It's hard to say what their intent is or how they have interpreted the
codes.  If it were a Group B occupancy then unsprinkled, the exit access
limitation is 200 ft of travel, with sprinklers they could go 300 ft BUT
per the table, that is for a completely sprinkled building.  Also with
sprinklers they don't have to have the corridor walls rated where
without sprinks the walls would have to be 1hr.  But to provide
sprinklers only in the corridors doesn't meet the Code requirements, or
the definition of sprinklered throughout which has been mentioned
several times as referenced from NFPA 13 by Ron's buddy Inspector
Gadget.


Craig L. Prahl, CET   
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Craig
Rauch
Sent: Thursday, May 29, 2008 1:47 PM
To: [email protected]
Subject: RE: RE: partial system

I admit I have never seen a corridor only sprinkler system. I was
wondering how well these systems work in practice. Do they in fact
improve the tenability of the hallway?

Craig Rauch
Washington Twp. Fire Department

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Thursday, May 29, 2008 12:53 PM
To: [email protected]
Subject: RE: partial system

It all depends on how the AE has classified the building from an
occupancy standpoint.  If he calls it Group "B" (business) occupancy
then the code will allow it to go unsprinkled if it meets certain other
criteria like egress distances, fire alarm system, height above exit to
grade, etc....   If that be the case then he could think that by
providing a partial system that he's doing something "above and beyond".



Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg
McGahan
Sent: Thursday, May 29, 2008 12:25 PM
To: [email protected]
Subject: partial system

OK, got a architect and engineer that claim that they can protect the
corridors only on a mini-storage warehouse.
:

The IBC states that if the building has sprinklers but does not say
sprinklered throughout - has anyone else seen/done this?




Thank you,
Greg McGahan

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to