If the data had REAL value they would want it protected by some means.
No protection guarantees the total loss of the data. I'd agree with
Brian, it's just the age old misconception of those drippy, leaky
sprinklers ruining their equipment. 

And the 20G P.A. system, yeah that makes sense.  It's all a matter of
value.  But I wonder if those people ever heard of off-site system
backup storage.  I think I'd be looking at something if it was that
valuable.


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg
McGahan
Sent: Friday, August 03, 2007 10:13 AM
To: [email protected]
Subject: RE: Telecom & Data Rooms

How much is the data worth to them though? That may be the problem.

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Friday, August 03, 2007 9:08 AM
To: [email protected]
Subject: RE: Telecom & Data Rooms

My situation is a little different though, they don't want any heads in
the Telecom/Data rooms. That's what I have a problem with.


 


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg
McGahan
Sent: Friday, August 03, 2007 10:01 AM
To: [email protected]
Subject: RE: Telecom & Data Rooms

I have to disagree. We were asked to quote a pre-action system for a 2
head room in an investment firm's office one time and I responded much
as many of you have on this issue. The reply was that if there servers
got ruined by water and they had to be replaced they were looking at a
cool million dollars in HARDWARE alone. So spending 10-20 G on a
preaction system is not a big deal to them when they consider the risk,
however small, that someone could break a sprinkler. 

With that said, if it was my million dollars, 20G would seem like a
small price to pay.
Greg

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Friday, August 03, 2007 8:09 AM
To: [email protected]
Subject: RE: Telecom & Data Rooms

That's the best compliment I've gotten in quite awhile.... 


 


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Friday, August 03, 2007 9:07 AM
To: [email protected]
Subject: RE: Telecom & Data Rooms

That's because you're not tHinKing like an Architect.   ;) 


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Friday, August 03, 2007 9:01 AM
To: [email protected]
Subject: RE: Telecom & Data Rooms

IMHO I don't see a Telecom Room squeaking by as an Electrical room
either, at this point the pipe and heads are installed and I have no
plans to remove them.


 


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Chris
Cahill
Sent: Thursday, August 02, 2007 4:48 PM
To: [email protected]
Subject: RE: Telecom & Data Rooms

See IFC 904.2, if you don't sprinkler the room and have an alternate
agent you have an UNSPRINKLERED building.

IFC 903.3.1.1.1 I don't see allows omission.  IFC usually supersedes
NFPA 13 exception. Code vs. standard in legal lingo.  AHJ interp.
required to determine if electrical room in NFPA 13 exception is
overruled by IFC 903.3.1.1.  And also as I think you imply is a telecomm
room an electrical room.  I say no and sprinkler the room but like the
rest of the forum have a biased opinion for sprinklering everything. 


Chris 




-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Thursday, August 02, 2007 8:06 AM
To: [email protected]
Subject: Telecom & Data Rooms

I'm being told by an Architect we are doing a school with that I need to
remove any heads from the Telecom & Data rooms and that I'm not allowed
to run any pipe above those ceilings either. He is basing it on the
provisions for eliminating heads in and Electrical room with a 2 hour
fire wall, am I missing something? I am not aware of Telecom & Data
rooms falling into the same category as an Electrical room. I have
approved plans from the AHJ with the heads shown in those rooms and
omitted from the Electrical rooms. Any thoughts?
 

 

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to