I can’t say I know what you are using for your model, nor how you model RTI’s 
for concealed heads and cover plates, but it sort of begs the question.  Why is 
there a NFPA 13 reduction in design areas for LH and OH when the QR concealed 
head might be slower than a standard response; assuming your model results are 
close to accurate regarding response times.

Considering that most fires are controlled with the first one or two sprinklers 
in LH and OH facility fires, maybe the QR vs SR isn’t a big deal when it comes 
to required design areas?

Thanks
Pete

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brad Casterline
Sent: Saturday, October 08, 2016 11:44 AM
To: [email protected]
Subject: [EXTERNAL] RE: FM and Concealed Sprinklers


You're welcome Scott.
And Pete-- I'll be a monkey's uncle if concealers are not actually closer to 
the oven plunge tests than regular pendents in real fires! In the plunge test 
the head is plunged into a stream of air at known constant temp and velocity, 
where as in real fires the stream is the ceiling jet at growing temp and 
velocity, and varies with fire size and ceiling height. In essence, a pend is 
'sitting' in the 'oven' at ignition where ceiling jet temp=ambient and 
velocity=0. For a concealer, once the plate falls off, the ambient temp pend is 
'plunged' into a celing jet of high temp and velocity!
Here are some 'real' activation times, according to the model-- nobody knows 
what will really happen :) (for the conealers I used a 135F cover plate but was 
not very exacting about the thermophysical properties of the solder. It falls 
off at ~82 seconds):

10 ft ceiling height, 225 s.f. spacing, LH Heat Release Rate Per Unit Area 
(1700kW/m^2):

155F QR Pend= 90 sec.
155F QR Concealer= 106 sec.
155F SR Pend= 101 sec.
155F SR Concealer= 116 sec.

Brad
On Oct 7, 2016 3:43 PM, "Scott Holman" 
<[email protected]<mailto:[email protected]>> wrote:
Thank you all for your responses! I enjoyed reading the conversation so much I 
forgot I had asked the question.

Regards,

Scott H

From: Sprinklerforum 
[mailto:[email protected]<mailto:[email protected]>]
 On Behalf Of rongreenman .
Sent: Friday, October 7, 2016 1:34 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: FM and Concealed Sprinklers

I don't think what the value of the rule is, or how it's determined or any 
other thing than what's required is germane to the discussion. If the AHJ wants 
squealing raccoons glued to the ceiling and FM wants quiet ones you have the 
problem of serving two masters. When they've both already decided what type of 
raccoon they demand logic entreaties to them will get a nod of acceptance from 
the one you agree with and  an harrumph from the other. you just need one to 
back off this time. That's it. After that you can go present your arguments to 
the International Raccoon Society and/or Raccoon Underwriters and try to get 
them to agree to a common requirement under all circumstances.

I heard that FM changed their co-effcients for hydrant test to coincide with 
NFPA's. How did that get fixed and why not the other way. It would be easiest 
to just use FM as it met the needs of both masters but what if doing so was the 
difference between a pump or not. You'd be best serving your other master, the 
owner, by getting a waiver from FM.


On Fri, Oct 7, 2016 at 12:54 PM, Larrimer, Peter A 
<[email protected]<mailto:[email protected]>> wrote:
Interesting topic.

In my humble opinion, the UL 199 tests to qualify concealed sprinklers as quick 
response is extremely questionable!  On the other hand, what do you think you 
are getting when you install a quick response sprinkler anyway?  Effectively, 
the UL 199 test requires the concealed sprinkler to be plunged into the test 
chamber exactly like the pendent sprinkler to get the RTI rating.  As far as I 
know, another test used by UL to measure the response time for a concealed 
sprinkler is to seal up a test room and force the heat of the test fire up 
through the sprinkler cover plate to measure response time.  Neither of those 
tests used by UL to qualify a concealed head as quick response reflect the 
conditions in the field that a concealed head would likely encounter.
I am not suggesting that concealed sprinklers won’t operate, but I would be 
willing to bet that they won’t go off any faster than a standard response 
sprinkler unless the conditions are such that the heat will be forced up 
through the cover plate, and that won’t often be the case.


