13R Garages are covered in 6.8.3 and 6.8.3.2 Says that garages accessible from more than 1 dwelling unit (you say 2) (Are they considered separate buildings per 6.8.3.1) if not, protect in accordance with 6.8.2 Are you less than 500Sf total area in garage Are you 130Sf or less per head coverage Are you using QR heads (6.8.2.3 does not list garages as appropriate for res. Heads) Are you flowing 0.10 Gpm/Sf (Openings to outside of building /unit are not limited by 50 Sf unless it's to another protected area, such as a corridor or protected exterior walkway.)
Say yes to the above and design 4 heads 0.10 Gpm/Sf. (You may still ignore the garage door per 6.8.3.2) Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan Sent: Wednesday, June 11, 2008 7:14 PM To: [email protected] Subject: 13r carport I need a quick opinion from some 13R experts. 13r condo with the first floor divided in half front to back and then the front half is divided into 4 parking areas seperated by fire walls. The front wall is completely open and each garage serves 2 units. 6.8.2.2 states that each compartment can nothave openings greater than 50 sq.ft. I am interpreting this to mean openings into adjacent compartments not to the atmosphere and therefore a 4 head calc would be appropriate using dry heads flowing in accordance with NFPA 13R. Thoughts please... Greg McGahan _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)