Until I read NFPA 2002-13 A3.7.1 (1) I agreed that is unobstructed. But this particular definition is the closest thing to this type of construction. It makes a big difference when you try to put EC sprinklers in a warehouse classified as OH Group II and one listing says unobstructed construction only and another company's listing on the similair sprinkler is UL listed for non-combustible obstructed construction.
On a second note my AFSA Fire Sprinkler School Book states that it is obstructed construction although most AHJ's will consider it unobstructed. Bobby Gillett Project Manager [EMAIL PROTECTED] (731)-424-0130 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of A.P.Silva Sent: Thursday, October 18, 2007 3:03 PM To: [email protected] Subject: RE: purlins UNOBSTRUCTED Steel deck is supported on purlins and purlins supported on beams perpendicular to the purlins. There is no pocket to trap the heat. So unobstructed. Tony -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan Sent: October 18, 2007 12:45 PM To: [email protected] Subject: purlins Poll: Are typical 8" and 10" purlins spaced 4-5' apart with open space above the beams where the purlins rest considered OBstructed or Unobstructed construction? Living Water Fire Protection, LLC 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 Fax: 850-937-1852 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)