterion for yellow you get listed as yellow.

Re: [EXTERNAL] RE: FM and Concealed Sprinklers

2016-10-11 Thread rongreenman .
t; > *From:* Sprinklerforum [mailto:sprinklerforum-bounces@lists.firesprinkler. > org] *On Behalf Of *Brad Casterline > *Sent:* Tuesday, October 11, 2016 11:12 AM > *To:* sprinklerforum@lists.firesprinkler.org > *Subject:* RE: [EXTERNAL] RE: FM and Concealed Sprinklers > > > > A Qui

RE: [EXTERNAL] RE: FM and Concealed Sprinklers

2016-10-11 Thread Larrimer, Peter A
t they say when you put garbage into the model. Pete From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Brad Casterline Sent: Tuesday, October 11, 2016 11:12 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: [EXTERNAL] RE: FM and Concealed Sprinkler

RE: [EXTERNAL] RE: FM and Concealed Sprinklers

2016-10-11 Thread Brad Casterline
-boun...@lists.firesprinkler.org] On Behalf Of Larrimer, Peter A Sent: Tuesday, October 11, 2016 9:18 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: [EXTERNAL] RE: FM and Concealed Sprinklers I can't say I know what you are using for your model, nor how you model RTI's for concealed

RE: [EXTERNAL] RE: FM and Concealed Sprinklers

2016-10-11 Thread Larrimer, Peter A
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Brad Casterline Sent: Saturday, October 08, 2016 11:44 AM To: sprinklerforum@lists.firesprinkler.org Subject: [EXTERNAL] RE: FM and Concealed Sprinklers You're welcome Scott. And Pete-- I'll be a monkey's uncle if concealers

Re: FM and Concealed Sprinklers

2016-10-08 Thread Brad Casterline
<bcasterli...@gmail.com> > *Sent:* Saturday, October 08, 2016 12:09 PM > *To:* sprinklerforum@lists.firesprinkler.org > *Subject:* Re: FM and Concealed Sprinklers > > > If you glue them right Ron, as I'm sure you know, racoons neither stay > silent nor squeal-- they sort of t

Re: FM and Concealed Sprinklers

2016-10-08 Thread Douglas Hicks
for those heads. Now about those racoons, did you use UL listed glue? From: Brad Casterline Sent: Saturday, October 08, 2016 12:09 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: FM and Concealed Sprinklers If you glue them right Ron, as I'm sure you know, racoons neither stay silent nor

Re: FM and Concealed Sprinklers

2016-10-08 Thread Brad Casterline
Listed Quick Response Fire Sprinkler is a listed quick >> response fire sprinkler. >> >> >> >> As for insurance companies and what they want well ask them, so long as >> it meets the applicable code its code compliant. >> >> >> >> Joh

RE: FM and Concealed Sprinklers

2016-10-08 Thread Brad Casterline
r 7, 2016 1:34 PM > *To:* sprinklerforum@lists.firesprinkler.org > *Subject:* Re: FM and Concealed Sprinklers > > > > I don't think what the value of the rule is, or how it's determined or any > other thing than what's required is germane to the discussion. If the AHJ > want

RE: FM and Concealed Sprinklers

2016-10-07 Thread Brad Casterline
t:* Friday, October 07, 2016 8:00 AM *To:* sprinklerforum@lists.firesprinkler.org *Subject:* [EXTERNAL] RE: FM and Concealed Sprinklers >From a code compliance standpoint Underwriters Laboratories is one of appx 22 Nationally Recognized Testing Laboratories (NRTL). Interestingly UL

RE: FM and Concealed Sprinklers

2016-10-07 Thread Scott Holman
@lists.firesprinkler.org Subject: Re: FM and Concealed Sprinklers I don't think what the value of the rule is, or how it's determined or any other thing than what's required is germane to the discussion. If the AHJ wants squealing raccoons glued to the ceiling and FM wants quiet ones you have

Re: FM and Concealed Sprinklers

2016-10-07 Thread rongreenman .
> > > > PS. By the way Todd, my bet is that it isn’t a tie especially if a > concealed sprinkler is involved. My guess is that, in an open room, a > standard response pendent sprinkler will operate faster than a quick > response concealed sprinkler. > > > >

RE: FM and Concealed Sprinklers

2016-10-07 Thread John Drucker
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Larrimer, Peter A Sent: Friday, October 07, 2016 3:55 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: FM and Concealed Sprinklers Interesting topic. In my humble opinion, the UL 199 tests to qualify concealed sprinklers

RE: FM and Concealed Sprinklers

2016-10-07 Thread Larrimer, Peter A
: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of John Drucker Sent: Friday, October 07, 2016 8:00 AM To: sprinklerforum@lists.firesprinkler.org Subject: [EXTERNAL] RE: FM and Concealed Sprinklers From a code compliance standpoint Underwriters Laboratories is one of appx

RE: FM and Concealed Sprinklers

2016-10-07 Thread John Drucker
...@redbanknj.org<mailto:jdruc...@redbanknj.org> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Morey, Mike Sent: Thursday, October 06, 2016 9:24 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: FM and Concealed Sprinklers I still don’t s

Re: FM and Concealed Sprinklers

2016-10-06 Thread Travis Mack
Correct Mike. In that case no variance would be needed as both criteria are met. Nice catch. Travis Mack, SET MFP Design, LLC "Follow" us on Facebook: https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to MFP Design via: https://www.hightail.com/u/MFPDesign Sent from

Re: FM and Concealed Sprinklers

2016-10-06 Thread Morey, Mike
I still don’t see why you’d need a variance, real world example, my apologies for not being brand agnostic but for this exercise its hard to avoid but I think most brands have similar offerings: Reliable G5-56 with G4 plate, UL listed Quick response, FM listed Standard response. FM does not

Re: FM and Concealed Sprinklers

2016-10-06 Thread Travis Mack, SET
Your argument is a moot point. It is about FM approval. FM does not have approval for those sprinklers. You have to get a variance from the FM reviewer. Then you may be battling an AHJ that says they don't recognize FM and you have to follow NFPA 13 criteria. These are real world

Re: FM and Concealed Sprinklers

2016-10-06 Thread Brad Casterline
Which activates quicker, in an LH, ~10' ceiling, 225 s.f. spacing: 200F QR, or, 155F SR? SURVEY SAID! it's a tie. I.O.W., I.M.H.O., (opinion being entire weekends spent jacking with it bcoz i been divorced for 16 years and the kids are grown and on their own) activation is more about ceiling

Re: FM and Concealed Sprinklers

2016-10-06 Thread rongreenman .
The problem with FM allowing something like SE where NFPA requires QR is that the AHJ may require compliance to NFPA. You then playing to two masters and which one will give. Probably FM but you have to get approval and ad was earlier stated your best served by getting it in writing. On

Re: FM and Concealed Sprinklers

2016-10-06 Thread Morey, Mike
If you look at data sheet 2-0, FM doesn’t require QR heads in HC-1, 2 or 3 if you use k5.6 standard coverage heads at least. And last I looked there are a number of QR concealed heads that are FM approved, only as standard response. Since your AHJ presumably uses NFPA/UL, they’re QR heads,