Bucket test, IMHO, was to "prove" the "shortcut" calcs allowed under 13D
worked. 13R calcs are done to the same level of care as #13 calcs, so no
bucket test was needed.

In #13D done with shortcut calcs, makes sense and isn't a big deal-
especially when you consider the downside (fire death in sprinklered house).

But flowing 20 heads in a 13 system? Be careful what you ask for is right.

glc


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ron Greenman
Sent: Thursday, April 10, 2008 12:39 PM
To: [email protected]
Subject: Re: What is a Bucket Test?

Chris,

This silly test tells you nothing that other tests don't already tell  
you. It certainly doesn't tell you if your system will work or not  
because it presumes that conditions at the moment of the bucket test  
reflect the moment of the water availability test. Main drain tests  
will tell you if pipe is collapsed or valves are shut. What needs to  
be done (and I know this won't happen) is to get the water purveyors  
to quit handing out old crap and calling it good today. Thanks for  
setting me up for this mini-rant.

Ron Greenman