Greg,
See table 508.2. in IBC. Incidental area that require sprinklers - storage
rooms over 100 SF need 1 hour walls or sprinklers. How big are the storage
areas?

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan
Sent: Thursday, May 29, 2008 12:25 PM
To: [email protected]
Subject: partial system

OK, got a architect and engineer that claim that they can protect the
corridors only on a mini-storage warehouse. 
:

The IBC states that if the building has sprinklers but does not say
sprinklered throughout - has anyone else seen/done this?




Thank you,
Greg McGahan