it is so that pumping will not flood the system if the valve is not tripped 
and so that closing of the control valve will not render the FDC unusable..

Garth

----- Original Message ----- 
From: "A.P.Silva" <[email protected]>
To: <[email protected]>
Sent: Monday, May 18, 2009 7:21 PM
Subject: FDC for Dry Pipe Systems


> The FDC is required to be connected between the main control valve and the
> dry pipe valve. I'v always thought this might be due to possible air leak
> from the FDC check valve, if it's connected on the dry side, downstream of
> the dry pipe valve. Is this the reason?
>
> For a project having a single dry system, the contractor has connected the
> FDC downstream of the DPV. The system seems to be holding. Any comments?
>
> Tony
>