In this case, it's the A/E firm that has all the responsibility:  This
is rural ND - there is no "AHJ".  Also, the A/E doesn't know who the
insurance provider is.  That leaves the owner, who should probably be
consulted.  That would also serve well to highlight how their "paid
experts" in the A/E firm aren't capable of doing their jobs.

Isn't it funny how I confident I am that no one in that A/E firm will be
seeing these public posts about them?

(Robert, I know of this project, but am not involved in any way)

Mark A. Sornsin, PE 
Fire Protection Engineer 
Ulteig Engineers, Inc. 
Fargo, ND  
701.280.8591
[EMAIL PROTECTED] 
 
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ron
Greenman
Sent: Wednesday, May 28, 2008 4:22 PM
To: [email protected]
Subject: Re: (no subject)

Doesn't the decision to let it burn or not belong to the owner (he
that gets to pay if it does), the insurer (he that gets to pay if
involved) and the AHJ (he that looks out for the public's interest as
defined by law)? Then there's the architect, the owner's paid expert,
that's supposed to consult with him regarding requirements, options
and best solutions. Unless you're being paid to be one of these your
only consideration should be as to how much your nether regions are
hanging in the wind and if the breeze is too cold to play.

On Wed, May 28, 2008 at 2:06 PM, Robert <[EMAIL PROTECTED]> wrote:
> I have a canola crushing facility that uses no solvents in the
extraction
> process.   Any ideas on the hazard classification?  NFPA 36 is for
solvent
> based extraction.
> I say that the delivery and load out areas should also be protected.
as
> well as the cooling tower and storage tanks.    They say let it burn.
>
> Thank you
>  Robert  Thompson
>
>  DAKOTA
> FIRE PROTECTION
> 1710 N. Washington Street
> Grand Forks ND 58206-5327
> Phone # (701) 772-8820
> Fax # (701) 772-7932
> Email [EMAIL PROTECTED]
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to