Absolutely, the best glue, great, everybody says, utube listed, the best,
great glue.
On Oct 8, 2016 3:57 PM, "Douglas Hicks" <[email protected]> wrote:

> At hospital request, we installed concealed heads in the psycho hold
> room.  The concern was someone would hang their self from the heads.  I
> looked, but did not find a ladder in the area that would allow them to
> reach the head and use it as a tie-off. But  I did order extra escutcheons
> for those heads.
>
> Now about those racoons, did you use UL listed glue?
>
> *From:* Brad Casterline <[email protected]>
> *Sent:* Saturday, October 08, 2016 12:09 PM
> *To:* [email protected]
> *Subject:* Re: FM and Concealed Sprinklers
>
>
> If you glue them right Ron, as I'm sure you know, racoons neither stay
> silent nor squeal-- they sort of trill.
> On Oct 7, 2016 3:35 PM, "rongreenman ." <[email protected]> wrote:
>
>> I don't think what the value of the rule is, or how it's determined or
>> any other thing than what's required is germane to the discussion. If the
>> AHJ wants squealing raccoons glued to the ceiling and FM wants quiet ones
>> you have the problem of serving two masters. When they've both already
>> decided what type of raccoon they demand logic entreaties to them will get
>> a nod of acceptance from the one you agree with and  an harrumph from the
>> other. you just need one to back off this time. That's it. After that you
>> can go present your arguments to the International Raccoon Society and/or
>> Raccoon Underwriters and try to get them to agree to a common requirement
>> under all circumstances.
>>
>> I heard that FM changed their co-effcients for hydrant test to coincide
>> with NFPA's. How did that get fixed and why not the other way. It would be
>> easiest to just use FM as it met the needs of both masters but what if
>> doing so was the difference between a pump or not. You'd be best serving
>> your other master, the owner, by getting a waiver from FM.
>>
>>
>> On Fri, Oct 7, 2016 at 12:54 PM, Larrimer, Peter A <
>> [email protected]> wrote:
>>
>>> Interesting topic.
>>>
>>>
>>>
>>> In my humble opinion, the UL 199 tests to qualify concealed sprinklers
>>> as quick response is extremely questionable!  On the other hand, what do
>>> you think you are getting when you install a quick response sprinkler
>>> anyway?  Effectively, the UL 199 test requires the concealed sprinkler to
>>> be plunged into the test chamber exactly like the pendent sprinkler to get
>>> the RTI rating.  As far as I know, another test used by UL to measure the
>>> response time for a concealed sprinkler is to seal up a test room and force
>>> the heat of the test fire up through the sprinkler cover plate to measure
>>> response time.  Neither of those tests used by UL to qualify a concealed
>>> head as quick response reflect the conditions in the field that a concealed
>>> head would likely encounter.
>>>
>>> I am not suggesting that concealed sprinklers won’t operate, but I would
>>> be willing to bet that they won’t go off any faster than a standard
>>> response sprinkler unless the conditions are such that the heat will be
>>> forced up through the cover plate, and that won’t often be the case.
>>>
>>>
>>>
>>> In addition, concealed sprinklers are not permitted by their listing to
>>> be installed in rooms where the space above the ceiling is at a higher
>>> pressure than the pressure in the room below.  One manufacture states
>>> “NOTE: Concealed sprinklers must be installed in neutral or negative
>>> pressure plenums only.”  That requirement can significantly limit the
>>> installation opportunities for those of us in the healthcare industry
>>> because we have many negative pressure rooms that are required for
>>> infection control purposes and installing a concealed head would be
>>> inappropriate (though it happens quite often).  Have the installers out
>>> there ever asked which rooms were designed to negative pressure
>>> requirements prior to installing the sprinkler system?
>>>
>>>
>>>
>>> We had one instance where we found out after the fact, that we evidently
>>> had leaking duct work in the plenum space above a ceiling and the pressure
>>> in the space above the ceiling was enough to have the soot line from a
>>> patient bed fire blacken the walls down to a foot off the floor even though
>>> we had a quick response sprinkler in the room.  The air leaking from the
>>> plenum space left a little white line around the cover plate of the
>>> concealed sprinkler and the quick response sprinkler didn’t operate at
>>> all.
>>>
>>>
>>>
>>> I am not saying concealed sprinklers are especially bad, but I would not
>>> consider them to be quick response even when listed as such by UL.  Maybe
>>> that is why there aren’t any FM Approved quick response sprinklers?  When
>>> somebody makes a concealed sprinkler that gets an FM Approval for quick
>>> response, then I would feel more comfortable that the sprinkler will
>>> actually operate faster than a standard response.  There are FM Approved
>>> standard response sprinklers, and FM has a test for quick response
>>> concealed sprinklers, but since nobody has a FM Approved concealed
>>> sprinkler on the market, it might make you wonder if their test might be
>>> more realistic.
