A real-world example:
Just a couple of years ago there was a situation at an auto parts
warehouse. Fully sprinklered, adequate for the commodity and storage
arrangement. Water supplied by a fire pump. Because of concerns that
system might leak, even though it was relatively new with no sign of
problems, the discharge valve was always shut before the weekly run of
the fire pump.
You can guess what comes next. There was a fire, the pump starts up, and
the system is subjected to pump pressure for the first time. A coupling
in a large main let go and the water the sprinklers needed went out the
open main instead, and the warehouse burned to the ground. The loss was
in the 8 figure range.
The moral of the story is that if you are afraid to pressurize the
system when there is no fire, you ought to be terrified of what could
happen if there is a fire.