When I called Lubrizol they indicated that the cpvc should be considered 
non-combustible UNLESS I totally misunderstood them (very possible this week).

Greg McGahan
Operations Manager

Living Water Fire Protection
1160 McKenzie Road
P.O. Box 877
Cantonment, Florida 32533
(850) 937.1850 | Fax (850) 937.1852 | CellĀ (850) 554.3231
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Johnson, Duane 
(NIH/OD/ORS) [C]
Sent: Tuesday, April 28, 2009 11:51 AM
To: [email protected]
Subject: RE: Rating of the sprinkler escutcheon

Yes.

-----Original Message-----
From: Dewayne Martinez [mailto:[email protected]] 
Sent: Tuesday, April 28, 2009 12:50 PM
To: [email protected]
Subject: RE: Rating of the sprinkler escutcheon

Duane,
The handbook you reference, is it for the IBC? 

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Johnson, Duane 
(NIH/OD/ORS) [C]
Sent: Tuesday, April 28, 2009 11:16 AM
To: [email protected]
Subject: RE: Rating of the sprinkler escutcheon

The handbook indicates this exception is for non-combustible pipes.  Note also, 
this exception is for pipes penetrating only one membrane of the assembly.  So 
if the pipe penetrates both sides of the wall, the side opposite of the 
sprinkler would need penetration protection (firestopping).

Duane Johnson, PE

Program Manager
Division of the Fire Marshal (Support Contractor) Office of Research Services 
National Institutes of Health
301-496-0487

-----Original Message-----
From: [email protected] [mailto:[email protected]]
Sent: Tuesday, April 28, 2009 11:34 AM
To: [email protected]
Subject: RE: Rating of the sprinkler escutcheon

And is that assuming that the pipe penetrating the membrane is of 
noncombustible materials? 

Any time you breach rated construction either the material penetrating has to 
be non-combustible or you provide a UL Listed , non-combustible sleeve assembly 
that is sealed at both ends.  


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Johnson, Duane 
(NIH/OD/ORS) [C]
Sent: Tuesday, April 28, 2009 11:28 AM
To: [email protected]
Subject: RE: Rating of the sprinkler escutcheon

IBC 712.3.2 #3 provides an exception to penetration protection of 1-hr partion: 
 The annular space created by the penetration of a fire sprinkler provided it 
is covered by a metal escutcheon plate.


Duane Johnson, PE

Program Manager
Division of the Fire Marshal (Support Contractor) Office of Research Services 
National Institutes of Health
301-496-0487

-----Original Message-----
From: [email protected] [mailto:[email protected]]
Sent: Tuesday, April 28, 2009 11:07 AM
To: [email protected]
Subject: RE: Rating of the sprinkler escutcheon

Not measurable.  If the wall is to be 1hr rated construction, the fire stopping 
material for the penetration must provide equal.  How would you measure the 
value of the sprinkler in relation to hours of equivalent resistance?


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Tuesday, April 28, 2009 11:03 AM
To: [email protected]
Subject: RE: Rating of the sprinkler escutcheon

What about the sprinkler itself? Doesn't it offer something of value at the 
point of penetration?

Greg McGahan
Operations Manager

Living Water Fire Protection
1160 McKenzie Road
P.O. Box 877
Cantonment, Florida 32533
(850) 937.1850 | Fax (850) 937.1852 | CellĀ (850) 554.3231 [email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Sal Izzo (TECH- 
103)
Sent: Tuesday, April 28, 2009 9:59 AM
To: [email protected]
Subject: RE: Rating of the sprinkler escutcheon

I believe CPVC is considered a combustible penetration when running through a 
rated assembly and therefore would require a listed firestop assembly.  Metal 
escutcheons provide no rating; the IBC permits only an escutcheon to cover the 
annular space of a sprinkler penetration when the pipe is noncombustible, i.e., 
steel, copper, conduit, etc.

Regards,

Salvatore Izzo, P.E. SFPE
Manager - Reliable Technical Services

________________________________________
From: [email protected] 
[[email protected]] On Behalf Of Bobby Gillett 
[[email protected]]
Sent: Tuesday, April 28, 2009 10:56 AM
To: [email protected]
Subject: Rating of the sprinkler escutcheon

Our situations - we have a hotel designed to 13R that requires our cpvc piping 
to be run through a fire rated wall between two units with 4.0K residential 
semi-recessed sidewall heads spraying into both units. The other is the 
extended coverage 8.0K semi-recessed sprinkler spraying into the stairwell 
(also fed by cpvc from the corridor). The question being asked by the fire 
marshall - What is the fire rating of the escutcheons?



Bobby Gillett

Sr. Project Manager

Key Fire Protection, Inc.

(731) 424-0130 office  (731) 424-9285 fax

(731) 267-4853 cell

 <mailto:[email protected]>
[email protected]







_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to