>>>
>>>
>>>
>>> VA sprinkler specifications require FM approved quick response
>>> sprinklers (not UL listed) for new projects.  Thus, no concealed sprinklers
>>> should be going into any VA Medical Centers.  We have negative pressure
>>> rooms and hope to get a quicker response from the sprinklers.
>>>
>>>
>>>
>>> Have a good weekend.
>>>
>>>
>>>
>>> Pete Larrimer
>>>
>>> VA
>>>
>>>
>>>
>>> PS.  By the way Todd, my bet is that it isn’t a tie especially if a
>>> concealed sprinkler is involved.  My guess is that, in an open room, a
>>> standard response pendent sprinkler will operate faster than a quick
>>> response concealed sprinkler.
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>> *From:* Sprinklerforum [mailto:sprinklerforum-bounces
>>> @lists.firesprinkler.org] *On Behalf Of *John Drucker
>>> *Sent:* Friday, October 07, 2016 8:00 AM
>>> *To:* [email protected]
>>> *Subject:* [EXTERNAL] RE: FM and Concealed Sprinklers
>>>
>>>
>>>
>>> From a code compliance standpoint Underwriters Laboratories is one of
>>> appx 22 Nationally Recognized Testing Laboratories (NRTL).  Interestingly
>>> UL 199, 1626 etc. are the defacto standards for fire sprinklers which any
>>> of the other NRTL’s would use to test and list a fire sprinkler (aside from
>>> perhaps FM Global)  should they choose to do so. So it’s not really UL
>>> itself but rather does the sprinkler comply with the applicable UL
>>> Standard. A UL Listed Quick Response Fire Sprinkler is a listed quick
>>> response fire sprinkler.
>>>
>>>
>>>
>>> As for insurance companies and what they want well ask them, so long as
>>> it meets the applicable code its code compliant.
>>>
>>>
>>>
>>> John Drucker, CET
>>>
>>> Assistant Construction Official
>>>
>>> Fire Protection Subcode Official
>>>
>>> Electrical Subcode Official
>>>
>>> Building Inspector
>>>
>>> Borough of Red Bank, NJ
>>>
>>> 90 Monmouth Street
>>>
>>> Red Bank, New Jersey 07701
>>>
>>> Cel/Text: 732-904-6823
>>>
>>> Email: [email protected]
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>> *From:* Sprinklerforum [mailto:sprinklerforum-bounces
>>> @lists.firesprinkler.org
>>> <[email protected]>] *On Behalf Of *Morey,
>>> Mike
>>> *Sent:* Thursday, October 06, 2016 9:24 PM
>>> *To:* [email protected]
>>> *Subject:* Re: FM and Concealed Sprinklers
>>>
>>>
>>>
>>> I still don’t see why you’d need a variance, real world example, my
>>> apologies for not being brand agnostic but for this exercise its hard to
>>> avoid but I think most brands have similar offerings:
>>>
>>>
>>>
>>> Reliable G5-56 with G4 plate, UL listed Quick response, FM listed
>>> Standard response.  FM does not require Quick response, so the fact they
>>> don’t accept it as QR is irrelevant.  Your real world AHJ should accept the
>>> UL listing.
>>>
>>>
>>>
>>> On Oct 6, 2016, at 7:57 PM, Travis Mack, SET <[email protected]>
>>> wrote:
>>>
>>>
>>>
>>> Your argument is a moot point.  It is about FM approval.  FM does not
>>> have approval for those sprinklers.
>>>
>>> You have to get a variance from the FM reviewer.  Then you may be
>>> battling an AHJ that says they don't recognize FM and you have to follow
>>> NFPA 13 criteria.  These are real world scenarios that come into play daily
>>> for many of us.
>>>
>>> Not everything comes down to 15 significant figures and exponents to the
>>> 1000th power.  Sometimes it is just dealing with what is available and
>>> playing the game.
>>>
>>> Travis Mack, SET
>>>
>>> MFP Design, LLC
>>>
>>> 2508 E Lodgepole Drive
>>>
>>> Gilbert, AZ 85298
>>>
>>> 480-505-9271
>>>
>>> fax: 866-430-6107
>>>
>>> email:[email protected]
>>>
>>>
>>>
>>> http://www.mfpdesign.com
>>>
>>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>>>
>>> Send large files to us via: https://www.hightail.com/u/MFPDesign
>>>
>>> LinkedIn: https://www.linkedin.com/in/travismack
>>>
>>> On 10/6/2016 4:52 PM, Brad Casterline wrote:
>>>
>>> Which activates quicker, in an LH, ~10' ceiling, 225 s.f. spacing:
>>> 200F QR, or,
>>> 155F SR?
