Chris, In these two instances, if the occupants had a grill, it would be set up in their living room. There are no balconies. If there were...and this was Type V....I have no doubt that they would be sprinklered balconies. The Forum discussions on the issue have made that balcony issue crystal clear to me.
I get your drift though.....but with respect to life safety vs. saving the building...... Ken -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Chris Cahill Sent: Wednesday, December 16, 2009 3:14 PM To: [email protected] Subject: RE: IBC and NFPA 13R - Linen/Trash Chutes Where do you throw the hot coals from your grill but in the chutes. That's the difference between an elevator. The record will reflect chute fires are much more common and severe than elevators. Chutes drop into a dumpster or the like with a lot more fuel load than misc. papers at the bottom of the elevator. And no I don't think you get out of the chutes in a 13R. Chris Cahill, P.E. Fire Protection Engineer Sentry Fire Protection, Inc. 763-658-4483 763-658-4921 fax Email: [email protected] Mail: P.O. Box 69 Waverly, MN 55390 Location: 4439 Hwy 12 SW Waverly, MN 55390 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Ken Holsopple (forum) Sent: Wednesday, December 16, 2009 1:43 PM To: [email protected] Subject: IBC and NFPA 13R - Linen/Trash Chutes Folks.....I need some opinions.... I have multiple buildings that fall into a Group R category and also qualify for the use of NFPA 13R. These buildings all have either trash or linen chutes. The IBC (2006) states the following.... 707.13.6 Automatic sprinkler system. An approved automatic sprinkler system shall be installed in accordance with Section 903.2.10.2. 903.2 Where required. Approved automatic sprinkler systems in new buildings and structures shall be provided in the locations described in this section. 903.2.7 Group R. An automatic sprinkler system installed in accordance with Section 903.3 shall be provided throughout all buildings with a Group R fire area. 903.2.10.2 Rubbish and linen chutes. An automatic sprinkler system shall be installed at the top of rubbish and linen chutes and in their terminal rooms. Chutes extending through three or more floors shall have additional sprinkler heads installed within such chutes at alternate floors. Chute sprinklers shall be accessible for servicing. 903.3.1.2 NFPA 13R sprinkler systems. WHERE ALLOWED in buildings of Group R, up to and including four stories in height, automatic sprinkler systems shall be installed throughout in accordance with NFPA 13R. NFPA 13R Section 6.8.5 Sprinklers shall not be required in attic....elevator machine rooms....elevator shafts......and other concealed spaces not intended for living purposes or storage and do not contain fuel fired equipment. With the sections noted above I am thinking that the blanket statement that IBC is trying to make is that sprinklers are required in any linen/trash chute whether the building has a fire sprinkler system or it doesn't. However, I am of the opinion that if I meet the qualifications for a building to use the NFPA 13R standard then 903.3.1.2 acts as an exception to the previous rules in the "where required" section. Anybody else see it this way? I am having a hard time accepting that I don't need sprinklers in an elevator pit or elevator machine room (ya know flammable hydraulic fluid?), but make sure you protect the discarded Sara Lee pie pans (that can't be used as heat collectors anymore) or Aunt Ethel's stinky socks. Is everybody lost but me again????? Best Regards and Happy Holidays, Ken Holsopple _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)