The IBC allows for the penetration of a sprinkler (IBC 2006, 712.3.2,3 Gives 
some latitude for membrane penetrations) of rated walls and partitions.  That 
is considering that the penetration is by steel, ferrous or copper pipes.  
Plastic isn't mentioned.

Ceilings are dealt with in the same way as mentioned 712.4.1.2,4.  Again no 
plastic pipe mentioned.
 


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Bobby Gillett
Sent: Tuesday, April 28, 2009 2:09 PM
To: [email protected]
Subject: RE: Rating of the sprinkler escutcheon

How do you propose fire rating the penetration when you have a HSW or pendent 
in a ceiling? Especially concealed or semi recessed.

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax
(731) 267-4853 cell
[email protected]
 
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Tuesday, April 28, 2009 1:03 PM
To: [email protected]
Subject: RE: Rating of the sprinkler escutcheon

Well, that's a lot of fancy words that don't say non-combustible.  

Some pipe won't sustain combustion without direct flame impingement, so maybe 
that's what they meant when they said it wasn't combustible.  But it also won't 
retain it's shape and when that occurs you have a breach in the rated wall.

Easiest thing to do is if you have to go through a rated wall, transition to 
steel and fire caulk it at the penetrations and be done with it.  Why debate it?

Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Thomas Watt
Sent: Tuesday, April 28, 2009 1:56 PM
To: [email protected]
Subject: Re: Rating of the sprinkler escutcheon



>From the Lubrizol website...

The flame spread and smoke generation characteristics of TempRite CPVC 
materials have been evaluated by Underwriters Laboratories, Inc. (ULI), 
Southwest Research Institute (SWRI), and Factory Mutual (FM) employing a number 
of recognized test methods.

ULI evaluated TempRite CPVC for flammability in accordance with UL 94, which is 
used for determining the flammability of plastic materials used in the 
components and parts of finished products. This test measures a material's 
resistance to burning, dripping, glow emission and burn through. CPVC has 
achieved the highest rating available within the scope of this test of V0, 5VB 
and 5VA.





----- Original Message -----
From: "Greg McGahan" <[email protected]>
To: <[email protected]>
Sent: Tuesday, April 28, 2009 1:31 PM
Subject: RE: Rating of the sprinkler escutcheon


When I called Lubrizol they indicated that the cpvc should be considered 
non-combustible UNLESS I totally misunderstood them (very possible this week).

Greg McGahan
Operations Manager

Living Water Fire Protection
1160 McKenzie Road
P.O. Box 877
Cantonment, Florida 32533
(850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231 [email protected]




_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to