I do understand the process for the back side of the wall. I'm not trying to
get out of fire caulking anything. I do not see how a semi-recessed,
concealed, etc. sprinkler with listed escutcheon in a rated wall can be
sealed on the sprinkler side. 

Please keep in mind this started with the AHJ wanting to know the fire
rating of the escutcheon.

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax 
(731) 267-4853 cell
[email protected]
 
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Sprinkler
Forum
Sent: Tuesday, April 28, 2009 1:30 PM
To: [email protected]
Subject: Re: Rating of the sprinkler escutcheon

Keep in mind that th exception in the code is assuming the sprinkler  
head has activated therefore preventing direct flame impingement.

The sprinkler spray argument goes away on the back side of the wall  
though.

Rather than debate whether cpvc is combustible or not with your AHJ,  
you should transition to steel, and caulk the penetration on the back  
side of the wall. Let the opening on the inside of the stair fall  
under the exception in the code.


Justin D. Reid, P.E.
RLH Fire Protection
16735 Saticoy St. #110
Van Nuys, CA 91406
213-798-0251

Sent from my iPhone

On Apr 28, 2009, at 11:08 AM, "Bobby Gillett"
<[email protected] 
 > wrote:

> How do you propose fire rating the penetration when you have a HSW or
> pendent in a ceiling? Especially concealed or semi recessed.
>
> Bobby Gillett
> Sr. Project Manager
> Key Fire Protection, Inc.
> (731) 424-0130 office  (731) 424-9285 fax
> (731) 267-4853 cell
> [email protected]
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of
> [email protected]
> Sent: Tuesday, April 28, 2009 1:03 PM
> To: [email protected]
> Subject: RE: Rating of the sprinkler escutcheon
>
> Well, that's a lot of fancy words that don't say non-combustible.
>
> Some pipe won't sustain combustion without direct flame impingement,  
> so
> maybe that's what they meant when they said it wasn't combustible.   
> But it
> also won't retain it's shape and when that occurs you have a breach  
> in the
> rated wall.
>
> Easiest thing to do is if you have to go through a rated wall,  
> transition to
> steel and fire caulk it at the penetrations and be done with it.   
> Why debate
> it?
>
> Craig L. Prahl, CET
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [email protected]
> http://www.ch2m.com
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of  
> Thomas Watt
> Sent: Tuesday, April 28, 2009 1:56 PM
> To: [email protected]
> Subject: Re: Rating of the sprinkler escutcheon
>
>
>
>> From the Lubrizol website...
>
> The flame spread and smoke generation characteristics of TempRite CPVC
> materials have been evaluated by Underwriters Laboratories, Inc.  
> (ULI),
> Southwest Research Institute (SWRI), and Factory Mutual (FM)  
> employing a
> number of recognized test methods.
>
> ULI evaluated TempRite CPVC for flammability in accordance with UL  
> 94, which
> is used for determining the flammability of plastic materials used  
> in the
> components and parts of finished products. This test measures a  
> material's
> resistance to burning, dripping, glow emission and burn through.  
> CPVC has
> achieved the highest rating available within the scope of this test  
> of V0,
> 5VB and 5VA.
>
>
>
>
>
> ----- Original Message -----
> From: "Greg McGahan" <[email protected]>
> To: <[email protected]>
> Sent: Tuesday, April 28, 2009 1:31 PM
> Subject: RE: Rating of the sprinkler escutcheon
>
>
> When I called Lubrizol they indicated that the cpvc should be  
> considered
> non-combustible UNLESS I totally misunderstood them (very possible  
> this
> week).
>
> Greg McGahan
> Operations Manager
>
> Living Water Fire Protection
> 1160 McKenzie Road
> P.O. Box 877
> Cantonment, Florida 32533
> (850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
> [email protected]
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to