Since you don't care about building codes do you omit the sprinkler
heads from balconies of apartments buildings in jurisdictions that have
adopted the 2003 IBC because the NFPA 13R says you can?
 
Trever Williams
Unlimited Sprinkler Fire Protection

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bill
Minkel
Sent: Tuesday, April 03, 2007 2:58 PM
To: [email protected]
Subject: RE: Sprinkler Design

 
I do Sprinkler Design for a Sprinkler Contractor. I design to NFPA-13.
Don't
know building codes, don't care building codes, that's for the Architect
or
Engineer of Record. I put a sidewall in every elevator pit with a
tampered
"Butterball" on the branch. If NFPA-13 says do something I do it and I
don't
worry about the plumbing inspector, the electrical inspector, the
building
inspector. I do worry about the Fire Marshall Inspector.