NFPA 13, 2007, section 8.17.2.3, (3) - For hydraulically calculated 
systems, the fire department connection shall be permitted to be less than 
4 in. and no less than the size of the system riser, where serving one 
system riser.

My opinion is that the pipe from the FDC itself to the riser needs to be 
4" minimum.  Based on your description I would interpret that as saying 
that the 2 1/2" pipe on the FDC is not permitted as the riser is 4" and I 
am assuming the 2 1/2" reduction is between the FDC and the riser. 

My opinion only.

Andrew Weisfield




"Brian Harris" <[EMAIL PROTECTED]> 
Sent by: [EMAIL PROTECTED]
07/18/2008 08:36 AM
Please respond to
[email protected]


To
<[email protected]>
cc

Subject
FDC Connection






Forum,
Quick FDC connection, I just saw on some drawings that came in that the 
FDC
is 4" with a 4" check valve and then reduced down to 2-1/2" with a 
reducing
coupling. The system riser is 4", can you choke it down like that?
Technically the FDC is the same size as the riser but where do you draw 
the
line? I'm not liking it, what say you???
 

Regards,

 
<http://www.firstdefensefire.com/> 

 

 




E-mail message checked by Spyware Doctor (6.0.0.354)
Database version: 5.10290e
http://www.pctools.com/en/spyware-doctor-antivirus/
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



This email is intended for named recipients only.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to