They are requiring a 2.5" FHV inside at the man doors 100 ft. apart. The
building is sprinklered 35 ft. high 300k sqft S1 (warehouse).

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of R
Richardson
Sent: Monday, February 05, 2007 1:34 PM
To: [email protected]
Subject: Re: IFC 503.1.1 Fire Apparatus Access

Technically they may be correct.  THe 2003 IFC requires the fire
apparatus to be within 150 ft. of all portions of the facility and all
portions of exterior walls of the first story of the building. 

We tend to allow a significant increase in the 150 ft. when sprinklered,
and have on occasion required a exterior "horizontal"
standpipe, or yard standpipe as mitigation for the long hose lays
required, but have never triggered a building standpipe.  It is a rare
firefighter that would expect a building standpipe in building less than
4 stories in height, and an even rarer firefighter that would use such a
connection if it is not in a protected enclosure accessed via a
protected passageway.

Are they requiring protected access to the hose connections, or are
these simply mid-floor hose connections.

Rich Richardson
Seattle Fire Department

>>> "Fletcher, Ron" <[EMAIL PROTECTED]> 02/05/07 12:20 PM >>>
503.1.1 "The fire apparatus access road shall comply with the
requirements of this section and shall extend to within 150 feet of all
portions of the facility and..."
 
We have a local AHJ that is requiring a Class I standpipe when all
"interior" portions of a facility are not within 150 ft.
 
A few questions.
 
Does the access requirement of 150 ft to "all portions of the facility"
refer to exterior or interior?
 
Is anything in writing like an official/unofficial interpretation?
 
What do AHJ's do when the access dimension cannot be accomplished?
 
P.S. Building in question is S1 300 ft. x 1025 ft.
 
Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum