A combined system needs to be valved so that sprinklers and standpipe(s) can be independently controlled, whether it's two separate risers or a combination standpipe riser with sprinkler connections however it's zoned. And since it's a code thing regarding the hoses, can we take the exception from 14 for a fully sprinklered building, where you simply omit the hose in favor of a 2.5" x 1.5" reducer and cap?
I think that the presence of hose stations on stages and in A-2 and A-3 occupancies is not congruent with the accepted practice of encouraging EVERYONE in the building to leave in case of a fire alarm or sign of fire. I would ask the serving fire dept. if they can live with points of connection and bring their hose for mop up. Steve L. -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] Behalf Of Roland Huggins Sent: Monday, March 26, 2007 7:38 AM To: [email protected] Subject: Re: Stage Hose Stations Look at 905.3.4 (03 ed). It says: Class III standpipe with outlets on both sides of the stage and hose for the 1.5 in outlet shall shall have sufficient length to provide protection of the stage (which I would say either side should reach the other side - would be nasty to go charging out there nozzle in hand and hit the end half way across the stage LOOKING LIKE CHARLIE BROWN TRYING TO KICK THE FOOTBALL). The question I have is the the allowance to supply it from the sprinkler system. Is the water demand combined since it is more than the common riser combined system (where it is NOT combined)? Roland On Mar 26, 2007, at 8:16 AM, Thom McMahon wrote: > We have a stage of 1066 SF , no Proscenium, (over the 1000 SF for > hose stations required by 2003 IBC) Is there any info on the > following: > 1) Minimum hose in Cabinet for a stage only 55 FT across (50' 75' > or 100') > 2) With hose stations on both sides of stage, should we calc each > at 250 Gpm, since the highest elevation is the same, thereby > getting the 500 Gpm total at the highest elevation? > 3) Any other special considerations for these hose stations, or stage? > > Thom McMahon > Firetech, Inc. > 2560 Copper Ridge Dr > Steamboat Springs, CO 80488-2136 > Tel: 970-879-7952 > Fax: 970-879-7926 > ----- Original Message ----- > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum