Mike,
I totally agree with the points you make.  

1. I can' tell you how many bid packages I looked at where the directive
on fire protection was "Install Sprinklers per NFPA 13". Good grief, be
a bit more imaginative.  If you don't know how to figure it out, find
someone that can.

2. Too often AE firms will dump the responsibility of determining water
supplies on the contractor.  At that point in the project discovering a
deficient water supply can have serious impact financially and on the
schedule.  As the engineer of record, make sure FIRST to ask for water
supply data and then SECOND, make sure it's recent.  Should be no older
than 6 months in some jurisdictions but the closer the date of the test
to the date of your drawings being issued the better.  Next thing is to
look at the numbers.  Here's where there's often a hang-up.  Recent case
in point was a water test where there was 135 psi static, 40 psi
residual and 900+/- gpm.  Now we knew that in an older test the supply
was far more favorable and the difference between static and residual
was a bit dramatic.  We asked for the test to be redone,  when it was,
it was found that the system had a lot of sediment in it, as that was
flushed out the final results were more in our favor with residual
coming up to around 80 psi with over two times the flow.  Don't take the
report at face value, look at it and ask questions if it looks funky.
Generally in a municipal situation the local water or fire departments
will do the test.  On a private system someone may need to be hired to
do the test.  Just don't dump it off because it take a bit too much work
to get the information.

3. This can be a tough one, especially for most AE firms.  Since the
industry standard deliverable from most AE firms is a usually a concept
drawing with no pipe routing and since most people producing these types
of drawings have little to no hydraulic calculation experience, it might
be a bit much to expect.

4. This kind of ties into 3.  With the AE firms deciding not to do
detailed engineering on fire protection, (why do it when the contractor
is going to do it again and he does it for free, "that's usually the
response when detailed design is mentioned"), it is usually left to the
contractor's design team do get the necessary drawings and perform the
coordination.  What seems to be the issue it time.  Since the FP systems
often need to be reviewed by the EOR, AHJ's, Underwriters and the like,
there needs to be time for all this to occur.  So the FP contractor
issues a layout drawing.  Often but not always, the system designs are
not coordinated with other trades as this becomes a field function.  If
you're lucky the AE firm has made space provisions for the sprinkler
systems but that doesn't always happen.  Please don't thing the FP guy
in that AE firm didn't try, it's just that many times other disciplines
don't understand the restrictive nature of fire protection system
installation.  But overall coordination of systems becomes a field
issue.  


We all have to work together, AE, EOR, Contractor, AHJ, to make this
work.  We should all have the same goal at the end of the day, save
lives, save property and NOT make the disaster section of the 6:00 news.



Craig L. Prahl, CET   
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Mike
Brown (TECH- GVL)
Sent: Thursday, April 24, 2008 9:15 AM
To: [email protected]
Subject: RE: What is a Bucket Test?

Actually, in several counties around Atlanta, the test was also required
for garden style apartments up to four stories.  You would be surprised
that, at least in the beginning, a number of projects that had full
blown hydraulic calculations failed when the bucket test showed them to
be incorrect.  Many times the main culprit was a water test supplied by
the water company that was faulty or not up to date.  Which brings me to
my point that I have made over the years, the "design" of sprinkler
systems really involves four major decisions by the design engineer and
the rest is mostly a layout of a system within the rules of the codes.

First Engineering Decision:     What is the hazard and what densities
are required.  The project must be classified as per the fire risk. What
are you protecting and how much water will it require to achieve the
fire protection objective.

Second Engineering Decision:  What is the water supply and has there
been a detailed analysis and testing of the water supply?  Generally,
engineers and others rely on water tests provide by others and sometimes
incorrect and out of date. Often very little time is devoted by the
engineer to insure that an adequate water supply at the needed pressure
is available.  This does not mean just throwing in a large fire pump
just to be safe.

Third Engineering Decision:  Where is the remote area?  It is easy to
just let the designer decide but the selection of the remote area can
change the hydraulics dramatically.

Fourth Engineering Decision:  Coordination and review of the plans. The
shop drawings and calculations may be checked and the coordination with
the other trades on the project.  Often, the engineer just passes these
functions to a trainee or someone else within the engineering firm. In
other cases the issue is just ignored.

Too often these decisions are not given the time and effort that they
deserve.


Michael L. Brown
Manager of Technical Services
The Reliable Automatic Sprinkler Company, Inc.'
[EMAIL PROTECTED]
www.reliablesprinkler.com
(864) 843-5228

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to