Well...

when I say "225 S.F." spacing it means I modeled (1) sprinkler at a radial
distance of 7.5*1.414=~10'-8" from the center of the fire. This would be
worse case.

If I modeled 120 S.F. spacing, I would leave the fire and all conditions the
same except move the sprinkler closer to the fire, where the Temp and
velocity of the ceiling jet are higher. It is in this way that an SR could
activate sooner than a QR.  If I kept every thing except ceiling height the
same, it could be that an SR in an 8' ceiling will activate sooner than a QR
in a 12' ceiling.

 

yes i know what they say... you get garbage out... :)

i cant help but take a shot though---  i know the numbers i get are better
than some W.A.G.

 

Brad

 

  _____  

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of rongreenman .
Sent: Tuesday, October 11, 2016 1:14 PM
To: [email protected]
Subject: Re: [EXTERNAL] RE: FM and Concealed Sprinklers

 

And "quick response" is just a listing classification that could have been
called yellow and standard response elephant. If you meet the criterion for
yellow you get listed as yellow. If not you don't. I don't know if Tyco kept
of discontinued it, but Grinnell had a head listed as quick response to a
certain height and standard above that.

 

On Tue, Oct 11, 2016 at 10:58 AM, Larrimer, Peter A
<[email protected]> wrote:

"A Quick Response sprinkler does not necessarily activate sooner than a
standard response sprinkler!"  

 

You can't change all the variables.  Even that scenario shouldn't make any
difference provided the fire is in the same location below the sprinklers.
Given the same scenario (spacing, fire size, room size etc.), most would
expect that a quick response would activate quicker than a standard response
sprinkler, but I would suggest otherwise when the QR is a concealed
sprinkler.

 

You can wing the input for the cover plate response, but that is the big
issue and you know what they say when you put garbage into the model.

 

Pete    

 

From: Sprinklerforum [mailto:sprinklerforum-
<mailto:[email protected]>
[email protected]] On Behalf Of Brad Casterline
Sent: Tuesday, October 11, 2016 11:12 AM
To: sprinklerforum@lists. <mailto:[email protected]>
firesprinkler.org
Subject: RE: [EXTERNAL] RE: FM and Concealed Sprinklers

 

A Quick Response sprinkler does not necessarily activate sooner than a
standard response sprinkler!

For example, 155 SRs at 120 S.F. spacing might activate sooner than 155 QRs
at 225 S.F., be they regular pendent or concealers.

 

We are allowed to use design area reduction when the RTI is 50 (m-s)^2 or
less and it is listed as quick response, and three other conditions are met.
The RTI is the physical, non site specific property of the sprinkler, and
the 'listed as quick response' is the various spacings, ceiling heights,
etc. tested, with some kind of pass/fail citeria, which i assume includes a
range of minimum 'real' activation times.

 

I used 50 and 80 RTI for the QR and SR in the four activation times I
showed. In more detailed scenarios I have used 38 and 90 based on glass bulb
manufactures published data. I kind of winged the concealer cover plate, but
not totally-- I input specific heat, conductivity, and density for a dab of
solder, and made the plate disappear when the dab reached 135F.

 

I have been using FDS-SMV for 10 years. For sprinkler activation it is for
personal curiosity and to try to get a little more insight than I can get
from NFPA alone.

I don't try to predict anything, I like looking at 'differences', based on
RTI, Temp rating, ceiling height, and spacing.

Fascinating stuff, and I'm glad you brought the 'concealer twist' to my
activation curiosity Pete!  

 

thanks,

 

Brad

 

 

  _____  

From: Sprinklerforum [mailto:sprinklerforum-
<mailto:[email protected]>
[email protected]] On Behalf Of Larrimer, Peter A
Sent: Tuesday, October 11, 2016 9:18 AM
To: sprinklerforum@lists. <mailto:[email protected]>
firesprinkler.org
Subject: RE: [EXTERNAL] RE: FM and Concealed Sprinklers

 

I can't say I know what you are using for your model, nor how you model
RTI's for concealed heads and cover plates, but it sort of begs the
question.  Why is there a NFPA 13 reduction in design areas for LH and OH
when the QR concealed head might be slower than a standard response;
assuming your model results are close to accurate regarding response times.


 

Considering that most fires are controlled with the first one or two
sprinklers in LH and OH facility fires, maybe the QR vs SR isn't a big deal
when it comes to required design areas?  

 

Thanks

Pete


_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists. <mailto:[email protected]>
firesprinkler.org
http://lists.firesprinkler.
<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.or
g> org/listinfo.cgi/sprinklerforum-firesprinkler.org





 

-- 

Ron Greenman


4110 Olson Dr., NW
Gig Harbor, WA 98335

[email protected]

253.576.9700

 

The Universe is monstrously indifferent to the presence of man. -Werner
Herzog, screenwriter, film director, author, actor and opera director
(1942-)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to