Well... when I say "225 S.F." spacing it means I modeled (1) sprinkler at a radial distance of 7.5*1.414=~10'-8" from the center of the fire. This would be worse case.
If I modeled 120 S.F. spacing, I would leave the fire and all conditions the same except move the sprinkler closer to the fire, where the Temp and velocity of the ceiling jet are higher. It is in this way that an SR could activate sooner than a QR. If I kept every thing except ceiling height the same, it could be that an SR in an 8' ceiling will activate sooner than a QR in a 12' ceiling. yes i know what they say... you get garbage out... :) i cant help but take a shot though--- i know the numbers i get are better than some W.A.G. Brad _____ From: Sprinklerforum [mailto:[email protected]] On Behalf Of rongreenman . Sent: Tuesday, October 11, 2016 1:14 PM To: [email protected] Subject: Re: [EXTERNAL] RE: FM and Concealed Sprinklers And "quick response" is just a listing classification that could have been called yellow and standard response elephant. If you meet the criterion for yellow you get listed as yellow. If not you don't. I don't know if Tyco kept of discontinued it, but Grinnell had a head listed as quick response to a certain height and standard above that. On Tue, Oct 11, 2016 at 10:58 AM, Larrimer, Peter A <[email protected]> wrote: "A Quick Response sprinkler does not necessarily activate sooner than a standard response sprinkler!" You can't change all the variables. Even that scenario shouldn't make any difference provided the fire is in the same location below the sprinklers. Given the same scenario (spacing, fire size, room size etc.), most would expect that a quick response would activate quicker than a standard response sprinkler, but I would suggest otherwise when the QR is a concealed sprinkler. You can wing the input for the cover plate response, but that is the big issue and you know what they say when you put garbage into the model. Pete From: Sprinklerforum [mailto:sprinklerforum- <mailto:[email protected]> [email protected]] On Behalf Of Brad Casterline Sent: Tuesday, October 11, 2016 11:12 AM To: sprinklerforum@lists. <mailto:[email protected]> firesprinkler.org Subject: RE: [EXTERNAL] RE: FM and Concealed Sprinklers A Quick Response sprinkler does not necessarily activate sooner than a standard response sprinkler! For example, 155 SRs at 120 S.F. spacing might activate sooner than 155 QRs at 225 S.F., be they regular pendent or concealers. We are allowed to use design area reduction when the RTI is 50 (m-s)^2 or less and it is listed as quick response, and three other conditions are met. The RTI is the physical, non site specific property of the sprinkler, and the 'listed as quick response' is the various spacings, ceiling heights, etc. tested, with some kind of pass/fail citeria, which i assume includes a range of minimum 'real' activation times. I used 50 and 80 RTI for the QR and SR in the four activation times I showed. In more detailed scenarios I have used 38 and 90 based on glass bulb manufactures published data. I kind of winged the concealer cover plate, but not totally-- I input specific heat, conductivity, and density for a dab of solder, and made the plate disappear when the dab reached 135F. I have been using FDS-SMV for 10 years. For sprinkler activation it is for personal curiosity and to try to get a little more insight than I can get from NFPA alone. I don't try to predict anything, I like looking at 'differences', based on RTI, Temp rating, ceiling height, and spacing. Fascinating stuff, and I'm glad you brought the 'concealer twist' to my activation curiosity Pete! thanks, Brad _____ From: Sprinklerforum [mailto:sprinklerforum- <mailto:[email protected]> [email protected]] On Behalf Of Larrimer, Peter A Sent: Tuesday, October 11, 2016 9:18 AM To: sprinklerforum@lists. <mailto:[email protected]> firesprinkler.org Subject: RE: [EXTERNAL] RE: FM and Concealed Sprinklers I can't say I know what you are using for your model, nor how you model RTI's for concealed heads and cover plates, but it sort of begs the question. Why is there a NFPA 13 reduction in design areas for LH and OH when the QR concealed head might be slower than a standard response; assuming your model results are close to accurate regarding response times. Considering that most fires are controlled with the first one or two sprinklers in LH and OH facility fires, maybe the QR vs SR isn't a big deal when it comes to required design areas? Thanks Pete _______________________________________________ Sprinklerforum mailing list Sprinklerforum@lists. <mailto:[email protected]> firesprinkler.org http://lists.firesprinkler. <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.or g> org/listinfo.cgi/sprinklerforum-firesprinkler.org -- Ron Greenman 4110 Olson Dr., NW Gig Harbor, WA 98335 [email protected] 253.576.9700 The Universe is monstrously indifferent to the presence of man. -Werner Herzog, screenwriter, film director, author, actor and opera director (1942-)
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org