Where do you throw the hot coals from your grill but in the chutes.  That's
the difference between an elevator.  The record will reflect chute fires are
much more common and severe than elevators.  Chutes drop into a dumpster or
the like with a lot more fuel load than misc. papers at the bottom of the
elevator.  And no I don't think you get out of the chutes in a 13R.  

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ken Holsopple
(forum)
Sent: Wednesday, December 16, 2009 1:43 PM
To: [email protected]
Subject: IBC and NFPA 13R - Linen/Trash Chutes

Folks.....I need some opinions....

I have multiple buildings that fall into a Group R category and also qualify
for the use of NFPA 13R. These buildings all have either trash or linen
chutes. The IBC (2006) states the following....

707.13.6 Automatic sprinkler system.
An approved automatic sprinkler system shall be installed in accordance with
Section 903.2.10.2.

903.2 Where required.
Approved automatic sprinkler systems in new buildings and structures shall
be provided in the locations described in this section.

903.2.7 Group R.
An automatic sprinkler system installed in accordance with Section 903.3
shall be provided throughout all buildings with a Group R fire area.

903.2.10.2 Rubbish and linen chutes.
An automatic sprinkler system shall be installed at the top of rubbish and
linen chutes and in their terminal rooms. Chutes extending through three or
more floors shall have additional sprinkler heads installed within such
chutes at alternate floors. Chute sprinklers shall be accessible for
servicing.

903.3.1.2 NFPA 13R sprinkler systems.
WHERE ALLOWED in buildings of Group R, up to and including four stories in
height, automatic sprinkler systems shall be installed throughout in
accordance with NFPA 13R.

NFPA 13R Section 6.8.5
Sprinklers shall not be required in attic....elevator machine
rooms....elevator shafts......and other concealed spaces not intended for
living purposes or storage and do not contain fuel fired equipment.

With the sections noted above I am thinking that the blanket statement that
IBC is trying to make is that sprinklers are required in any linen/trash
chute whether the building has a fire sprinkler system or it doesn't.
However, I am of the opinion that if I meet the qualifications for a
building to use the NFPA 13R standard then 903.3.1.2 acts as an exception to
the previous rules in the "where required" section. Anybody else see it this
way?

I am having a hard time accepting that I don't need sprinklers in an
elevator pit or elevator machine room (ya know flammable hydraulic fluid?),
but make sure you protect the discarded Sara Lee pie pans (that can't be
used as heat collectors anymore) or Aunt Ethel's stinky socks.

Is everybody lost but me again?????

Best Regards and Happy Holidays,

Ken Holsopple






_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to