Chris, John, and Matt,

I think my error stems from treating IBC Section  903.3.1.2 as an exception.
In the same "Where required" section of the IBC....it tells me that I need
to follow 903.3. This is where the 13R "exception" is allowed if the
building meets the qualifications.

Although, when you add in the Chapter 7 stuff....it does indicate (as
you'ins pointed out) that the IBC folks want sprinklers in the chutes no
matter what.

Just didn't sit right with me, but I see all of your points and wouldn't
dream of arguing with a PE or an AHJ. And especially not with a fellow
contractor. :)

Thanks for your input fellas.

John:

Are you talking about elevators/elevator machine rooms for storage or just
concealed spaces in general?