In addition, concealed sprinklers are not permitted by their listing to be 
installed in rooms where the space above the ceiling is at a higher pressure 
than the pressure in the room below.  One manufacture states “NOTE: Concealed 
sprinklers must be installed in neutral or negative pressure plenums only.”  
That requirement can significantly limit the installation opportunities for 
those of us in the healthcare industry because we have many negative pressure 
rooms that are required for infection control purposes and installing a 
concealed head would be inappropriate (though it happens quite often).  Have 
the installers out there ever asked which rooms were designed to negative 
pressure requirements prior to installing the sprinkler system?

We had one instance where we found out after the fact, that we evidently had 
leaking duct work in the plenum space above a ceiling and the pressure in the 
space above the ceiling was enough to have the soot line from a patient bed 
fire blacken the walls down to a foot off the floor even though we had a quick 
response sprinkler in the room.  The air leaking from the plenum space left a 
little white line around the cover plate of the concealed sprinkler and the 
quick response sprinkler didn’t operate at all.

I am not saying concealed sprinklers are especially bad, but I would not 
consider them to be quick response even when listed as such by UL.  Maybe that 
is why there aren’t any FM Approved quick response sprinklers?  When somebody 
makes a concealed sprinkler that gets an FM Approval for quick response, then I 
would feel more comfortable that the sprinkler will actually operate faster 
than a standard response.  There are FM Approved standard response sprinklers, 
and FM has a test for quick response concealed sprinklers, but since nobody has 
a FM Approved concealed sprinkler on the market, it might make you wonder if 
their test might be more realistic.

VA sprinkler specifications require FM approved quick response sprinklers (not 
UL listed) for new projects.  Thus, no concealed sprinklers should be going 
into any VA Medical Centers.  We have negative pressure rooms and hope to get a 
quicker response from the sprinklers.

Have a good weekend.

Pete Larrimer
VA

PS.  By the way Todd, my bet is that it isn’t a tie especially if a concealed 
sprinkler is involved.  My guess is that, in an open room, a standard response 
pendent sprinkler will operate faster than a quick response concealed sprinkler.



From: Sprinklerforum 
[mailto:[email protected]<mailto:[email protected]>]
 On Behalf Of John Drucker
Sent: Friday, October 07, 2016 8:00 AM
To: 
[email protected]<mailto:[email protected]>
Subject: [EXTERNAL] RE: FM and Concealed Sprinklers

From a code compliance standpoint Underwriters Laboratories is one of appx 22 
Nationally Recognized Testing Laboratories (NRTL).  Interestingly UL 199, 1626 
etc. are the defacto standards for fire sprinklers which any of the other 
NRTL’s would use to test and list a fire sprinkler (aside from perhaps FM 
Global)  should they choose to do so. So it’s not really UL itself but rather 
does the sprinkler comply with the applicable UL Standard. A UL Listed Quick 
Response Fire Sprinkler is a listed quick response fire sprinkler.

As for insurance companies and what they want well ask them, so long as it 
meets the applicable code its code compliant.

John Drucker, CET
Assistant Construction Official
Fire Protection Subcode Official
Electrical Subcode Official
Building Inspector
Borough of Red Bank, NJ
90 Monmouth Street
Red Bank, New Jersey 07701
Cel/Text: 732-904-6823<tel:732-904-6823>
Email: [email protected]<mailto:[email protected]>






From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Morey, Mike
Sent: Thursday, October 06, 2016 9:24 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: FM and Concealed Sprinklers

I still don’t see why you’d need a variance, real world example, my apologies 
for not being brand agnostic but for this exercise its hard to avoid but I 
think most brands have similar offerings:

Reliable G5-56 with G4 plate, UL listed Quick response, FM listed Standard 
response.  FM does not require Quick response, so the fact they don’t accept it 
as QR is irrelevant.  Your real world AHJ should accept the UL listing.

On Oct 6, 2016, at 7:57 PM, Travis Mack, SET 
<[email protected]<mailto:[email protected]>> wrote:


Your argument is a moot point.  It is about FM approval.  FM does not have 
approval for those sprinklers.

