Rich,
"belts, hoses"
"There are filters, including fuel, oil, air, water, and hydraulic types,
all sizes and shapes."
Any plastic filters??
How much of the above? Remember NFPA 13, 2002, section 5.6.1.2.3, mixed
commodities u are allowed 10 pallet loads in a 40K whse, u half this amount
so u are now at 4-5 pallet loads. More then 5 and u have to protect the
ENTIRE whse at the higher commodity. IF u design for a class 2 commodity,
now u are allowed 2 pallet loads! see (3) in the NFPA section above.
This material could be classified as a Grp A Plastic.
Regards
Tom LaCorte
Chubb Insurance
Check out our web site for hands- on fire protection training.
http://www.chubb.com/businesses/service/chubb5999.html
From: "Jeff Hewitt" <[EMAIL PROTECTED]>
Reply-To: [email protected]
To: <[email protected]>
Subject: Re: Determining a Warehouse Commodity Classification
Date: Tue, 6 Feb 2007 13:56:56 -0600
You mentioned wood crates. You did not mention if there are any pallets
involved. If there are any plastic pallets involved you may have to
increase the commodity class.
Jeff Hewitt, PE, SET, SFPE (Prof. Member)
Corporate Engineer
Bi-State Fire Protection Corporation
636-946-0011
636-946-5172 (FAX)
This e-mail and any attachments are CONFIDENTIAL and may be protected by
one or more legal privileges. It is intended solely for the use of the
addressee identified above. If you are not the intended recipient, any
use, disclosure, copying or distribution of this e-mail is unauthorized.
If you received this e-mail in error, please notify the sender immediately
at the above captioned address.
----- Original Message ----- From: "Lindner, Richard"
<[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Tuesday, February 06, 2007 11:42 AM
Subject: Determining a Warehouse Commodity Classification
(I seem to have lost access to the archives, so I can't research this..)
I am involved in an initial design (performance spec) for a warehouse type
project consisting of a butler building approx. 300'x60' and 35' high in
size (18,000 sq. ft.). Approx 7000 sq. ft. of floor area will consist of
25' high rack storage that is 42" deep with a 12" space and then another
42" deep rack. There are 5 racks of this arrangement with an aisle at
minimum 9'-6" width between them. The shelving itself is wire decking.
The center part of the building has some administrative area offices and
other storage areas (no shelving shown). The other end of the building is
a maintenance garage for repairs of vehicles.
We have asked about what they intend to store on the shelving and have been
told that primarily they are storing spare machinery parts, some of which
are in wood crates; these are small, medium, large and very large. These
include hydraulic cylinders, engines, transmissions, radiators, air
chambers, pumps, belts, hoses, fittings, nuts, bolts (small items are in
cardboard boxes in most cases), and tools (both power and non-power tools).
Aerosol cans include brake cleaner, starting fluid, lubricant (WD-40),
window cleaner, and paint. They carry no more than two cases (24 cans) of
each item in stock. There are filters, including fuel, oil, air, water,
and hydraulic types, all sizes and shapes. They also store spare
pre-charged batteries. These are heavy equipment batteries; (2) large, (2)
medium and (4) small are typically all they have on hand.
We feel the rack storage area is our most demanding area. We have reviewed
our options and feel that Commodity Class II would be appropriate based on
the above information. Does anyone see something that might reflect using
a different classification?
Appreciate any response.
Richard
Richard K. Lindner
Plumbing Senior Designer
Morris, Johnson & Associates, Inc.
611 Industrial Way West
Eatontown, New Jersey 07724
P: 732-380-1100 ext. 4186 | F: 732-380-1111
[EMAIL PROTECTED]
www.morrisjohnson.com
--------------------------------------------------------
This message contains confidential information and is intended only for the
individual named. If you are not the named addressee you should not
disseminate, distribute or copy this e-mail. Please notify the sender
immediately by e-mail if you have received this e-mail by mistake and
delete this e-mail from your system. E-mail transmission cannot be
guaranteed to be secure or error-free as information could be intercepted,
corrupted, lost, destroyed, arrive late or incomplete, or contain viruses.
The sender therefore does not accept liability for any errors or omissions
in the contents of this message, which arise as a result of e-mail
transmission. If verification is required please request a hard-copy
version.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_________________________________________________________________
Laugh, share and connect with Windows Live Messenger
http://clk.atdmt.com/MSN/go/msnnkwme0020000001msn/direct/01/?href=http://imagine-msn.com/messenger/launch80/default.aspx?locale=en-us&source=hmtagline
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum