How about taking any reference whatsoever out of 13D/13R including the annex
material and handbooks to the word "property".  Yes both standards at 1.2
Purpose use the phrase "improved protection against injury, life loss, and
PROPERTY DAMAGE".  ah carumba ! 

Additionally when the 13R handbook commentary makes statements about "lesser
degree of property protection" it only confusses the issue. Just what is
lesser ?. 

The same can be said for the 15 min thermal barrier exception. Had one just
the other day were the sprinkler designer took the liberty only to have the
field inspector note the barrier was missing and no head in the bathroom to
which the builder replied, "these guys are killing me, why didnt they just
put the %$#*& sprinkler head in !." Take that exception out of the standard
please its more trouble then its worth.

Someone mentioned about rocket science. Unlike rocket science theres no
bizzilion dollar payload, government sponsored exploration or unlimited
defense budget. Sprinklers plain and simple have got to be cost effective. 

John Drucker
Fire Protection Subcode Official (AHJ)
New Jersey


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Steve Leyton
Sent: Tuesday, February 26, 2008 8:29 PM
To: [email protected]
Subject: RE: 2nd request 13d attic storage

Don't even kid about that.   We have plenty of jurisdictions here in CA
that require fully sprinklered attics and then there's the .15 density
in garages.  Don't get me started.   

13D and 13R very specifically disclaim that they are both life-safety
standards.   Sure, we might all want sprinklered attics, but we'll be
shooting ourselves in the foot if we push for that and frankly, I'm
always at the ready to argue AGAINST such changes if they're proposed.
Leave 13D the way it is.   Why?  Because it continues to feed the fire
regarding costs and homebuilders continue to hold the upper hand in that
argument.   Let's say IRC adopts sprinkler requirements - any state can
amend the model code and not adopt that provision if they so choose.
Why give them more ammo?


Steve Leyton
Protection Design & Consulting


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ron
Greenman
Sent: Tuesday, February 26, 2008 1:49 PM
To: [email protected]
Subject: Re: 2nd request 13d attic storage

Rick,

Require 13 systems in SFDs and you get your wish. Make it apply to
buildings over X sqft and keep 13D for buildings under x sqft. Don't
make 13D something it isn't.

On 2/26/08, Matsuda, Richard <[EMAIL PROTECTED]> wrote:
> There was a "slight" code change between the 1996 and 1999 editions of
>  NFPA-13D, paragraph 4-6, exception #4.
>
>  It changed from stating, "...not required in attics, crawl spaces,
and
>  other concealed spaces that are not used or intended for living
purposes
>  or storage"...to ..."not required in attics, crawl spaces, and other
>  concealed spaces that are not used or intended for living purposes".
>
>  The committee omitted the words "or storage" which makess it seem
that
>  they accept that most attics would be used for storage and sprinklers
>  would not be required. They have since changed the wording again in
the
>  2007 edition, par 8.6.5 to state "...and do not contain fuel-fired
>  equipment".
>
>  Some big homes that we have in Dallas have a standard doorway into
the
>  attic which is decked with lighting provided, but it's not
conditioned
>  space and no walls or ceilings are provided. It's just open to the
roof
>  joists. Per the wording of 13D, we allow sprinklers to be omitted.
>
>  I don't agree with this position cause I'd like to have sprinklers in
>  every attic, bathroom, closet and dog house, but until changes are
made
>  again I will abide with the committee's decisions.
>  rick matsuda, city of dallas
>
>
>  -----Original Message-----
>  From: [EMAIL PROTECTED]
>
> [mailto:[EMAIL PROTECTED] On Behalf Of Steve
>  Leyton
>  Sent: Tuesday, February 26, 2008 2:55 PM
>  To: [email protected]
>
> Subject: RE: 2nd request 13d attic storage
>
>  But does your attic have a pull-down or fixed stair?   All good
points
>  Todd, which underscores how subjective this issue really is.  If it's
a
>  storage "room", I'd consider it part of the dwelling unit.  If it's
dead
>  space above the ceiling in which the home owner chooses to put stuff,
>  then it quacks like an attic.
>
>  Steve Leyton
>  Protection Design & Consulting
>
>
>  -----Original Message-----
>  From: [EMAIL PROTECTED]
>  [mailto:[EMAIL PROTECTED] On Behalf Of Todd
>  Williams - FPDC
>  Sent: Tuesday, February 26, 2008 12:31 PM
>  To: [email protected]
>  Subject: Re: 2nd request 13d attic storage
>
>  13D says that sprinklers in attics may be omitted, provided they are
>  not intended for "living purposes". Does storage in an attic space
>  constitute a living purpose? I'm not sure if it does or not. I would
>  think that a case could be made, considering that 13D is a Life
>  Safety System. (My assumption here is that the access to the space is
>  more on the idea of a pull-down stair as opposed to a carpeted
>  staircase.)
>
> _______________________________________________
>  Sprinklerforum mailing list
>  [email protected]
>  http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>  To Unsubscribe, send an email
to:[EMAIL PROTECTED]
>  (Put the word unsubscribe in the subject field)
>


-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to