You have to get a variance from the FM reviewer.  Then you may be battling an 
AHJ that says they don't recognize FM and you have to follow NFPA 13 criteria.  
These are real world scenarios that come into play daily for many of us.

Not everything comes down to 15 significant figures and exponents to the 1000th 
power.  Sometimes it is just dealing with what is available and playing the 
game.

Travis Mack, SET

MFP Design, LLC

2508 E Lodgepole Drive

Gilbert, AZ 85298

480-505-9271<tel:480-505-9271>

fax: 866-430-6107<tel:866-430-6107>

email:[email protected]<mailto:email:[email protected]>



http://www.mfpdesign.com<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesign.com%2F&data=01%7C01%7Csholman%40rlhfp.com%7C97c342b457be438dc9dc08d3eef169e7%7C5b96a743f74947d78e3af7ba92a15e59%7C1&sdata=t7pfwoWGkFjdo6wGInGHTl1R%2FrVSJ%2BLTE46%2BY2jTTjk%3D&reserved=0>

https://www.facebook.com/pages/MFP-Design-LLC/92218417692<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2Fpages%2FMFP-Design-LLC%2F92218417692&data=01%7C01%7Csholman%40rlhfp.com%7C97c342b457be438dc9dc08d3eef169e7%7C5b96a743f74947d78e3af7ba92a15e59%7C1&sdata=yHIhI1mDbEjCJKfmxCZc2th8f7VMSCkfVQObj4dWKfI%3D&reserved=0>

Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=01%7C01%7Csholman%40rlhfp.com%7C97c342b457be438dc9dc08d3eef169e7%7C5b96a743f74947d78e3af7ba92a15e59%7C1&sdata=CJeH0pnwfImdDmhnxIL789DpnuRUBGiyrF%2Bu8PrizVY%3D&reserved=0>

LinkedIn: 
https://www.linkedin.com/in/travismack<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=01%7C01%7Csholman%40rlhfp.com%7C97c342b457be438dc9dc08d3eef169e7%7C5b96a743f74947d78e3af7ba92a15e59%7C1&sdata=YSrcNlvjZyJdb4O5pclmRfMxdLtXvhNh7uWllLhE3UY%3D&reserved=0>
On 10/6/2016 4:52 PM, Brad Casterline wrote:

Which activates quicker, in an LH, ~10' ceiling, 225 s.f. spacing:
200F QR, or,
155F SR?

SURVEY SAID!

it's a tie.

I.O.W., I.M.H.O., (opinion being entire weekends spent jacking with it bcoz i 
been divorced for 16 years and the kids are grown and on their own)

activation is more about ceiling height, temp rating, and spacing than QR vs SR.
On Oct 6, 2016 6:39 PM, "rongreenman ." 
<[email protected]<mailto:[email protected]>> wrote:
The problem with FM allowing something like SE where NFPA requires QR is that 
the AHJ may require compliance to NFPA. You then playing to two masters and 
which one will give. Probably FM  but you have to get approval and ad was 
earlier stated your best served by getting it in writing.

On Thursday, October 6, 2016, Todd Williams 
<[email protected]<mailto:[email protected]>> wrote:
[cid:[email protected]]
I am working on a hospital job that is FM. FM was very good about allowing us 
to use concealed QR (even concealed sidewalls). However, it needs to be run 
past their loss control peeps to make sure they are OK with it.
Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080<tel:860-535-2080> (ofc)
860-608-4559<tel:860-608-4559> (cell)

via Newton 
Mail<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fcloudmagic.com%2Fk%2Fd%2Fmailapp%3Fct%3Dti%26cv%3D9.1.9%26pv%3D9.3.5%26source%3Demail_footer_2&data=01%7C01%7Csholman%40rlhfp.com%7C97c342b457be438dc9dc08d3eef169e7%7C5b96a743f74947d78e3af7ba92a15e59%7C1&sdata=eiXWSVBv0EILfXwXxNByc9oOdpFzdZlR2f5TaoMpQDM%3D&reserved=0>

