Well if you call NFPA (as our SFMO did) they will apparently tell you what
it connects into is not regulated other than a main connection. 

Where it gets fuzzy IMHO is what is a main?  I know there is a definition.
Can main fees sprinkler directly?  Think a 6" down a corridor serving BL's
and run out to another area.  This is most always is considered a main.  If
it has 1" openings serving the heads below the ceiling is it a main or a BL?
And if you are sure it's a main and the drops are the BL mentioned in the
definition then what if you have 1/2" openings with pendant heads for a
combustible concealed space issue. Granted that might be rare and raise
other issue in the hypothetical but still.  Substitute 2" for the 6" and
what has changed assuming the 2" is the supply to another area.  Following
the logic game (which shouldn't be done with codes). What about pipe
schedule pipe sizing or graduated pipe sizing (but not a scheduled system)
with a mess of armovers with say two drops off the 1 1/4"?  Is the 1 1/4" a
main or branch line? And if any of the above are both can I connect a 4" FDC
run to a 1 1/4" main (/branch line).  What if the tree example I #2 below
the main graduates down to 1 1/2"?  Obviously either I don't understand the
definitions or there are some holes.  I don’t have a better definition
either way.  Another obviously - I'm thinking way too much on a Friday.


Excerpts from our SFMO policy:

In recent Report on Proposals (ROP) A2006 (13-110 Log #CP111) and Report on
Comments (ROC) A2006 (13-96 Log #253) the NFPA 13 Technical Committee
affirmed the purpose of the Fire Department Connection is to supplement the
water supply, but not necessarily provide the entire sprinkler system
demand. Fire department connections are not intended to deliver a specific
volume of water. The committee also clarified that the fire department
connection shall only connect to main piping on the system it serves and not
to branch line piping. (ROP 13-355 Log #557)

The following two examples are typical of the types of arrangements that are
allowed.

Example #1: A gridded wet system with a 4” riser, 4” feed main, 3” primary
main, 2½” secondary main and 2” branch lines. If the FDC is connected to the
system riser, the FDC piping and associated components from the riser to the
inlet shall be 4”. If the FDC is connected to the 2½” secondary main, the
FDC piping and associated components from the 2½” secondary main to the
inlet shall be 4”.

Example #2: A wet tree system with a 3” riser, 2½” feed main, 2” cross main,
and 1¼” branch lines. If the FDC is connected to the system riser, the FDC
piping and associated components from the riser to the inlet shall be 3”. If
the FDC is connected to the 2” cross main, the FDC piping and associated
components from the 2” cross main to the inlet shall be 3”.

The full MNSFMO policy can be seen at:
http://www.dps.state.mn.us/fmarshal/fireprot/Interpretations/INTERPFP04(2007
)-FDCsupplysizing.pdf


Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [EMAIL PROTECTED]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Friday, July 18, 2008 10:54 AM
To: [email protected]
Subject: RE: RE: FDC Connection

I have always interpreted the section for FDC's  to mean that the 4" FDC 
must tie into a 4" main.

As I re-read 8.17.2.3, the code does not clearly state this.  8.17.2.4.1.2 
permits connecting to a main on the system served, but again, I always 
refer back to 8.17.2.3 and size the FDC to equal the riser size, and then 
make sure it ties into a main of equal size or the riser.

Maybe some clarification to the language would be good.

Andrew Weisfield



Craig Rauch <[EMAIL PROTECTED]> 
Sent by: [EMAIL PROTECTED]
07/18/2008 11:35 AM
Please respond to
[email protected]


To
"[email protected]" <[email protected]>
cc

Subject
RE: RE: FDC Connection






Would Apendix 8.17.2.4.1 indicate that the intent of the code is to 
require that the 4" must tie in to a 4" main?

It would seem that the language in this section needs a bit of 
clarification.

Would it be wise to modify 8.17.2.4.1.2 to refer to 8.17.2.3 for the size 
of the main?

Or, if it is decided the actual intent is to allow such a connection, the 
apendix needs to be changed.

