In the past we have done similar test in the UK albeit on High velocity systems in Power Stations. Our guys were very excited when they got results consistent with the calculations but were somewhat deflated when I pointed out that the calculations were done with a Hazen-Williams constant of 120 which allows for some years of pipe degradation so the results should have been better with new pipe!
Pip Males CAD Manager (FIRECAD) Tyco Fire & Integrated Solutions Tyco Park Grimshaw Lane Newton Heath Manchester UK M40 2WL -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of IPA Sent: 09 April 2008 20:47 To: [email protected] Subject: Re: What is a Bucket Test? What kind of variance in calcs from actual bucket test results are considered acceptable? I'm just curious since taking out the head and flowing straight from a 1/2" threaded outlet vs. flowing a 7/16" orifice (like a 4.2k sprinkler w/ element removed) could possibly work in your favor to a small degree but could also work against you depending on what k-factor of sprinkler you used. In a 13R bucket test do you actually remove more than one sprinkler and flow up to four? Or is it always just one? Seems like a source calc w/ one sprinkler flowing would make more sense if you're only required to bucket test one sprinkler... -B- On 4/9/08, Todd Williams - FPDC <[EMAIL PROTECTED]> wrote: > > If you have a really bad water supply, instead of a pitot you use a > 5-gallon bucket and a stop watch. 8-) > > > At 02:19 PM 4/9/2008, you wrote: > > > This is the first time I've heard it being done for 13R. 13D, yes. But > > not > > 13R. Are there other jurisdictions requiring a bucket test for 13R? > > > > Tony > > > > -----Original Message----- > > From: [EMAIL PROTECTED] > > [mailto:[EMAIL PROTECTED] On Behalf Of Brian > > Harris > > Sent: April 9, 2008 12:01 PM > > To: [email protected] > > Subject: RE: What is a Bucket Test? > > > > A bucket test / barrel test is when you remove a head(s) in the remote > > area > > and fill up a bucket/barrel to see if it is flowing the gpm the is > > called > > for in the calc's. In our case with the density and heads we are using > > that > > would be 20 gpm, we are getting around 15 gpm. > > > > > > Brian Harris > > FDFP INC. > > > > -----Original Message----- > > From: [EMAIL PROTECTED] > > [mailto:[EMAIL PROTECTED] On Behalf Of > > [EMAIL PROTECTED] > > Sent: Wednesday, April 09, 2008 1:50 PM > > To: [email protected] > > Subject: What is a Bucket Test? > > > > Perhaps a dumb question, but what is a bucket test and is it conducted > > the > > same way in every jurisdiction? > > > > Bill Brooks > > > > William N. Brooks, P.E. > > Brooks Fire Protection Engineering Inc. > > 372 Wilett Drive > > Severna Park, MD 21146 > > 410-544-3620 Phone > > 410-544-3032 FAX > > 412-400-6528 Cell > > > > -------- Original Message -------- > > Subject: Failed Bucket Test > > From: "Brian Harris" <[EMAIL PROTECTED]> > > Date: Mon, April 07, 2008 2:30 pm > > To: <[email protected]> > > > > Fellow forum people: > > I have a situation where we have designed and installed a 13R system, it > > is > > completely finished and wham-o we fail the bucket test! Our system was > > designed based on the flow test provided by the city fire dept., turns > > out > > that a test taken now with the failed test shows a 25% drop in static & > > residual pressures, hence the failed test. Of course the owner is > > looking to > > us to pull a magic rabbit out of our #$% , err I mean hat, we have tried > > a > > few different things but with that big of a pressure loss there's really > > not > > much we can do. I don't feel it's our liability at this point since we > > went > > off the city's water flow test and per the calc's we were good, any > > thoughts? > > > > > > Regards, > > > > > > <http://www.firstdefensefire.com/> > > > > > > > > > > > > > > > > > > E-mail message checked by Spyware Doctor (5.5.0.178) Database version: > > 5.09560 http://www.pctools.com/spyware-doctor/ > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > To Unsubscribe, send an email > > to:[EMAIL PROTECTED]<[EMAIL PROTECTED] sprinkler.org> > > (Put the word unsubscribe in the subject field) > > > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > To Unsubscribe, send an email > > to:[EMAIL PROTECTED]<[EMAIL PROTECTED] sprinkler.org> > > (Put the word unsubscribe in the subject field) > > > > > > > > > > > > E-mail message checked by Spyware Doctor (5.5.0.178) Database version: > > 5.09590 http://www.pctools.com/spyware-doctor/ > > > > > > > > > > > > E-mail message checked by Spyware Doctor (5.5.0.178) Database version: > > 5.09590 http://www.pctools.com/spyware-doctor/ > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > To Unsubscribe, send an email > > to:[EMAIL PROTECTED]<[EMAIL PROTECTED] sprinkler.org> > > (Put the word unsubscribe in the subject field) > > > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > To Unsubscribe, send an email > > to:[EMAIL PROTECTED]<[EMAIL PROTECTED] sprinkler.org> > > (Put the word unsubscribe in the subject field) > > > > Todd G. Williams, PE > Fire Protection Design/Consulting > Stonington, Connecticut > www.fpdc.com > 860.535.2080 _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email to:[EMAIL PROTECTED]<[EMAIL PROTECTED] sprinkler.org> > (Put the word unsubscribe in the subject field) > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) ********************************************************************** Tyco Fire & Integrated Solutions (UK) Ltd. Registered in England, Number 1952517 Registered office: Tyco Park, Grimshaw Lane, Newton Heath, Manchester M40 2WL, England This e-mail is intended to be delivered only to the named addressee(s) and may contain information that is confidential and proprietary. If this information is received by anyone other than the named addressee(s), the recipient(s) should immediately notify the sender by e-mail and promptly delete the transmitted material from your computer and server. In no event shall this material be read, used, stored, or retained by anyone other than the named addressee(s) without the express written consent of the sender or the named addressee(s). This footnote also confirms that this email message has been swept by MIMEsweeper for the presence of computer viruses. www.mimesweeper.com ********************************************************************** _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)