Chris,

Wouldn't a building service chute fall under "other concealed spaces not
intended for
living purposes or storage and do not contain fuel fired equipment"?

On Wed, Dec 16, 2009 at 3:14 PM, Chris Cahill <[email protected]>wrote:

> Where do you throw the hot coals from your grill but in the chutes.  That's
> the difference between an elevator.  The record will reflect chute fires
> are
> much more common and severe than elevators.  Chutes drop into a dumpster or
> the like with a lot more fuel load than misc. papers at the bottom of the
> elevator.  And no I don't think you get out of the chutes in a 13R.
>
> Chris Cahill, P.E.
> Fire Protection Engineer
> Sentry Fire Protection, Inc.
>
> 763-658-4483
> 763-658-4921 fax
>
> Email: [email protected]
>
> Mail: P.O. Box 69
>        Waverly, MN 55390
>
> Location: 4439 Hwy 12 SW
>              Waverly, MN 55390
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Ken
> Holsopple
> (forum)
> Sent: Wednesday, December 16, 2009 1:43 PM
> To: [email protected]
> Subject: IBC and NFPA 13R - Linen/Trash Chutes
>
> Folks.....I need some opinions....
>
> I have multiple buildings that fall into a Group R category and also
> qualify
> for the use of NFPA 13R. These buildings all have either trash or linen
> chutes. The IBC (2006) states the following....
>
> 707.13.6 Automatic sprinkler system.
> An approved automatic sprinkler system shall be installed in accordance
> with
> Section 903.2.10.2.
>
> 903.2 Where required.
> Approved automatic sprinkler systems in new buildings and structures shall
> be provided in the locations described in this section.
>
> 903.2.7 Group R.
> An automatic sprinkler system installed in accordance with Section 903.3
> shall be provided throughout all buildings with a Group R fire area.
>
> 903.2.10.2 Rubbish and linen chutes.
> An automatic sprinkler system shall be installed at the top of rubbish and
> linen chutes and in their terminal rooms. Chutes extending through three or
> more floors shall have additional sprinkler heads installed within such
> chutes at alternate floors. Chute sprinklers shall be accessible for
> servicing.
>
> 903.3.1.2 NFPA 13R sprinkler systems.
> WHERE ALLOWED in buildings of Group R, up to and including four stories in
> height, automatic sprinkler systems shall be installed throughout in
> accordance with NFPA 13R.
>
> NFPA 13R Section 6.8.5
> Sprinklers shall not be required in attic....elevator machine
> rooms....elevator shafts......and other concealed spaces not intended for
> living purposes or storage and do not contain fuel fired equipment.
>
> With the sections noted above I am thinking that the blanket statement that
> IBC is trying to make is that sprinklers are required in any linen/trash
> chute whether the building has a fire sprinkler system or it doesn't.
> However, I am of the opinion that if I meet the qualifications for a
> building to use the NFPA 13R standard then 903.3.1.2 acts as an exception
> to
> the previous rules in the "where required" section. Anybody else see it
> this
> way?
>
> I am having a hard time accepting that I don't need sprinklers in an
> elevator pit or elevator machine room (ya know flammable hydraulic fluid?),
> but make sure you protect the discarded Sara Lee pie pans (that can't be
> used as heat collectors anymore) or Aunt Ethel's stinky socks.
>
> Is everybody lost but me again?????
>
> Best Regards and Happy Holidays,
>
> Ken Holsopple
>
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to