It's hard to say what their intent is or how they have interpreted the codes. If it were a Group B occupancy then unsprinkled, the exit access limitation is 200 ft of travel, with sprinklers they could go 300 ft BUT per the table, that is for a completely sprinkled building. Also with sprinklers they don't have to have the corridor walls rated where without sprinks the walls would have to be 1hr. But to provide sprinklers only in the corridors doesn't meet the Code requirements, or the definition of sprinklered throughout which has been mentioned several times as referenced from NFPA 13 by Ron's buddy Inspector Gadget.
Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.ch2m.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Craig Rauch Sent: Thursday, May 29, 2008 1:47 PM To: [email protected] Subject: RE: RE: partial system I admit I have never seen a corridor only sprinkler system. I was wondering how well these systems work in practice. Do they in fact improve the tenability of the hallway? Craig Rauch Washington Twp. Fire Department -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED] Sent: Thursday, May 29, 2008 12:53 PM To: [email protected] Subject: RE: partial system It all depends on how the AE has classified the building from an occupancy standpoint. If he calls it Group "B" (business) occupancy then the code will allow it to go unsprinkled if it meets certain other criteria like egress distances, fire alarm system, height above exit to grade, etc.... If that be the case then he could think that by providing a partial system that he's doing something "above and beyond". Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.ch2m.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan Sent: Thursday, May 29, 2008 12:25 PM To: [email protected] Subject: partial system OK, got a architect and engineer that claim that they can protect the corridors only on a mini-storage warehouse. : The IBC states that if the building has sprinklers but does not say sprinklered throughout - has anyone else seen/done this? Thank you, Greg McGahan Living Water Fire Protection, LLC 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 Fax: 850-937-1852 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)