>>>
>>> SURVEY SAID!
>>>
>>> it's a tie.
>>>
>>> I.O.W., I.M.H.O., (opinion being entire weekends spent jacking with it
>>> bcoz i been divorced for 16 years and the kids are grown and on their own)
>>>
>>> activation is more about ceiling height, temp rating, and spacing than
>>> QR vs SR.
>>>
>>> On Oct 6, 2016 6:39 PM, "rongreenman ." <[email protected]> wrote:
>>>
>>> The problem with FM allowing something like SE where NFPA requires QR is
>>> that the AHJ may require compliance to NFPA. You then playing to two
>>> masters and which one will give. Probably FM  but you have to get approval
>>> and ad was earlier stated your best served by getting it in writing.
>>>
>>> On Thursday, October 6, 2016, Todd Williams <[email protected]>
>>> wrote:
>>>
>>> [image: Image removed by sender.]
>>>
>>> I am working on a hospital job that is FM. FM was very good about
>>> allowing us to use concealed QR (even concealed sidewalls). However, it
>>> needs to be run past their loss control peeps to make sure they are OK with
>>> it.
>>>
>>> Todd G Williams, PE
>>>
>>> Fire Protection Design/Consulting
>>>
>>> Stonington, CT
>>>
>>> 860-535-2080 (ofc)
>>>
>>> 860-608-4559 (cell)
>>>
>>>
>>>
>>> via Newton Mail
>>> <https://cloudmagic.com/k/d/mailapp?ct=ti&cv=9.1.9&pv=9.3.5&source=email_footer_2>
>>>
>>>
>>>
>>> On Thu, Oct 6, 2016 at 7:23 PM, Morey, Mike <[email protected]> wrote:
>>>
>>> If you look at data sheet 2-0, FM doesn’t require QR heads in HC-1, 2 or
>>> 3 if you use k5.6 standard coverage heads at least. And last I looked there
>>> are a number of QR concealed heads that are FM approved, only as standard
>>> response. Since your AHJ presumably uses NFPA/UL, they’re QR heads, and
>>> since FM doesn’t care, it’s fine that they accept them only as standard
>>> response. Since our client is all FM it’s always a picnic trying to design
>>> systems that satisfy both because it’s easier to deal with the AHJs without
>>> having to explain the FM design criteria in detail (they do accept them
>>> when its an issue though).
>>>
>>> > On Oct 6, 2016, at 6:29 PM, Mark Phillips <[email protected]>
>>> wrote:
>>> >
>>> > Just ask their rep for a variance in a written letter.
>>> >
>>> > Have done many a hospital this way.
>>> >
>>> > Sent from my Verizon 4G LTE Droid
>>> > On Oct 6, 2016 6:13 PM, Scott Holman <[email protected]> wrote:
>>> >
>>> > Hello All,
>>> >
>>> >
>>> >
>>> > I have an FM job where the customer wants concealed sprinklers in
>>> light hazard occupancies. Since it is light hazard, quick response
>>> sprinklers are required. However, FM does not have any approved quick
>>> response concealed pendents that I could find. Has anyone dealt with this
>>> before?
>>> >
>>> >
>>> >
>>> > Thank you for your input!
>>> >
>>> >
>>> >
>>> > Scott H.
>>> >
>>> >
>>> > _______________________________________________
>>> > Sprinklerforum mailing list
>>> > [email protected]
>>> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-f
>>> iresprinkler.org
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-f
>>> iresprinkler.org
>>>
>>>
>>>
>>> --
>>> Sent from Gmail Mobile
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-f
>>> iresprinkler.org
>>>
>>>
>>>
>>> _______________________________________________
>>>
>>> Sprinklerforum mailing list
>>>
>>> [email protected]
>>>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>
>>>
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-f
>>> iresprinkler.org
>>>
>>>
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-f
>>> iresprinkler.org
>>>
>>>
>>
>>
>> --
>> Ron Greenman
>>
>> 4110 Olson Dr., NW
>> Gig Harbor, WA 98335
>>
>> [email protected]
>>
>> 253.576.9700
>>
>> The Universe is monstrously indifferent to the presence of man. -Werner
>> Herzog, screenwriter, film director, author, actor and opera director
>> (1942-)
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-
>> firesprinkler.org
>>
>> ------------------------------
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to