On Thu, Oct 6, 2016 at 7:23 PM, Morey, Mike 
<[email protected]<mailto:[email protected]>> wrote:
If you look at data sheet 2-0, FM doesn’t require QR heads in HC-1, 2 or 3 if 
you use k5.6 standard coverage heads at least. And last I looked there are a 
number of QR concealed heads that are FM approved, only as standard response. 
Since your AHJ presumably uses NFPA/UL, they’re QR heads, and since FM doesn’t 
care, it’s fine that they accept them only as standard response. Since our 
client is all FM it’s always a picnic trying to design systems that satisfy 
both because it’s easier to deal with the AHJs without having to explain the FM 
design criteria in detail (they do accept them when its an issue though).

> On Oct 6, 2016, at 6:29 PM, Mark Phillips 
> <[email protected]<mailto:[email protected]>> wrote:
>
> Just ask their rep for a variance in a written letter.
>
> Have done many a hospital this way.
>
> Sent from my Verizon 4G LTE Droid
> On Oct 6, 2016 6:13 PM, Scott Holman 
> <[email protected]<mailto:[email protected]>> wrote:
>
> Hello All,
>
>
>
> I have an FM job where the customer wants concealed sprinklers in light 
> hazard occupancies. Since it is light hazard, quick response sprinklers are 
> required. However, FM does not have any approved quick response concealed 
> pendents that I could find. Has anyone dealt with this before?
>
>
>
> Thank you for your input!
>
>
>
> Scott H.
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]<mailto:[email protected]>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&data=01%7C01%7Csholman%40rlhfp.com%7C97c342b457be438dc9dc08d3eef169e7%7C5b96a743f74947d78e3af7ba92a15e59%7C1&sdata=c020XYl6Lr%2Fo6AOLBWIdSYB0xzdT5u8xs49XDQAFvtc%3D&reserved=0>

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&data=01%7C01%7Csholman%40rlhfp.com%7C97c342b457be438dc9dc08d3eef169e7%7C5b96a743f74947d78e3af7ba92a15e59%7C1&sdata=c020XYl6Lr%2Fo6AOLBWIdSYB0xzdT5u8xs49XDQAFvtc%3D&reserved=0>


--
Sent from Gmail Mobile

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&data=01%7C01%7Csholman%40rlhfp.com%7C97c342b457be438dc9dc08d3eef169e7%7C5b96a743f74947d78e3af7ba92a15e59%7C1&sdata=c020XYl6Lr%2Fo6AOLBWIdSYB0xzdT5u8xs49XDQAFvtc%3D&reserved=0>


_______________________________________________

Sprinklerforum mailing list

[email protected]<mailto:[email protected]>

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&data=01%7C01%7Csholman%40rlhfp.com%7C97c342b457be438dc9dc08d3eef169e7%7C5b96a743f74947d78e3af7ba92a15e59%7C1&sdata=c020XYl6Lr%2Fo6AOLBWIdSYB0xzdT5u8xs49XDQAFvtc%3D&reserved=0>

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&data=01%7C01%7Csholman%40rlhfp.com%7C97c342b457be438dc9dc08d3eef169e7%7C5b96a743f74947d78e3af7ba92a15e59%7C1&sdata=c020XYl6Lr%2Fo6AOLBWIdSYB0xzdT5u8xs49XDQAFvtc%3D&reserved=0>


_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&data=01%7C01%7Csholman%40rlhfp.com%7C97c342b457be438dc9dc08d3eef169e7%7C5b96a743f74947d78e3af7ba92a15e59%7C1&sdata=c020XYl6Lr%2Fo6AOLBWIdSYB0xzdT5u8xs49XDQAFvtc%3D&reserved=0>



--
Ron Greenman

4110 Olson Dr., NW
Gig Harbor, WA 98335

[email protected]<mailto:[email protected]>

253.576.9700<tel:253.576.9700>

The Universe is monstrously indifferent to the presence of man. -Werner Herzog, 
screenwriter, film director, author, actor and opera director (1942-)

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to