The connection from the FDC must be below the DPV and the connection tee must be above a swing check in the riser in most every case.
Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 3300 King Ave Cleveland, OH 44114 216-621-8899 216-570-7030 cell -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of A.P.Silva Sent: Monday, May 18, 2009 7:21 PM To: [email protected] Subject: FDC for Dry Pipe Systems The FDC is required to be connected between the main control valve and the dry pipe valve. I'v always thought this might be due to possible air leak from the FDC check valve, if it's connected on the dry side, downstream of the dry pipe valve. Is this the reason? For a project having a single dry system, the contractor has connected the FDC downstream of the DPV. The system seems to be holding. Any comments? Tony _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)