Craig Rauch
Washington Township Fire Department
Dayton, Ohio

-----Original Message-----
From: [EMAIL PROTECTED] 
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, 
Ron
Sent: Friday, July 18, 2008 11:05 AM
To: [email protected]
Subject: RE: FDC Connection

Supplemental? If 150 psi is pumped into the FDC the riser check will close 
making the FDC the only supply.

Ron Fletcher
Aero Automatic
Phoenix, AZ

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom 
McMahon
Sent: Friday, July 18, 2008 7:45 AM
To: [email protected]
Subject: RE: FDC Connection

I think it's important to remember that the FDC is "supplemental" to the 
supply, not "Equal" to a supply. I feel that the 4" tied to the 2-1/2"
MAIN
meets the intent of the standard. It does not need to be 4" all the way 
from the riser to the FDC, when the FDC is remote from the riser and 
connects to a MAIN.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Garth W.
Warren
Sent: Friday, July 18, 2008 9:38 AM
To: [email protected]
Subject: Re: FDC Connection

it should be 4" from the connection to the main and then connected through 
a
21/2x21/2x4 tee.  I disagree that NFPA allows for connection anywhere on 
the system, it states "provided the pipe size meets the requirements of 
8.17.2.3."  Otherwise "creative" companies would have 1" fdc piping 
connected to the end of a line.

Garth
----- Original Message -----
From: "Brian Harris" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Friday, July 18, 2008 9:02 AM
Subject: RE: FDC Connection


> The FDC is actually remote from the riser & ties into a 2-1/2"
floating
> main. I think it should at least be 4" all the way to the back main
and
then
> reduce it there....
>
>
> Brian Harris
> FDFP INC.
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of
> [EMAIL PROTECTED]
> Sent: Friday, July 18, 2008 8:48 AM
> To: [email protected]
> Subject: Re: FDC Connection
>
> NFPA 13, 2007, section 8.17.2.3, (3) - For hydraulically calculated
systems,
> the fire department connection shall be permitted to be less than
> 4 in. and no less than the size of the system riser, where serving one
> system riser.
>
> My opinion is that the pipe from the FDC itself to the riser needs to
be
4"
> minimum.  Based on your description I would interpret that as saying
that
> the 2 1/2" pipe on the FDC is not permitted as the riser is 4" and I
am
> assuming the 2 1/2" reduction is between the FDC and the riser.
>
> My opinion only.
>
> Andrew Weisfield
>
>
>
>
> "Brian Harris" <[EMAIL PROTECTED]> Sent by:
> [EMAIL PROTECTED]
> 07/18/2008 08:36 AM
> Please respond to
> [email protected]
>
>
> To
> <[email protected]>
> cc
>
> Subject
> FDC Connection
>
>
>
>
>
>
> Forum,
> Quick FDC connection, I just saw on some drawings that came in that
the
> FDC
> is 4" with a 4" check valve and then reduced down to 2-1/2" with a
> reducing coupling. The system riser is 4", can you choke it down like
> that?
> Technically the FDC is the same size as the riser but where do you
draw
> the
> line? I'm not liking it, what say you???
>
>
> Regards,
>
>
> <http://www.firstdefensefire.com/>
>
>
>
>
>
>
>
>
> E-mail message checked by Spyware Doctor (6.0.0.354) Database version:
> 5.10290e http://www.pctools.com/en/spyware-doctor-antivirus/
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
>
>
> This email is intended for named recipients only.
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
>
>
>
>
> E-mail message checked by Spyware Doctor (6.0.0.354) Database version:
> 5.10290e http://www.pctools.com/en/spyware-doctor-antivirus/
>
>
>
>
>
> E-mail message checked by Spyware Doctor (6.0.0.354) Database version:
> 5.10290e http://www.pctools.com/en/spyware-doctor-antivirus/
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG - http://www.avg.com
Version: 8.0.138 / Virus Database: 270.5.1/1559 - Release Date:
7/17/2008
6:08 PM



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)




This email is intended for named recipients only.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to