"A Quick Response sprinkler does not necessarily activate sooner than a 
standard response sprinkler!"

You can't change all the variables.  Even that scenario shouldn't make any 
difference provided the fire is in the same location below the sprinklers.  
Given the same scenario (spacing, fire size, room size etc.), most would expect 
that a quick response would activate quicker than a standard response 
sprinkler, but I would suggest otherwise when the QR is a concealed sprinkler.

You can wing the input for the cover plate response, but that is the big issue 
and you know what they say when you put garbage into the model.

Pete

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brad Casterline
Sent: Tuesday, October 11, 2016 11:12 AM
To: [email protected]
Subject: RE: [EXTERNAL] RE: FM and Concealed Sprinklers

A Quick Response sprinkler does not necessarily activate sooner than a standard 
response sprinkler!
For example, 155 SRs at 120 S.F. spacing might activate sooner than 155 QRs at 
225 S.F., be they regular pendent or concealers.

We are allowed to use design area reduction when the RTI is 50 (m-s)^2 or less 
and it is listed as quick response, and three other conditions are met. The RTI 
is the physical, non site specific property of the sprinkler, and the 'listed 
as quick response' is the various spacings, ceiling heights, etc. tested, with 
some kind of pass/fail citeria, which i assume includes a range of minimum 
'real' activation times.

I used 50 and 80 RTI for the QR and SR in the four activation times I showed. 
In more detailed scenarios I have used 38 and 90 based on glass bulb 
manufactures published data. I kind of winged the concealer cover plate, but 
not totally-- I input specific heat, conductivity, and density for a dab of 
solder, and made the plate disappear when the dab reached 135F.

I have been using FDS-SMV for 10 years. For sprinkler activation it is for 
personal curiosity and to try to get a little more insight than I can get from 
NFPA alone.
I don't try to predict anything, I like looking at 'differences', based on RTI, 
Temp rating, ceiling height, and spacing.
Fascinating stuff, and I'm glad you brought the 'concealer twist' to my 
activation curiosity Pete!

thanks,

Brad


________________________________
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Larrimer, Peter A
Sent: Tuesday, October 11, 2016 9:18 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: [EXTERNAL] RE: FM and Concealed Sprinklers

I can't say I know what you are using for your model, nor how you model RTI's 
for concealed heads and cover plates, but it sort of begs the question.  Why is 
there a NFPA 13 reduction in design areas for LH and OH when the QR concealed 
head might be slower than a standard response; assuming your model results are 
close to accurate regarding response times.

Considering that most fires are controlled with the first one or two sprinklers 
in LH and OH facility fires, maybe the QR vs SR isn't a big deal when it comes 
to required design areas?

Thanks
Pete
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to