I think it would be a one head calc (assuming only one head per
balcony and they are not contiguous), but it is 5 AM and no coffee yet.
At 09:29 PM 6/11/2008, you wrote:
One more.... HAve we discussed to calcs required for the sidewalls
on balconies that the IBC requires?
On Wed, 11 Jun 2008 21:13:50 -0400 "Greg McGahan"
<[EMAIL PROTECTED]> wrote:
I need a quick opinion from some 13R experts.
13r condo with the first floor divided in half front to back and
then the front half is divided into 4 parking areas seperated by
fire walls. The front wall is completely open and each garage serves 2 units.
6.8.2.2 states that each compartment can nothave openings greater
than 50 sq.ft. I am interpreting this to mean openings into
adjacent compartments not to the atmosphere and therefore a 4 head
calc would be appropriate using dry heads flowing in accordance with NFPA 13R.
Thoughts please...
Greg McGahan
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)