I need a quick opinion from some 13R experts.

13r condo with the first floor divided in half front to back and then the front half is divided into 4 parking areas seperated by fire walls. The front wall is completely open and each garage serves 2 units.

6.8.2.2 states that each compartment can nothave openings greater than 50 sq.ft. I am interpreting this to mean openings into adjacent compartments not to the atmosphere and therefore a 4 head calc would be appropriate using dry heads flowing in accordance with NFPA 13R.

Thoughts please...
Greg McGahan
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to